I have a Vaillant EcoTEC Plus 415 Heat Only Open Vent Boiler throwing up a F.22 fault code as soon as it ignites and then goes idle. It then sits with pump running and an S.98 status until the boiler is switched off and reset.

F.22 = Too little water in the appliance, water pressure sensor defective, cable to pump or water sensor defective, pump blocked or defective, pump output too low.
S.98 = Flow-/Return-sensor check is running, demand (DHW or heating) is blocked.

This happened after MagnaClean was cleaned, fired back up and heard a few knocks at boiler followed by it shutting down. Found fair amount of sludge at pump, motorised valve and section of pipe near F&E supply so all replaced. Thermistors also replaced. Pump sounds like it is happily sending water round system but boiler fault code unchanged.

I'm thinking sludge has been thrown into boiler and clogged up heat exchange? Or possibly PCB fault throwing incorrect error? Any agreement or anything else I should try?
 
Are you gas safe registered??
 
All work on the appliance is being done by a gas safe registered individual (not me). I am merely looking for expert third party advice from you guys on this problem.
 
I had that recently!! Was scratching my head for ages- had lots of air in the boiler/system. Changed the pump and it was ok- now I have a different problem, radiators are very noisy when heating up- cust complaining? Should I have changed the system to sealed ch? I don't know! sorry to hi-jack your post o_O
 
Yep, ecotec plus 415 Open Vent. Had a bit of air in the system but nothing serious.
 
Last edited:
I think it's slow flow, there's not a great enough temperature difference between the thermisters. Speed up the pump and see if that works. And is the bypass set correctly?
 
I've managed to get a PCB which is going to be tried later but hopes are low on this. Tried pump on high setting with no luck. There is an auto bypass valve fitted but never touched the settings, shall I fully open it then?
 
Hi
It’s just lack of flow. Could be a few things.
Blocked heat exchanger.
Sludged up pipework.
Air locked.
Or pump sited too far from the boiler.
 
New PCB reports same fault so not that!

I was thinking wrong board to be honest because I've never seen a 4 series with an F22 fault. There is no pressure sensor on them.

If a 6 or 8 series came up with F22, the pump would not run!!

All sounds strange to me. I would say @Chalked was on the right track though.
 
Thanks guys - some good advice! Think I'll go with isolating the boiler and attempting to flush the HE as the next thing to do.
 
Status
Not open for further replies.

Reply to Vaillant Heat Only Boiler - Water Flow Problem? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I just had a quote for a new boiler install as follows I dont undertand why a 15-60 boiler pump is needed and a 25-100 pump is needed as well I currently have an ideal mexico 2 heat only boiler - It has one DAB pump on the boiler return and a 2 port valve at the flow pipe to allow for heating...
Replies
3
Views
535
Got fd code on Ideal Logic Heat 15. Had two plumbers out and no joy. It’s had a new water flow sensor, flush with sentinel x800 and refurbished grundfos water pump. Boiler tries to light and water pump power light comes on but goes off immediately and boiler flashes fd again. It’s heat only so I...
Replies
16
Views
526
Hello, I am looking for a heating engineer to diagnose and resolve an issue with my Vaillant EcoTec 832 combi boiler. Job Location: Copeland Rd, London. Job Description: Problem: The boiler is not providing heating under normal conditions, although hot water supply is fine. Interestingly...
Replies
1
Views
386
Removing pump and installing a new pump for Vaillant ecoTEC Plus 400 15kW Heat Only Boiler. Connecting the pump to the boiler and completing all wiring for the thermostat and consumer heating controller.
Replies
0
Views
620
A (if) CH system has a very high head loss due to improperly sized pipework and long runs and possibly partially blocked pipes and requires a UPS2 pump running at its 8M head to feed 21 rads with a theoretical output of 25kw at a 20C dT. A fairly old Vaillant 438 boiler is being replaced, the...
Replies
16
Views
1K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock