Hi,

I have a large three storey cold Victoria house and I'm having an extension being built which adds a large amount of additional volume to heat. The new space will be UFH and the existing heating system zoned to upstairs and downstairs.

The entire heating system is a single zone in 22mm copper tee'd off in 15mm to radiators. Currently have a 37kW Worcester combi (6 years old) which is being replaced with a Vaillant EcoTec 637 system boiler (+megaflo).

My builders have moved a ground floor riser in the kitchen and replaced about 5m of 22mm copper with 15mm plastic.

The upstairs of the house has always been much colder than downstairs and I've just accepted this. Do I potentially just need to be rebalance the system to fix this?

Since builder has moved the riser, some of the upstairs radiators are now lukewarm, but there is loads of air in the system and some of the radiators are so old they can't be bled so I think I may need to replace them.

Also noticed that if the boiler pressure drops to around 1.1bar then there is practically zero pressure in the highest radiator in the system (nothing comes out when I open the bleed valve, unless I add more water to the system).

I know the 22mm copper has about 3 times the internal pipe area than the 15mm plastic. Should I be worried this? If so, what would the effect be on the upstairs rads? Would this explain colder radiators?

Builder will replace the 15mm plastic with 22mm plastic(!) if I'm not happy but I don't want to waste time/money doing this if it will add no value.

Thanks,
 
Filled with dread at “my builder has done xyz” was a plumber involved? Who fitted your new boiler? Was the system flushed? Who fitted the megaflow, have they upgraded your mains feed and tested pressure and flow? Sounds like they have cocked up the pipework as 15mm and 22mm pipes will only be able to carry a certain kw. Sounds like this hasn’t been sized appropriately to accommodate the new House heating requirements. Sorry to sound negative but plumbers don’t build walls builders do hence why builders don’t size heating systems
 
None of the heating changes have been made yet apart from moving the riser. Its all proposed at this stage.

The heating engineer has seen the plans and the house and seems pretty competent and thinks that the EcoTec 37kW and a Super Oso cylinder is adequate for the heating and UFH.

However its the builder who has moved the riser as part of knocking through a wall - plumber / heating engineer not consulted.

I suppose what I am asking is will a 5m section of previously 22mm copper that is now in 15mm plastic have a noticeable impact on the heat output in the 9 radiators above it on the upper two floors?

Thanks.
 
Who designed the system??Without knowing the exact heating requirements above (room sizes, double glazing etc) I’d say it should be a MINIMUM of 22mm, personally I would get the heating engineer in NOW to ensure all pipe runs are adequate for your requirements. It’s a damn site easier to alter pipework now rather than when you are turning on the new boiler for the first time
 
Also has anyone tested that your mains is suitable for an unvented cylinder
 
Your builder has fecked it. Unless it was just a temporary measure to get him away. Builders and pipes don't mix.

Either way it needs to be changed back to 22mm copper.
 
Having a brand new water main fitted in 25mm MDPE direct off the 6" main in the street (asked for 32mm, but they said no). Am assuming this will be okay with the megaflo, but there is no way to tell. I'd be surprised if it wasn't.

The water main and gas main are both being replaced and every component on the heating/water system replaced so its impossible to know how it will behave. The only bit to stay the same is the existing pipework (22mm heating, 15mm hot/cold water) with the new hot and cold runs to the riser being in 22mm.

If I ask the builder to re-do the 5m heating stretch in 22mm plastic (which is about 25% smaller cross-section area than 22mm copper?) then I think he'd do that. He hasn't quoted for 10m+ of copper pipe in his quote which means I'll end up having to pay for it. No problem paying this unless the heat difference between the 22mm plastic/copper is marginal - definitely not cutting corners.

I did wonder whether the capability of the pump in the old boiler might have some input into the temperature of the upstairs rads.
 
I’d be asking the water board for some pressure and flow assurances. They should be able to provide you with rough figures. Likewise the plumber should be able to test pressure, flow and dynamic pressure so you know what you have currently. Sounds like a lot of finger in the wind to me.

How many bathrooms do you have/will you have?? As 15mm hot and cold seems undersized. This will be coming off the unvented cylinder so should really be run in 22mm prior to downsizing at sanitary ware. If you have a hot water demand over a number of floors then a secondary return pump on the hot water side would prevent a lot of wastage
I think you need to revisit the pipe sizing.
Again who designed the layout?
It sounds like this really needs some re-thought.
The pump in the old boiler could be an affecting factor although heat does rise.
 
Last edited:
Separate pumps for each zone and the plastic will be throttling the heating more than you think due to the inserts in the pipe.

Don't get the builder to do the pipes get the plumber. Tell builder it's coming off his Bill for screwing it up.
 
SO who planned the new layout?
 
Having a brand new water main fitted in 25mm MDPE direct off the 6" main in the street (asked for 32mm, but they said no). Am assuming this will be okay with the megaflo, but there is no way to tell. I'd be surprised if it wasn't.

The water main and gas main are both being replaced and every component on the heating/water system replaced so its impossible to know how it will behave. The only bit to stay the same is the existing pipework (22mm heating, 15mm hot/cold water) with the new hot and cold runs to the riser being in 22mm.

If I ask the builder to re-do the 5m heating stretch in 22mm plastic (which is about 25% smaller cross-section area than 22mm copper?) then I think he'd do that. He hasn't quoted for 10m+ of copper pipe in his quote which means I'll end up having to pay for it. No problem paying this unless the heat difference between the 22mm plastic/copper is marginal - definitely not cutting corners.

I did wonder whether the capability of the pump in the old boiler might have some input into the temperature of the upstairs rads.

I always thought that upgradinjg mains water supply needs to be signed off and certified? it also hast to be well insulated and installed at least 750mm below floor level
 
It does mate but they can dig the trench and run everything up to the connection in the street
 
It does mate but they can dig the trench and run everything up to the connection in the street
alright, i would have thought so. normally its very expensive if thr water board does it
 
Had to do 6 of them in one property recently
 
I always thought that upgradinjg mains water supply needs to be signed off and certified? it also hast to be well insulated and installed at least 750mm below floor level
The water board are inspecting and connecting at the street, and yes its a 750mm trench insulated as it enters the house through the foundation. Builder is doing all that for me.

SO who planned the new layout?
There isn't a new layout really. All of the new extension space is UFH (using VarioTherm). The extent of the works means a lot of localised pipe re-routing which is where my problem comes in. I can't do much about any of the existing heating pipework except to try to maintain appropriate sized feeds as it dissapears into the ceiling void.
 
What I’m trying to say though is that if you have radiators not warming correctly now then it’s the prime time to correctly design your system that will have to deal with a greater workload following the extension.
 
Thanks for the all of the replies so far.

I've requested pressure and flow data from the water board who have said they will make enquiries and get back to me.

What I’m trying to say though is that if you have radiators not warming correctly now then it’s the prime time to correctly design your system that will have to deal with a greater workload following the extension.

Sounds like good advice.

A couple of the old rads have historically not heated up well on the top floor. The system was completely drained to re-route the pipework and that can't have been done in years (I moved in a year ago). Most of the rads in the house are 40 years old minimum and the bleed valves don't seem to be working which means there is now air all over the system that is proving difficult to shift. Randomly though, highest radiator (a towel rail) is mega hot.

Builder thinks as a separate issue I should replace some/all of the older radiators for more efficient modern versions. I am wondering whether very old rads are contributing to the problem? Certainly I don't have any issues with the newer towel rails.

Another issue I currently have is that there doesn't seem to be sufficient expansion capacity on the system - its a Worcester 37kW combi supplying a lot of radiators without any external expansion vessel outside of the small one I assume is in the boiler, so it will randomly dump water out of the pressure relief valve dropping the pressure to around 1 bar which then means that the water struggles to get to the top floor. New system will sort out that one though, but unsure that this situation isn't also contributing.
  • Would replacing very old radiators potentially help?
  • Would a badly fitted combi with insufficient expansion capacity contribute to this issue?
  • Would a flushed-out system and new boiler potentially alleviate some of the symptoms?
  • Could a lot of this be fixed if I just got the heating engineer to balance the system?
Really appreciate all of the advice!
 
how many rads do you have totally ish?

and yes its best to replace any old rads when your redesigning the system

get the rooms individually heat lossed plus 10% and then size your rads on this

also rule of thumb no more than 2 1600 x 600 kw on 15mm this is a realistic figure

also sounds like you need to size the pump correctly to pump the water up 3 floors etc
 
Thanks for all of the replies.

Builder has agreed to replace the 5m stretch in 22mm copper with push-fit joints which I'm happy with. This is after a conversation with the heating engineer!

how many rads do you have totally ish?

also sounds like you need to size the pump correctly to pump the water up 3 floors etc

Looking at 13 rads of various sizes over 3 floors - mostly horribly old ones. That's existing, plus about 50m² of new UFH. Heating engineer thinks that a Vaillant ecoTec Plus 637 is sufficient for that based on a walk around the house and review of the UFH plans.

He's also proposed a Super Oso 250L for the cylinder.

Not entirely sure what he is proposing pump wise. Would more than the pump in the boiler be required do you think?
 
What floor is the boiler going on? Kw wise you should be ok. As I think was mentioned previously it might be better and more effective to pump each zone
 
What floor is the boiler going on? Kw wise you should be ok. As I think was mentioned previously it might be better and more effective to pump each zone

Currently the old 37kW combi is in the cellar and manages to pump up to the second floor with the internal pump. No external pumps or expansion vessels.

The new system boiler (and cylinder) will be a floor up on the ground floor which I assume should help with pressure drops and pump effort.

Will talk with the heating engineer about what he's thinking with the the zones. If zone pumps are in the mix, would that mean the pump in the boiler is just supplying the cylinder?
 
Your looking at needing around 18l of expansion

Also he should do a heat loss calculation as the cylinder will take around 15kw
 
Has the heating engineer done anything?
 
Has the heating engineer done anything?
Not really. He's walked round the house and kicked a few tyres.

I've suggested most of the stuff regarding new water main, new boiler location, moving from combi to cylinder.

I chose the EcoTec+ 637 and he confirmed that its up for the job and suggested the Super Oso 250L.

I completely trust his professional opinion ( assume he's told the builder he needs to replace the 22mm copper yesterday), I've just not seen much of him. My interface is with the builder.

When I see him I'll mention if he's planning two use two external pumps for the zones. He did mention that I could use a low-loss header but it might be overkill. He also suggested it would be expensive!
 
:D so basically he's done nothing and the builder has done the plumbing
 
:D so basically he's done nothing and the builder has done the plumbing
Pretty much! A red carpet is being rolled out for him to turn up to connect up the boiler, cylinder, UFH and my new gas supply.

The builder is doing the rest - he's been pretty open about that as its to keep costs down.

I suppose the the downside of that is that it cost less in general but then random costs extra when they make mistakes that I pick up on.

I've painted them in a really bad light, but they are a great dedicated bunch. They just aren't experts in plumber/heating.
 
That's the thing we have a lot of these builder doing the plumbing not many end up without problems / the systems don't work etc

My advice get the builder to do the building work and the gas safe engy / heating engy to do the pipework and heating etc
 
I am sorry to say it but I think you are asking for trouble if you let the builder do all the plumbing work. If they are talking about hanging the boiler etc then I would tell them you want a new gas safe engineer and for them to do all of the wet and gas. It is not worth you saving a couple of quid for the potential headache this could cause you in what is quite a major upheaval in your home. The fact that you say they aren’t experts in plumbing and heating set all kinds of alarm bells ringing with me have you checked their insurance coverage etc it’s just not worth it its your home after all
 
Last edited:
Status
Not open for further replies.

Reply to Effect of replacing 22mm copper with 15 plastic in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...
Replies
2
Views
253
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
207
P
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
481
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
140
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock