Not open for further replies.
Messages
110
hi,

Ok so have a 4 bedroom house.

Vaillant System boiler 637

No rads just underfloor heating. 3 x manifolds and nothing too big.

UV hot water tank.

Client complained that UFH has never worked properly.

I found system to be surprisingly dirty. Pumps knackered.

I replaced all manifold pumps, pump on boiler, removed actuators, replaced balancing valves and flow meters. Through all of these steps it always produces a new problem.

The issue I have is that the boiler keeps cutting out. Apparently it’s noticibg to small a differential temperature on flow and return. I’ve added a bypass to system which hasn’t helped. It will ramp up to 70 when asking for 60 and cut out. There’s no restriction on the system and Vaillant can’t give me an answer. Seems as though heat exchanger ok, but thing won’t stay lit. I’m at wits end. I understand that UFH has never known to work by client so I’m in the clear there but really do t want them to spend all this money and I can’t get it up and running. If anyone can help me brainstorm this one I’d be much appreciated.
 
Boiler is to big how is it piped a low loss header ? you could try down rating the boiler its in the installation manual how to do this or ring Valliant technical they will talk you through it i would try 24kw this is enough . Do you have zone valves and a auto bypass valve at the UFH manifolds the heating load needs somewhere to go even if it modulates right down the boiler needs the facility for pump over run , sounds like a design fault put some pictures up bud .Cheers kop
 
:(Note to one self, read OP’s post properly
 
Last edited by a moderator:
What make is the manifold, in fact pictures would be better.?

Lots of pics, pipework at boiler any valves, manifold etc.
 
Hi,

Have tried down rating at quite a few different kws. Currently at 12kw but no help.

It’s a polypipe manifold and have spoken to them but no help.

Hot zone valves at each manifold. 1 bypass internal to boiler and additional bypass near to boiler.

Will try and attach some pics on laptop when I get home as can’t work it out on phone.

I was thinking low loss header the only way forward but really want to give customer a difinitive answer.
 
Does it look like this manifold?

828939D0-89D3-4F79-8239-108076AF417E.png
 
If it does, have you removed the filter from the top and checked for debris?
 
Status
Not open for further replies.

Reply to CANT GET UFH to work!!! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
311
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
391
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
217
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
218
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
235
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock