Just prior to removing the rads you might consider (with boiler shut down) shutting off the valves on one of the downstairs rads, remove the vent complete or if installed, the plug at the other end, open one isol valve fully and let the water flow into a container for say exactly 10 secs (but no longer than 30 secs) and measure this amount, shut off this valve and repeat with the other valve open and compare measurements, before commencing each test, top up boiler pressure to exactly 2 bar, this test may show if the problem is either a blocked flow or a blocked return, but not guaranteed if the bottom of the rad is full of sludge. If a open vented system test time can be 30 secs or so.