Discuss Central heating pump in the Central Heating Forum area at PlumbersForums.net
The above makes no real sense either as the temperature keeps rising when the burner is apparently off.
What signal/indication are you using to tell you that the burner is firing or not?.
I would suggest monitoring the burner firing time (boiler on/off) by watching the flame actually coming on/off in the viewing window and monitoring the temperatures.
I would also suggest that you do the above on the UFH(s) and monitor the manifold flow temp (which I don't think you have been) and note the total flow as per the flow tubes, the UFH output can then be cross checked reasonably well by using the % boiler cycle firing time. The manifold temperature gauges should also give reasonably accurate temperatures.
Is this manifold plumbed correctly?.
I monitored the boiler exactly how you suggest. I will do the manifold today, it’s very confusing as to why the temp rises when the flame is off.
It sure is, and the other puzzle is that Laundry manifold (the good one?) above which seems to be sending mixed water temperature back to the boiler, also the pump is connected between the UFH cold return and the manifold flow, the troubled manifold is plumbed the normal way like below.
The troubled manifold was plumbed the same as the laundry manifold until 4 weeks ago, we changed the pump set. We are going to replace the laundry pump set the the same as above as well.
Ok I’ll have a look, thank you
Well I have watched the flow and return on the manifold after the mixing valve which was set to 42 degrees, I found the flow going into the manifold reached 52 degrees. The boiler fired continuously for the entire 2 hours and 25 minutes. As far as the flow rates through the circuits were 5 @ 3lpm, 3 @ 4lpm, 1@ 2.5lpm, a total of 29.5lpm. As per attached photos the flow meters were turned down low but still showing extreme flow through them. (Sorry about the sideway photos)
Very good, all adds up thermodynamically any way, S.sheet shows boiler output of 24.7kw, almost flat out, hence constant firing.
Suggest throttling hot water before the manifold to see if mixing temp drops, this would then point to excesss boiler feed pump pressure and/or reduce manifold pump to speed 2, at least that will point you, hopefully, in the right direction.
So the o
Thanks John you are very helpful. So our boiler originally 35kw was fine and didn’t need to be downsized at all. If it’s firing ar 24.7 kw with the Troubled manifold it clearly isn’t going to run the 2 x UFH manifold/circuits, 15 radiators and 28m of trench, in fact I wonder when all of them are firing 35 kw was also to small as well.
Yes but remember you don't have any control
Over the heat output of the UFH since you have no control of the mixing temperature, this will have to be sorted out.
The pump set is only 3 weeks old are you suggesting the mixing valve could be faulty? Hence the water entering the manifold at a temperature higher than the set value?
Possibly but unlikely, the boiler circ pump pressure though at 1.4bar or whatever may be preventing it from operating correctly which is why I suggested throttling it somewhere. Most boiler circ pumps will only be running with a head of 4M (0.4bar) or so. I throttling it works, re install your old pump.
Yes I agree re installing old pump, I will try throttling the pump back again and also turn the manifold pump back to 2, it’s currently set on 3. I must admit the floors are heating up better with the new pump set as opposed to the pump set on the good manifold. John thank you very much for all the information you have supplied to me. To balance a ufh manifold is it only done with the flow meters, or can you slow the return water?
I wouldn't reduce the flow rate excessively as the loops are parallel circuits and you want to keep the flows equal, temperature control is the way go INO.
temperature reduction/control is the way to go O
Hi John, well I have throttled back the boiler pump to 1 bar and the manifold pump to speed setting 2 and I achieved 65 degrees flow, and 49 degrees return at the boiler and 45 degree flow through the manifold and 35 return. The boiler is cycling though of 15 mins on 1.15 mins off. I feel we are getting somewhere 🙂
Numbers not adding up there as the boiler return temp should be the same as the manifold return temp at 35C (assuming UFH only on)
Hi John I thought that as well, yes underfloor only on, once the manifold was up to temp would the excess water return back to boiler, making the boiler return higher? I did notice however that with the boiler thermostat set to 60, the flow did get as high as 70 at one point. I see there are two ports on either side on the top of the boiler ther thermostat probes are in the left, I am picking that has actually been set up correctly.
Maybe this TMV is sending mixed flow temperature water back to the boiler?, I always thought it was supposed to be the UFH cold water return.
The boiler thermostat should control the flow temperature at whatever setpoint its set to.
Did you check that the boiler flow and return pipes are installed correctly?.
interesting you say that because yesterday the laundry manifold had a flow of 60 at the boiler and returning 59, and that water has to travel 55m there and back.
I checked the flow and return out of the boiler, and the seem to be ok.
Another thought I’ve just had, I think this boiler is way undersized even at the original 35kw. This diesel boiler replaced a 26kw gas boiler which ran all the rads and trench heating and replaced a 16 kw heat pump that was to small to run the underfloor heating, hence why we decided to change. Is there a formula to work out what size boiler one would need.
We already know that when the troubled manifold is on it needs 24.7kw.
What’s the flow rate of all the zones on this manifold ?
Which is 4kw required so very strange why it needs 5 x that
Something definitely very strange, I get a UFH heat output of 5.8kw at your flowrate of 8.3LPM and dT of 10C which should only result in a boiler flowrate of 2.77LPM at a boiler return temp of 35C., the measured return is 49C which means that 2.42LPM at 65C is either bypassing through the TMV or through a external bypass to give a boiler return flow of 5.2LPM. But the boiler is outputting ~ 24kw based on your burner cycling times, you may be losing up to 5kw in all that pipework if uninsulated but still wouldn't remotely account for that boiler output, the only logical explanation is that there is another zone (maybe rads) on as well, taking the few temperatures I suggested will show if the TMV is by passing but will not explain the very high boiler output.
I’m with you John it is very strange. All pipe work is insulated, we have doubled checked the flow and return today and all seems ok. There is an external bypass on the boiler but nothing seems to be flowing through it, as the pipes are cold. I wonder if it because of the stupid pump setup on the laundry manifold it’s bypassing and going back to the boiler. I’m about ready to rip the whole system out 😂😂😂 I really can’t find an answer.
Bypass on its own shouldn't increase boiler demand,
Can you just run on DHW demand only and see what kind of cycling and flow/return temps you are getting.
Also ensure you check those manifold temperatures sometime.
Ok, I’ll go do that now. I have turned the manifold temperatures down like you suggested yesterday. (Is that what you mean)
No, the next time the troubled manifold is on check the temperatures where highlighted with the heat gun as suggested in post 69, we can then see if that TMV is bypassing.
Ok, yes i wil do that. Well I ran the DHW system and this was the result
But also while I was standing there, I think I've discovered the problem. We have two pipes running from the boiler to the gas boiler as the radiators are piped to work on gas if something happens to the boiler. On further inspections these flow and return pipes are exceptionally hot, and the DHW is in the complete opposite direction. As you can see from the photos there are 2 valves but these are only shut if the rads are operating by the gas boiler. So it would seem we have flow going along these pipes circulating into the gas boiler, and heading back to the other boiler. This is a 28m loop
( I do hope that makes sense ) This would also explain why the boiler return temperature is higher than the manifold return temp.
Can you shut those valves temporarily and put a note on the gas boiler to that effect and see how the UFH operates.
Can't see attachment 76410 re DHW.
Yes I can shut those valves temporarily, if the rads call for heat off this troubled boiler they use those pipes for flow and return, both boilers can not operate at the same time. The gas is purely for backup.
Attached DHW graph
If you mean that the boiler ran continuously for 45.37 mins then its output was ~ 19.7kwh and if all that energy was inputted to the hot water cylinder then the cylinder volume would need to be 846 liters to only rise by 20C, not likely, if the HW cylinder is say a more realistic 250 liters then it would only take 5.81kwh or 13.5 min to rise it by 20C. still not clear as to what's going on but with these valves now closed then it may be become clearer.
No boiler didn’t run continuously, the blue on the graph is where the flame stops but the pump still runs to circulate the water, the boiler only fired for 29 mins 38 seconds out of the 44.37 mins (sorry was not clear on my outcome)
There’s a set of valves on the boiler so worth a test
Hi John
I run the troubled manifold with the rad valves turned off and the boiler return temp was exactly the same as the ufh manifold return temp. Although the boiler ran continuously for 42.07 mins and only got to 59 degrees. The manifold points you told me to measure were spot on, so the TMV is doing it’s job. I now believe the pump set to constant pressure and being such a big pump is another issue, as water was also bypassing through the external bypass.
As you can see the Rads literally T into the flow and return so no valves to stop the flow of water, with valves turned off water was still flow the this point in these pipes.
Reply to Central heating pump in the Central Heating Forum area at PlumbersForums.net
Hi Everyone I wasn’t sure whether to post this in here or UFH but hopefully I’m posting this in the correct group. I’m in the throes of a full...
Hi, I am replacing our 11 year old boiler (due to H.Ex. leak) with a new one. This is in a "sealed" system with red expansion vessel in airig...
My central heating is run off a heat pump ( air to water ) quite expensive to run , So I’m plainning to fit a wood burning with a back boiler to...
Hi All, Looking for a bit of advice on the best way to pipe this. - 24kW Worcester regular boiler in kitchen, approx. 9 years old - unvented...