Hi guys,

I installed a ideal logic for my grandparents, I've installed loads of them and never had an issue. Unfortunately for me, my grandfather is complaining it sounds like a train coming through the house ( maybe a slight over reaction lol) but to be honest i can hear the boiler running from downstairs in the living room, which is directly beneath where the boiler is installed. I would say its the pump or the water flow that can be heard more than anything. Don't get me wrong, it's not ridiculously bad, it's just it can be heard slightly louder than it should. Normally I can't hear a thing!!

any ideas what could cause this? I worried it may be cos I didn't clip the pipes as much as I normally do. Only reason for this was because the pipes where all in the wrong positions ( old ferroli used to be there instead) and I could have clipped it as much as I wanted as the pipes wouldn't of gone in the clips due to the wall being all over the place

any advice appreciated
 
Last edited by a moderator:
Is it when the boiler is firing or also when its just pump over run?
Was it the same with the old boiler?
Any pipes hitting floor boards/joists?
If you hold the flow & return does it stop?
 
Have them post up in the i'm looking for a plumber section to get a reputable forum member to come take a look....


;)

no valves on the main flow or return? Anywhere?
 
Fit a bypass below boiler adjust to remove noise. Did have one tho with vertical flue sounded horrific was gas valve.
 
Thanks for the info guys, will double check the obvious things and rebalance rads

What 'clips' do people use when walls are uneven to ensure pipes are nice and neat?
 
Well guys, boilers still that little bit to noisey. Had another look today. I think I need get those pipes clipped as best as possible as that may help a bit but after a search on google it seems it's a bit of a common problem. It's seems to be related to the pump speed, so I fired the boiler up and disconnected the pump and long behold the noise stopped. Now I don't think it's a noise from a faulty pump, just seems the pump is running at full sipped and there's no way to turn it down. I've opened all the rad valve fully (lock shield and trv's) and it's still the same. The pump must be well over powered as even with all the lock shields open, all the rads in the house are getting hot whereas before with the isar installed (yes I know lol) I had to balance the rads to get the heat downstairs. Btw the heating system has 10mm to all rads

ideal are coming out Friday to take a look but I really don't see what can be done. I've read something about putting a new variable speed pump in there instead but I'm guessing that will void the warranty plus it'll cost more money, also read about putting in a auto bypass to curb the noise

what do you think? Can't believe I've took an isar out and the boiler I've replaced it with is worse in the customers mind.
 
I've read something about putting a new variable speed pump in there instead but I'm guessing that will void the warranty plus it'll cost more money, also read about putting in a auto bypass to curb the noise

Let Ideal engineer worry about that. It is their responsibility to sort it out.
BTW, your grandparents are not customers, they are family :D
 
I've read something about putting a new variable speed pump in there instead but I'm guessing that will void the warranty plus it'll cost more money, also read about putting in a auto bypass to curb the noise

Let Ideal engineer worry about that. It is their responsibility to sort it out.
BTW, your grandparents are not customers, they are family :D

Haha, definitely family cos I get paid for fitting a boiler from customers. Not the case when it's family :-(
 
I fit these boiler & I've had 2 similar problems

1 was a faulty ideal RF room stat / programer telling the boiler to go in to 'pump over run' non-stop, ideal changed the RF room stat & pump.

2 was at my grandparents, sounded like the boiler was fitted with a dump-valve, that was a faulty gas valve. Ideal engineer said sometimes a big moth or spider can get stuck in the flue / air way's, allowing poor air / gas mix.

Both problems was sorted by IDEAL, both boilers working fine now.
 
We'll guys, ideal engineer came out, seems it is the fact that the pump is too powerful and the fact it's on a 10mm piped system is making it worse. Had a good chat with him about options but he did say as of next year, all boilers will need to have modulating pumps so should solve these issue but could make things worse.
 
If the system is not very clean, then it would make it a lot worse. Any build up of sludge in the system & it will make the pumps play up.

Thats the way I understand it, how true I'm not sure. But I know with a heat only set up, when I've fitted the new style of pumps & the system is dirty they seem to play up a bit. Taking longer to heat the rads etc etc.

What use to be a quick pump change could now be a power flush before hand
 
Status
Not open for further replies.

Reply to Brand new ideal logic plus install - boiler can be heard in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
I've got a 2016 Logic PLus Combi 30 and a Salus RT505TX RF Thermostat The thermostat seems to keep losing connection, no matter the placement. It...
Replies
4
Views
785
Hi, As per the thread title, I have an Ideal Logic Combi 30 and I am having a problem with the pump, which keeps activating without any DHW/DCH...
Replies
2
Views
1K
Hello All, I was hoping you could help with a potential boiler build query for my father. He has recently had a new boiler installed via British...
Replies
5
Views
280
Hi, I am replacing our 11 year old boiler (due to H.Ex. leak) with a new one. This is in a "sealed" system with red expansion vessel in airig...
Replies
3
Views
566
Hi. I have an issue with my Ideal Logic+ System S24 boiler which I hope someone can help with. Below is as much detail as I can think of. The...
Replies
4
Views
1K
Back
Top