Posted this last week in the wrong forum so this is a (modified) repeat and I like to three who answered that post.

Currently have a very old open system gas boiler which services the hot water system, via a storage cylinder and a ring of 11 radiators.

Needs to be replaced and I have selected the plumber to carry out the work. Others who quoted for the work mentioned that the gas feed would have to be upgraded to 22mm (based upon the visual inspection of 1.6m of 15mm pipe rising from the floor to the current boiler). Only one asked about the current pipe work feeding to this 15mm length.

The proposed condensing boiler to be installed is the Vaillant Ecoplus 618 which has an inlet gas pressure requirement of 20mbar on a 15mm connection.

The position of the new boiler is up in the loft which will require a 6mtr extension to the current gas pipe.

The feed from the street to the gas meter is 28mm steel reducing to 22mm copper and the outlet from the meter is 22mm copper back to 28mm steel that then goes under the floor (solid) across to the garage and then is fed up to a T in the floor - a length of 4.3m. The T splits the gas to the 15mm for the boiler and then goes under the floorboards to feed a supply to the cooker which is not used.

Unfortunately the split happens under the dining room floor which is covered in wood laminate. To access the joint will require the room to be cleared and the whole floor being lifted.

My neighbour had his boiler moved to the loft about 2 years ago and the installer used 15mm pipe all the way.

Have read numerous feeds about 15mm vs. 22mm and the Corgi changes to the regulations and have got confused..

I do not know the gas pressure into the house – but surely the size of the gas inlet pipe should be enough to feed the required mbar pressure required by the boiler?

Thank you any guidance you can offer.

Regards
 
try simplify to the following.
and will work it out for you,
size of meter first
appliances been supplied in k/w
size of pipe to first tee etc
size and length of pipe to first appliance +k/w requirement
size and length of pipe to remaining appliance. k/w requirement
 
Thank you for your reply and offer to help here are the answers to your questions:

size of meter - unknown but Manu. is Actaris (M32 Epsilon) installed Jan 2006 [govenor states Inlet 30m/Outlet unreadable Type 1&2 500 ft 3"(?) Maxflow stamped in the metal]
appliances been supplied in k/w - only 1 at 18kw
size of pipe to first tee - 28mm [length 4.3m]
size and length of pipe to first appliance - 15mm [length 9m] – 18kw (moving boiler to loft - extending pipework by 6m)
size and length of pipe to remaining appliance. - 28mm [length 5m] – Cooker point [not used].


Will look at the meter again if you can help with suggestions of what to look for.

Regards
 
9 meters of 15mm copper feeding 18kw will be undersized.
 
Thank you for your reply and offer to help here are the answers to your questions:

size of meter - unknown but Manu. is Actaris (M32 Epsilon) installed Jan 2006 [govenor states Inlet 30m/Outlet unreadable Type 1&2 500 ft 3"(?) Maxflow stamped in the metal]
assume its a u6/ga capable of supplying 6 cbm per hour

appliances been supplied in k/w - only 1 at 18kw
size of pipe to first tee - 28mm [length 4.3m]
size and length of pipe to first appliance - 15mm [length 9m] – 18kw (moving boiler to loft - extending pipework by 6m)

15mm not big enough require 22mm should do

size and length of pipe to remaining appliance. - 28mm [length 5m] – Cooker point [not used].
 
Status
Not open for further replies.

Reply to Gas pipe extension 15mm or 22mm (from a 28mm supply). in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
481
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...