Hi guys, I’m in the process of ripping out an old one pipe system and replacing it with a two pipe, feed and return. The new system will be on two zoning valves one for upstairs and one for downstairs.

Originally i wanted the system on a single stat and single zone valve... with a flow of 0.477 l/s and a 3.9m head loss (excluding loss over the boiler) I was going to use the Grundfos Alpha 1 as I liked the idea of balancing the system from the mobile app (potentially a time saver) and the option of auto adjusting flow rate as the TRVs close.

I’ve since changed my mind to a multi zone with upstairs and downstairs on separate zone valves and wondered if the same pump would be able to adjust flow automatically when the zone valves close.

If I go with the two zones, at the pump the flow is still 0.477 l/s but of one zone valve closes, the upstairs loop has a flow of 0.22 l/s with 1.5m head (excluding boiler) and the downstairs loop has a flow of 0.25 l/s with a head loss of 2.1m. Would the alpha 1 be able to reduce the flow rate enough to keep the return temp to the boiler the same no matter which valves are open or closed?

Thanks
 
Thanks for the replies...

In terms of piping it's a vented S-plan system with a 24kW Worcester Greenstar Ri boiler. There's a bypass (gate valve) fitted which I hoped would maintain flow when the zone valves close.

I was hoping to add an additional zone valve in parallel with the existing CH valve? Would I need a low loss header/close couple tees for this to work?
 

Reply to Circulating pump for Multi zone? in the Plumbing Zone area at PlumbersForums.net

Similar plumbing topics

Afternoon Fellas If anyone has time to help with this snag it'd be much appreciated. We have a wet-floor system controlled by John Guest UH3 and...
Replies
2
Views
501
I have an older gas boiler HW heating system with a taco circulator pump for each zone that worked fine last season. When turning it on for the...
Replies
4
Views
480
A bit of clarification - I have extended a 3 bedroom semi detached and at the time central heating pipes were going in I told the plumber could I...
Replies
0
Views
481
Hi. A new house regulation for a 2 zone heating system because it's bigger that 150sqm. I'm I right in saying zone 1 should be all of the...
Replies
10
Views
2K
Hi all, Hoping to check if I have a genuine fault, or something I've overlooked. I've just moved into a my first house with a conventional...
Replies
5
Views
924
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock