rizz077

I have an interesting problem with Baxi Eco80 boiler which i inherited when i moved into my flat a few month ago.

At first i thought it was the thermostat so i recently replaced it with a 3rd Gen Nest. However its evidently not the thermostat.

Problem occurs when the boiler has been idle for a long time i.e both CH and DHW have not been running.
When the thermostat kicks in, i can hear the pump running but no flame ignition. The problem seems to be resolved only by turning on a hot water tap after which the flame ignition sequence seems to work just fine and the CH system fires up.

Once the system is running it seems to be able turn off and on (as demanded by the thermostat) however if left off for too long the same problem occurs.

I have checked the system pressure is set correctly to 1.5 barg,

Ay idea what the problem could be?

location GU15 postcode
 
Last edited by a moderator:
If interested please pm the op directly.
 
Last edited by a moderator:
Status
Not open for further replies.

Reply to Baxi Eco80 wont fire CH unless i turn on DHW tap in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
257
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
391
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
247
P
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
518
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
282
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock