Hi Guys

I had UFH added to my extension, my system was a Baxi 30he with CH and unvented cylinder.

The UFH has never really worked correctly first of all I noticed they had install the flow and return the wrong side of the circulation pump which I rectified myself as they have disappeared on me. The UFH now works but I have noticed an issue that if the CH is not running the boiler cuts out if the UFH is calling for heat. If the CH is running then the UFH runs fine, I’ve been searching online for diagrams


Do I need an auto bypass valve on the flow and return after the circulation pump ? At the moment the circulation pump is in the loft and the boiler on the ground floor about 8m away and all my rads have TRV fitted?
 
What temperature is the boiler set to, the UFH manifold (flow) temp and what is the UFH return temperature, if known?.
Also boiler make/model.
Edit: See its a Baxi 30he
 
Last edited:
You will find the ufh heat load is less than the boiler min load so it will cycle two options use a buffer or llh/ccts
 
That boiler has a minimum output of 11.9kw so will definitely spend a lot of time cycling with the UFH only on.
A LLH or some form of bypass won't prevent this but will reduce the dT across the boiler, with no by pass and assuming boiler flow temp of 70c with UFH manifold of 45C/35C then the boiler dT is 35C, a boiler flow temp of 65C will give a dT of 30C and 60 will give a dT of 25C, the boiler may not have a dT trip.
 

Reply to Auto bypass required ? in the The Welcome Wagon :) area at PlumbersForums.net

Similar plumbing topics

I recently had a new 2023 Vaillant ecoTec plus 630 (30kW) system boiler installed along with a Low Loss Header (LLH) in my house. I have 21 rads...
Replies
10
Views
819
Do people with this type of mixed flow temperature control have any problems with achieving the required manifold flow temperature? The one below...
Replies
3
Views
720
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
208
Hi We have had a LLH installed after major issues of UFH robbing heat from CH. now installed want to ensue working as expected. All 3 systems...
Replies
16
Views
1K
Good morning, wondered if anyone can advise please on a resolution? My set up at home is that I have a 4-bed detached with 21 radiators...
Replies
61
Views
5K
Back
Top