The more I investigate the system I have inherited I wonder who was employed to maintain it?
A couple of meters along the boiler output point is a pipe stat. A Honeywell L641B1004 which has a range of 10 to 40˚C, . I think what should have been installed is a L641B1012 which has a range of 50 to 95˚C. There is a frost stat nearby so assuming not meant to be another frost stat
 
Last edited:
What does the boiler supply/ heat ?
 
Is there any tees before the stat ?
 
Nothing at all leaves the boiler in 28mm stat is positioned about 75mm after a 90deg elbow which as mentioned before is about 2m from the boiler outlet.
 
Do you know if the stat is controlling the pump ?
 
Sounds like the correct pipe stat as it needs to be set at 25 C. Only thing is it should be on the return and within 600mm of boiler
 
  • Agree
Reactions: deg
Checked and found both are operating as frost stats. If either are switched on the boiler comes on but not the pump! All seems a bit odd as the two stats are literally a foot apart. So much for my theory that the pipe stat was an overtemp device.
 
Checked and found both are operating as frost stats. If either are switched on the boiler comes on but not the pump! All seems a bit odd as the two stats are literally a foot apart. So much for my theory that the pipe stat was an overtemp device.
The frost stat (which measures air temperature) and pipe stat (measures water temp and fitted to return pipe) should be wired in series. The boiler lights when the air temperature drops below the frost stat setting (5-10C). The pipe stat turns the boiler off when the water returning to the boiler reaches the set temperature (25C).

If there is no pipe stat, the boiler temperature will rise until the boiler stat operates - may be 80C. This would heat the house unnecessarily and be wasteful.
 
Well I reckon the pipe stat is stuffed as it does nothing. If I turn on the boiler by raising the frost stat up, so the boiler kicks in, the pipe stat can be set anywhere between the minimum 10˚C and the max 40˚C with no result. By my reckoning from what "doitmyself" said the stat must be shorted, or boiler would not fire. Finally is not 25˚C rather high, why heat the whole setup to this figure as a frost protection? Anyway my setup does not switch on the pump so seems to defeating itself!
 
Here is a wiring diagram showing how the frost and pipe stats should be connected. Use it to check your wiring. (Ignore terminal numbers - assumes Honeywell method - valve wire colours are the thing to follow.)

Don't forget that 25C is the temperature of the water in the pipe, not the air temperature. When the boiler is running for heating the water could be as much as 80C.

The frost/pipe stats should turn the pump on so the water circulates.

Could it be a DIY installation of the pipe/frost stat?

Frost Kit.jpg
 
Hi
Sounds very much like a DIY job, and a poor one at that. Having delved in found pipe stat wire in the terminal but covered in insulation tape, do not ask why, I have no idea either. System now seems to be working ok and pump now does run. Have copied your diagram for future reference. I never knew about the stat switching the boiler off, one learns something new everyday, many thanks.
 
Status
Not open for further replies.

Reply to Inherited system another anomaly! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Our kitchen mixer tap has started dripping. Like so much of the plumbing in our almost new build bungalow, it is lacking! The plumber didn't install any isolating cocks in the H&C feed to the tap so how can I identify which of the valves is passing? Shut the whole H&C water system down?
Replies
12
Views
338
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
189
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
231
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
472
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
178
PSxxxxxx
P
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock