if its a 24kw boiler and you get that gas rating it and the fga checks out ok ? why then do you need to do burner pressure ?
 
so you are assuming that the person who fitted the boiler in the first place did so correctly? personally i would assume nothing.
 
I had one today Worcester 240 RSF. Screw for burner pressure wouldn't turn and as I have a habbit of snapping screws I was reluctant to force this one. No MI, I'm sure the boiler is a 24kw but the heat input is 30kw for DHW. Gas Rated this at 29kw, FGA 0.0007. Working pressure. Seals, flame picture and burner insulation all good. I had a cooker and a boiler it took me 1.5 hours is that normal for a landlord certificate 2 appliances. Or am I just slow?
 
its around 10mb for 24kw boilers aint it ?
Guessing/assuming is not good enough as far as I am concerned. Off top of my head a Worc. 24 CDI BP is 13mbar to name but one.

Ideally,(although rarely carried out) it is good practice to do BP & Gas Rate where possible. How do you know the correct injector is in place otherwise. It is possible to have an LPG nozzle not been swapped for a gas one or vise-versa. Doing a Gas Rate and BP would indicate this as the readings would not tally up.


As others mentioned, unless you know the appliance settings, in the absence of a data plate, MI's or info from manufacturer you should not be carrying out any work on the appliance. Simple as that.
 
1.5 hours for cooker and boiler , took me about hour and quarter to do each boiler service today not sure if thats slow but then i'm usually install. As far as i'm concerned working with gas isn't a race rather take my time and double check again if not sure .
 
Well if there is a gas meter with pipework leading from it to the boiler, I'm happy to assume its Natural gas. If the boiler case states "Joe Bloggs 24 cdi" for example, I will then ring the "joe Bloggs" tech line and confirm the appliance and ask for the burner pressures which I will then check and adjust accordingly. Simples.

ive seen lpg water heater connected to natural gas
 
Status
Not open for further replies.

Reply to burner pressures in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going...
Replies
1
Views
318
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason...
Replies
3
Views
335
Fitted unvented hotwater cylinder building control looking forms signed it off job was in england i am qualified northern ireland send out a form...
Replies
4
Views
231
Our kitchen mixer tap has started dripping. Like so much of the plumbing in our almost new build bungalow, it is lacking! The plumber didn't...
Replies
12
Views
432
Hi, I have an old steel water mains pipe (approx 45mm) that I need to connect to a new pehd water mains (25mm). I can't get at it to create a new...
Replies
2
Views
241

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock