Not getting much joy in the GSE closed forum so thought I'd start a thread here in the open ...
Boiler as above, 4yrs old. No issue with gas as there is plenty when working on hi setting. FGA hi & lo both 9.3% Co2 Exactly, Cleaned out condensate trap, just in case and also checked the sump is clear. Whilst there you could hear the boiler attempt to light, on some occasions 1st attempt others 3rd or it would fail to detect the flame all together and F1 ---- I though I'd cured it as the connection to the spark gen was loose, however it came back today F1 again ... :sad_smile:
My next step is to renew the spark electrode but it's a mare to get at! Horrible boiler to work on !!!!! Anyone worked on these with a similar problem? This is the first I've had to get involved with regards ignition/detection and I'm not looking forward to removing the burner ..... :veryangry2:
Any advice would be appreciated ....
Boiler as above, 4yrs old. No issue with gas as there is plenty when working on hi setting. FGA hi & lo both 9.3% Co2 Exactly, Cleaned out condensate trap, just in case and also checked the sump is clear. Whilst there you could hear the boiler attempt to light, on some occasions 1st attempt others 3rd or it would fail to detect the flame all together and F1 ---- I though I'd cured it as the connection to the spark gen was loose, however it came back today F1 again ... :sad_smile: