Went to the above boiler to do a service as requested but I stupidly forgot to test fire it before I pulled it apart.

Gave it a clean out, new nozzle and new oil lines.
Then when I fired it up it was stop start stop start then eventually locked out.
Checked the oil tank and there is plenty of oil and no contamination. (Brand new filter)

cant get any pump pressure. So changed the oil pump.
New oil pump fitted (although doesn't seem to be the exact same model even though part numbers are right as it's not got pressure and vacuum ports on the front.
Still the same.

Swapped the tiger loop (above burner) over quickly and still locking out. Just can't get any oil through it.
Cant check the pump pressure though as the test port is on the underside of the new oil pump.

Am I being really thick as it must be something really simple. Just every time I go there it's like 5-6 at night and dark and my brain is frazzled.

Cheers for any suggestions.
 
Really need to get the gauge on, even if you have to drop the burner out to get it on.

Any fuel in the tiger loop ?
 
Get yourself in the arms as well. Plenty of posts to qualify.
 
Have you got single pipe system from the oil tank ? Did you bleed the system ? Did you change any settings on the air shutter? I assume the right nozzle is installed.
 
Last edited by a moderator:
Changed the plastic coupling. And solenoid as always change them at the same time.
No oil at all in the tiger loop. Can't seem to get the system primed.

Will drop the burner out to get the gauge on, if I can.

Single pipe from tank to firevalve and then into tigerloop.
 
Changed the plastic coupling. And solenoid as always change them at the same time.
No oil at all in the tiger loop. Can't seem to get the system primed.

Will drop the burner out to get the gauge on, if I can.

Single pipe from tank to firevalve and then into tigerloop.
 
You will need to make sure you have got a steady oil flow. release the fuel bleed port and place a suitable container beneath.Put the programmer on to heating and hot water and allow the burner to run through to lockout.
wait a couple of minutes and reset the burner control box.
do it a couple of times or until a steady stream of oil, without air.
 
Check oil hoses are done up tight and right way around or tiger wont prime.
Ive done it myself!
 
you could also try with a bucket filled with oil and using that as the tank if you like...just to see whether it's related to a supply issue
 
Went to the above boiler to do a service as requested but I stupidly forgot to test fire it before I pulled it apart.

Gave it a clean out, new nozzle and new oil lines.
Then when I fired it up it was stop start stop start then eventually locked out.
Checked the oil tank and there is plenty of oil and no contamination. (Brand new filter)

cant get any pump pressure. So changed the oil pump.
New oil pump fitted (although doesn't seem to be the exact same model even though part numbers are right as it's not got pressure and vacuum ports on the front.
Still the same.

Swapped the tiger loop (above burner) over quickly and still locking out. Just can't get any oil through it.
Cant check the pump pressure though as the test port is on the underside of the new oil pump.

Am I being really thick as it must be something really simple. Just every time I go there it's like 5-6 at night and dark and my brain is frazzled.

Cheers for any suggestions.


Any update on that ?
 
Not been able to get back as it's a charity and they arnt there most of the time. Just waiting on a time when our timetables cross.
 
Finally got back to this one. Fitted the correct oil pump. Changed a hose that was sucking in air and she is running like a goodun.
 
Status
Not open for further replies.

Reply to Worcester Danesmoor Wallhung in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi My oil boiler keeps locking out after running for 30/40 minutes! I then try to reset it but it won’t fire back up! I have to leave it for several hours before it will fire back up! Only to lock out again after 30/40 minutes! The boiler has had a new nozzle, coil and pump in the last 2...
Replies
19
Views
779
I'm looking for some advice on a frustrating problem I'm having with my old Eurostar 50-60s oil boiler please? Although it's old, most parts needed to operate it are now new. The symptoms indicated a broken/seized burner motor or oil pump. I wrongly assumed the motor so I ordered a new one only...
Replies
3
Views
712
Any advice welcome as plumber stumped Had 36-46 grant vortex utility boiler 7 years no problem recently oil tank move and tigerloop install (tank about 1m lower). 10 days later and boiler either doesn't fire or fires stops, fires runs splutters stops. Most it runs now is 10 mins, but that's...
Replies
4
Views
579
I have a SIP space heater and fitted a new matching spec oil nozzle as part of a service on it. I wanted to check the pump pressure with the new nozzle and its difficult to be sure what port to connect to. And that these pumps are definitely adjustable! I turned an Allen screw which is not...
Replies
2
Views
305
Hi there. I have Grant oil fired boiler which when cold, takes multiple times to fire up. It will run for say 20 or 30 seconds with hot exhaust gases then it stops. The fan is still going then it starts off again and stops again. After 4 or 5 goes it runs fine. When the boiler gets up to...
Replies
1
Views
732
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock