Is there anyway of testing electrically with a multimeter or any other way. Of testing that when you turn a room stat up it is creating a demand and opening the zone valve? Thank you
 
S_plan_wiring_diagram.gif


  • Call for demand on the programmer and the room stat down
  • Turn your multi meter to 600~ or what ever is similar. Put one probe into terminal 3 and the other into terminal 5. You should get 0 on the meter
  • Turn the room stat up. You should now get 230-240 on the meter. If you don't the room stat isn't working or the test was incorrect.
  • Now put one probe into 10 and 3. You should still get 230-240 on the meter. If you don't the valve isn't working
  • To confirm you've done the above correctly, turn the room stat down again and testing 10 and 3 you should get 0 on the meter

We've skipped a load of steps to start with, If you don't know much about electrical diagnostics I would start from the beginning and confirm the fused circuit and programmer are all working first.
 
240v on the orange to blue or green/yellow earth wire
 
Yes
 
You need to test AC (alternating current) on brown and blue to the valve when the call for heat is there. They are live and neutral to the motor. I would check the live to earth too. The grey is permanent live into a micro-switch and the orange is switched live from the micro-switch to boiler/pump etc.

Using Ohms, you can test the resistance through the synchron motor inside the valve. They can be replaced if it is that. It does not matter which wire off the motor is live or neutral.
 

Reply to Controls and zone valve in the Plumbing Zone area at PlumbersForums.net

Similar plumbing topics

I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
192
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
252
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
189
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock