After some thought as to whether the towel-rail substitute for an ABV was the right long-term solution, I decided to replace the Honeywell DU144 pressure-driven ABV by a Caleffi Autoflow 127 from Altecnic that limits bypass flow to 0.2m3/hr (the boiler’s recommended minimum).
The Grundfos UPS2 25-80 pump was then switched into the lowest of the three proportional-pressure modes. With all the TRVs (now including the towel rail) almost shut on hot days the pump should be running at a head of just over 2m and the system is very quiet, but it heats up as quick as ever on cold days.

The Caleffi valves are about £10 more (plus a couple of BSP-to-compression adaptors) than Honeywell ABVs but should be the right solution, whereas in my view the Honeywell (and any other pressure-driven) ones aren’t.
 
I decided to replace the Honeywell DU144 pressure-driven ABV by a Caleffi Autoflow 127 from Altecnic that limits bypass flow to 0.2m3/hr (the boiler’s recommended minimum).
So now you have a continuous flow through the bypass, even if it is limited to 0.2m3/hr. o_O

Grundfos recommend a Taconova Setter valve (does the same job as a Caleffi) in series with the ABV. The bypass then only opens when the pressure exceeds the ABV setting and the flow is restricted by the Setter if the pressure rises.
 

Attachments

  • BypassCommissioningAlpha2or2L.pdf
    167.4 KB · Views: 9
IMO, to satisfy a PP1 setting of 2.0 M above then the ABV setting would have to be set as low or lower than this to give any flow if all zone v/vs, TRV's etc are closed, then as the heating demand increases the Tacosetter will restrict the flow rate which would otherwise be enormous using the ABV on its own, also I thought the tacosetter is more or less a adjustable fixed setting with a flowmeter and is not automatic so, for example if its set to flow 0.2M3/hr @ 2M head then if the heating demand increased to require a PP head of say 4M then the flowrate would increase to almost 0.3 M3/hr whereas, theoretically anyway, the Caleffi will maintain 0.2M3/hr even if the head increased to over 20M(200 kpa).
 
Re John.g's reply: spot on!
I was writing identical comments but was beaten to the draw.
The underlying problem is that a pump such as any in the Grundfos domestic range running in proportional-pressure mode has its lowest pressure at lowest flow (or no flow) - typically when all the TRVs shut on a hot day or when there the CH + DHW demand ceases and the boiler tells the pump to overrun for a few minutes. A pressure-driven ABV set to this pressure will simply open all the time.
And when I looked at the Tacosetter's tech spec, it appeared to operate as a fixed valve with a flow meter. Perhaps the flow set-point is resilient to pressure changes but this wasn't obvious from the spec: perhaps someone more familiar with them can correct me.
 
Re John.g's reply: spot on!
I was writing identical comments but was beaten to the draw.
The underlying problem is that a pump such as any in the Grundfos domestic range running in proportional-pressure mode has its lowest pressure at lowest flow (or no flow) - typically when all the TRVs shut on a hot day or when there the CH + DHW demand ceases and the boiler tells the pump to overrun for a few minutes. A pressure-driven ABV set to this pressure will simply open all the time.
And when I looked at the Tacosetter's tech spec, it appeared to operate as a fixed valve with a flow meter. Perhaps the flow set-point is resilient to pressure changes but this wasn't obvious from the spec: perhaps someone more familiar with them can correct me.

Could this be Honeywell's answer to the Caleffi?.
 

Attachments

  • Honeywell Balancing valve.pdf
    2.1 MB · Views: 7
Sorry I’m lost why is this a problem if you don’t want a bypass valve install a bypass rad eg airing cupboard

Depending on the sys it’s more to go wrong and service it’s only a domestic system
 

Reply to Constant flow automatic bypass valves in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
190
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
219
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
554

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock