Discuss does gas hob need rigid connection? in the Plumbing Jobs | The Job-board area at PlumbersForums.net
bluesky
hi all, i am in training of gas safe, one plumber told me that gas hob should use rigid pipe, i know gas cooker can use flexible hose for connection but really not sure about gas hob...
cheers
it actually says in BS6891 that a flexi can be used unless otherwise stated in the MI that a rigid pipe must be used, it further expands that if a flexi is allowed it needs to conform with BS691 (I think it is this one) which says the flexi should not come in contact with a surface over 70 degrees C or subjected to damage from drawer runners etc
Here it is:
BS 6172
11.1.3 Unless stated otherwise in the manufacturer’s instructions, a gas hob shall be connected to the
termination point by a rigid fixed connection.
11.1.6 Where rigid pipework is used, an isolation valve with means of disconnection shall be provided.
rigid yes cooker hose no for a start it will be unlikely it can hang in a loop,secondly if its a built in oven under the hob it will touch it and melt and its so rough its like cowboy territory so cooper with a gas quality isolation valve the ONLY way to do it
the thing that amazes me is were suppose to keep wires away from gas pipes and on a hob they are allowed to come out adjacent they should be on opposite side of the hob
Kirk is using a different British Standard when he says "it actually says in BS6891 that a flexi can be used unless otherwise stated in the MI that a rigid pipe must be used,".
I think that I will stick with BS 6172 as thats in line with my recollection and I dont want to leard new tricks unless its absolutely necessary!
Tony
Tony
it is a typo by me, the quote is correct but as you say it is from 6172, (BS 6891 is for installation pipework)
Reply to does gas hob need rigid connection? in the Plumbing Jobs | The Job-board area at PlumbersForums.net
Im fitting a kitchen in my own house . When removing the gas oven on a bayonet fitting and turned the gas hob off and removed a four burner gas...
  • Article
Hi, I’m changing my kitchen and swapping from a gas hob to an electric induction hob. Rest assured, I have no intention of doing any work at all...
Hello I’d like to replace gas cooker. Curry’s do install but I know they will refuse to install if regs are not met. So I want to understand...
Hi, I’m having a gas cooker pipe capped off. The GS registered plumber/ fitter, has told me that to do this, he’ll also have to service the combi...
