Discuss 13,333 btus off 15mm pipe. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
Messages
910
Hi I am putting the pipework in for a heating system and am left with 3 rads to pick up with 13,333 btus of heat needed for this 3 rads. After the last rad on the circuit before these 3. Is around 4 meters, I have ran 22mm from there. I plan on reducing down to 15mm around 300 mm before picking up the first of these 3 rads. Should that be ok?
 
If temperature difference across rad (Delta T) is 11C then you are within margin for 15mm, but for the sake of extra 300mm ,why not take 22mm to tails of first rad. then larger or extra
rads could be added in future.
 
No it won't simple answer
 
If you've ran 22mm for the rest of the system, why not just keep it that way, why create future problems with a system you've put in from brand new?
 
can we please go metric or imperial and stop mixing it up, poor brain can't cope
 
My old fashioned pipe limit on open vented is 20,000 btu on 15mm pipes.
That said, I would always try to have maximum only on very large rad coming solely from 15mm pipes.
Do no harm to take 22 mm to the last tee branch off for last two radiators unless they are very small rads. Better to be looking at it, as looking for it, as the saying goes, - especially when the customer decides later to add a little extension
 
can we please go metric or imperial and stop mixing it up, poor brain can't cope

Simple conversion:- 1litre weighs 2.2 lbs 1 degree C = 1.8 degree F
Therefore to raise 1 litre by 1degree C requires 2.2 X 1.8 BTUs Approx 4 BTUs for sizing purpose. The metric energy system of a Newton force for 1 metre does not have the same simple direct relationship with mass of water and rise in temperature.
 
No it won't simple answer
?

If temperature difference across rad (Delta T) is 11C then you are within margin for 15mm, but for the sake of extra 300mm ,why not take 22mm to tails of first rad. then larger or extra
rads could be added in future.

Where as if you designed at 20deg C difference (so 70 Flow & 50 Return as you should) then a 15mm will p*ss it = 11kW, which I think is around 37K of them very out of date, pre decimal thermal units, that are so difficult to work with. :6:
 
Dividing output in BTUs by 4 X (Delta T) to get flow in litres per hour is all my pre senile brain can manage.
 
If temperature difference across rad (Delta T) is 11C then you are within margin for 15mm, but for the sake of extra 300mm ,why not take 22mm to tails of first rad. then larger or extra
rads could be added in future.
So carry on in 22mm to the first rad of the 3, the reduce down to 15mm to pick up the final two rads with a btu rating of about 9000btu between them.
 
Would mostly likely use a 22mm,15mm,15mm tee to pick up this rad then go to 15m to the finale two.
 
Status
Not open for further replies.

Reply to 13,333 btus off 15mm pipe. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
189
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
243
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...
Replies
2
Views
252
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock