Hobo128
- Messages
- 302
Went to a dfe service the other day and found that there was no MI or data badge on the fire. So i had to assess the installation against the requirment of the current and reletive british standard regs.
Measured hearth requirments: Ok
Measure flue diameter/height against builders opening:Ok
Checked for adequit ventilation ( Document j part 3.11 100cm2): Ok
Visually inspected flue :Ok
Flue flow test:Ok
Took note of position of coals and cleaned them and burner then replaced:Ok
Checked FSD (29 second fail safe):Ok
Checked working pressure at meter 22.5
Checked working pressure at appliance 21.5:Ok
Spillage test as stated using method from Essential gas safety:Ok
Then finally i gas rated it (3600x10.76x21/120=6.77kwgross)
My question is that is there any point me gas rating this appliance without having a data badge or Mi or should i have just capped the appliance straight away even though everything seems in good working order?
Flue flow test:Ok