It's not going above 42 degrees. Burners on. Have checked thermostat and it's working fine. It ramps up every now and temp goes to 50 odd and then ramps straight back down and temp goes back to 42...????
 
428 is a regular boiler
but any how, check thermistor value and see if it can be moved to gas safe only area
 
Can this thread please be moved to gsr only forum pppppplease???
 
Had this before on this exact boiler years ago but can't remember for the life of me how I overcame it.
Think it was something to do with insufficient difference between flow & return temps. These Vaillants can be too clever for their own good sometimes.

Try changing output (D0) from Auto to about 18Kw or 20Kw
 
Sounds like it's been adjusted to low output or something's if possible... or maybe a sludged is hex.?
 
Sounds like it's been adjusted to low output or something's if possible... or maybe a sludged is hex.?

I thought about the low output thing but the owners wouldn't have a clue how to do it.

Sludged is hex???
 
Yeah the vaillants are complicated, any chance the max flow was adjusted to 50 by mistake?

I meant sludge in hex as Iv had them kettle a lot with that silly spiral hex, but the flow went up 70 & then shut down & ticked over on minimum from memory...
 
Yeah the vaillants are complicated, any chance the max flow was adjusted to 50 by mistake?

I meant sludge in hex as Iv had them kettle a lot with that silly spiral hex, but the flow went up 70 & then shut down & ticked over on minimum from memory...

Ohhh sorry.. forgot hex is short for heat exchanger..

How do you adjust max flow temp? Also, why would it ramp up to 65 then drop back down to 42? It does this every 10-15 mins. The burner is on continuously too. Never goes out. I'm gonna bring a ntc sensor with me next week in case it's that but I don't think it is.
 
Most likely heat exchanger blocked. Classic symptoms and prone to blocking. Although had one which was blocked and also been turned down to minimum output by manufacturer.
 
If your Delta T is too low or too high then the boiler will go into a blocking mode. Check the S codes when.the boiler is in operation (they are all in the book) any code ending in 8 is a blocking code.
Is the pump wired to the boiler of wired externally? If it's external this can cause damage to the Heat exchanger as you effectively have no pump overrun.

You can view the Flow & Return temperatures via the D codes (D40 / D41)
 
The heat exchanger on the 4 series is not as bad for blocking as on the 6/8 series although anything is possible, as for your original problem i suspect that when the boiler is on and struggling to reach over 42* the status code would be S53/54 and would be down to the temperature rise when first starting up........ Ie so many degrees in so many seconds etc etc, if it doesn't see the correct rise it will drop its power too a lower output for approximately 20mins before re trying, and so on and so on, this is can also be accompanied after 5 failed attempts with a corresponding F codes but not always ...... And as previously mentioned is down to circulation wether it be appliance or system
 
The heat exchanger on the 4 series is not as bad for blocking as on the 6/8 series although anything is possible, as for your original problem i suspect that when the boiler is on and struggling to reach over 42* the status code would be S53/54 and would be down to the temperature rise when first starting up........ Ie so many degrees in so many seconds etc etc, if it doesn't see the correct rise it will drop its power too a lower output for approximately 20mins before re trying, and so on and so on, this is can also be accompanied after 5 failed attempts with a corresponding F codes but not always ...... And as previously mentioned is down to circulation wether it be appliance or system

There aren't any status codes.. the boiler itself shows no errors. I put in an alpha2L pump and set it to the highest variable flow - think I'll put it to set flow and see if that changes anything. Must be circulation though as before the upper rads were getting up to temp but downstairs rads weren't. Checked pump which was weak. They go through a pump every couple years. Also tenant has to constantly bleed towel rad in top floor bathroom.
 
There are always status codes?????? Not visable without looking but there all the same and without them you wouldn't know what the boiler was doing
 
There are always status codes?????? Not visable without looking but there all the same and without them you wouldn't know what the boiler was doing

On the digital display it literally just reads the temp :/
 
You've got to press the i button........ Then it will show 5.(then a number) that's what tell you what the boiler is thinking so too speak
 
You've got to press the i button........ Then it will show 5.(then a number) that's what tell you what the boiler is thinking so too speak

Ohh - sorry. Not used to Vaillants!!! Cheers Rabbitman! Are the meaning of such codes in the manual? As obv can't call them as will be at custards in an hour
 
Put the pump to set flow and all was well so yes, circulation!! Thanks for all your help guys, very much appreciated!!! :)
 
Status
Not open for further replies.

Reply to Vaillant ecotec Plus 428 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Just started gound work on self build bungalow and wondering best way to do below ground soil pipes. For toilet I was going to go straight down through slab and out through deadwork into a manhole. I will work out falls from manhole and set the height of the waste water system as required. For...
Replies
2
Views
94
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
127
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
186
Hi all Noticed bad smell in my drain out side put my hand down and it unclogged it for now however I checked my sewer drain and after flushing my toilet a good few times nothing is going to the sewer so don't know is there a blockage or what way it works many thanks and advice would be grateful
Replies
3
Views
494
Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...
Replies
2
Views
238
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock