so if you was to tightness test a job you haven’t worked on. During the let by test there is a drop. You then test for tightness on an e6 and it drops 1mbar over 2 minutes and pipework not all accessible and appliances not all with iso valves. Would you deem it unsafe
Post automatically merged: Yesterday at 3:41 PM
Appreciate the feedback. We used a full can of leak detector on all the new joints (probably about 15 in total) over and over again. And nothing. Not even a slight bubble. The engineer was happy that it was in the safe limit. But for some reason he was checking.

Would you guys walk away from that or not?

also is it possible rocol leak detector wouldn’t pick it up? is there a good gas sniffer on the market that’s reasonably priced and more reliable than ldf. Thanks

I wouldn't deem it unsafe going off that information.

I would find out how much is leaking and where from in this situation (you have made alterations).

Cutting the boiler off temporarily and testing pipework only would take less time than squirting LDF everywhere and once you have done that you will be a lot clearer on what is leaking. Then you can decide whether it is safe to leave it.

You have to put things in perspective. If this was an existing installation with appliances connected and no smell of gas on a domestic property with an E6, then I would be happy to forget it. I would still need to let by test the ECV.
If there is gas passing through that and leaking out elsewhere, you cannot carry out testing accurately.

ROCOL, is good LDF in my opinion. It will find most things where joints are concerned but it can depend on the position and size of the leak, whether you see it or not.

Sniffers are available from ten's of pounds to thousands of pounds depending on your needs.
They are well worth having.

The Engineer you are working with may well have made his/her mind up going off a vast amount of knowledge and experience for all we know. It may look like they had doubts but I wouldn't think they would leave it if there was any danger to be fair. Have you discussed this in detail with them? If you ask why they arrived at the decision they did, you may be surprised at their thought process. It might make perfect sense.
 
Aslong as there’s no smell of gas / report of smell then it’s fine some of the new digi meters have an allowable limit of around 4-6 mbar depending on brand

External pipe work or internal ?

A mix of internal and external. But mainly long runs and not many fittings. Think he was using a Kane. It was well within tolerance but we was still checking the joints With ldf so had me wondering why. I have only worked with water u gauges before

cheers
[automerge]1587428128[/automerge]
I wouldn't deem it unsafe going off that information.

I would find out how much is leaking and where from in this situation (you have made alterations).

Cutting the boiler off temporarily and testing pipework only would take less time than squirting LDF everywhere and once you have done that you will be a lot clearer on what is leaking. Then you can decide whether it is safe to leave it.

You have to put things in perspective. If this was an existing installation with appliances connected and no smell of gas on a domestic property with an E6, then I would be happy to forget it. I would still need to let by test the ECV.
If there is gas passing through that and leaking out elsewhere, you cannot carry out testing accurately.

ROCOL, is good LDF in my opinion. It will find most things where joints are concerned but it can depend on the position and size of the leak, whether you see it or not.

Sniffers are available from ten's of pounds to thousands of pounds depending on your needs.
They are well worth having.

The Engineer you are working with may well have made his/her mind up going off a vast amount of knowledge and experience for all we know. It may look like they had doubts but I wouldn't think they would leave it if there was any danger to be fair. Have you discussed this in detail with them? If you ask why they arrived at the decision they did, you may be surprised at their thought process. It might make perfect sense.

Thanks for your response. Forums like this can really help people like myself out. Thing is I have trained with many different engineers, with completely different ways. The guy who I’m with now is just helping me out for the time being as college is closed and the company I’m doing my time with have closed for the time being. But He’s probably not the kind of guy who wants to be questioned too much. I guess you can imagine time is money for him. I’m still getting experience and helping out aswell.

but thanks for the replies
[automerge]1587428357[/automerge]
I wouldn't deem it unsafe going off that information.

I would find out how much is leaking and where from in this situation (you have made alterations).

Cutting the boiler off temporarily and testing pipework only would take less time than squirting LDF everywhere and once you have done that you will be a lot clearer on what is leaking. Then you can decide whether it is safe to leave it.

You have to put things in perspective. If this was an existing installation with appliances connected and no smell of gas on a domestic property with an E6, then I would be happy to forget it. I would still need to let by test the ECV.
If there is gas passing through that and leaking out elsewhere, you cannot carry out testing accurately.

ROCOL, is good LDF in my opinion. It will find most things where joints are concerned but it can depend on the position and size of the leak, whether you see it or not.

Sniffers are available from ten's of pounds to thousands of pounds depending on your needs.
They are well worth having.

The Engineer you are working with may well have made his/her mind up going off a vast amount of knowledge and experience for all we know. It may look like they had doubts but I wouldn't think they would leave it if there was any danger to be fair. Have you discussed this in detail with them? If you ask why they arrived at the decision they did, you may be surprised at their thought process. It might make perfect sense.

So maybe stick a lever ball valve on gas feed to boiler. For the sake of testing everywhere ?
 
Last edited:
A mix of internal and external. But mainly long runs and not many fittings. Think he was using a Kane. It was well within tolerance but we was still checking the joints With ldf so had me wondering why. I have only worked with water u gauges before

cheers
[automerge]1587428128[/automerge]


Thanks for your response. Forums like this can really help people like myself out. Thing is I have trained with many different engineers, with completely different ways. The guy who I’m with now is just helping me out for the time being as college is closed and the company I’m doing my time with have closed for the time being. But He’s probably not the kind of guy who wants to be questioned too much. I guess you can imagine time is money for him. I’m still getting experience and helping out aswell.

but thanks for the replies
[automerge]1587428357[/automerge]


So maybe stick a lever ball valve on gas feed to boiler. For the sake of testing everywhere ?
I would discuss it with the owner or responsible person first as always but that would be the way forward for me.
 
It could easily rise and drop .50 mbar due to heat / cooling eg if he started the test when the sun was out then the clouds came etc
 
Hello. First of all I’m new to this site. I’m in the process of doing my apprenticeship, but now with the current circumstances we are not working. I have a couple of basic questions which no doubt will raise eyebrows, but every body starts somewhere.

In tightness testing. Regarding permissible drops. It outlines new installations and existing installations.. so what would an installation be if it was a partial upgrade. So half existing/half new

in let by. We are testing to see if the ECV is letting by and rising on the gauge. But if there’s an ever so slight constant drop. That would suggest a leak. So what do you do then, if say the tightness test was satisfactory, 1mbar drop over 2 minutes on an E6?

Apologies for the silly questions. But I keep getting told conflicting information and the book doesn’t actually cover everything

thanks
The key point here is it was an existing installation that has been altered so is not new.

What should have been done is a tightness test carried out before alteration with appliances connected and pressure drop noted. For example 1mb- no smell of gas.

After alterations as long as drop is no different than 1mb and no smell of gas all is ok. You are within permissible drop!

As soon as you isolate any appliances and have a drop you MUST then trace and repair as you are not permitted to walk away from a drop on the carcass!

Another point to be aware of is your employer specific guidelines. Some employers do not permit any pressure drop at all!
 
Thanks everyone for the feedback. Great to hear other opinions.

Today we installed a new gas pipe, where eon had capped the meter off for a 3mbar leak on another e6. Not sure why or if gas was smelt. He renewed the gas pipe, only a 3 meter run, feeding one hob.

tightness test showed a 0.15mbar drop on tightness testing. It’s the first time I have seen digital being used. it’s always been a u-gauge before where you would not see that movement. He signed it off and said that was ok.

Guess with things close to the mark it’s a game of opinions?
 
Hello. First of all I’m new to this site. I’m in the process of doing my apprenticeship, but now with the current circumstances we are not working. I have a couple of basic questions which no doubt will raise eyebrows, but every body starts somewhere.

In tightness testing. Regarding permissible drops. It outlines new installations and existing installations.. so what would an installation be if it was a partial upgrade. So half existing/half new

in let by. We are testing to see if the ECV is letting by and rising on the gauge. But if there’s an ever so slight constant drop. That would suggest a leak. So what do you do then, if say the tightness test was satisfactory, 1mbar drop over 2 minutes on an E6?

Apologies for the silly questions. But I keep getting told conflicting information and the book doesn’t actually cover everything

thanks
If you have upgraded a installation treat it as a new no drop

if it’s not letting by go on to stabilisation and tightness test and see how much it’s dropping by then resolve the leak.
 
Thanks everyone for the feedback. Great to hear other opinions.

Today we installed a new gas pipe, where eon had capped the meter off for a 3mbar leak on another e6. Not sure why or if gas was smelt. He renewed the gas pipe, only a 3 meter run, feeding one hob.

tightness test showed a 0.15mbar drop on tightness testing. It’s the first time I have seen digital being used. it’s always been a u-gauge before where you would not see that movement. He signed it off and said that was ok.

Guess with things close to the mark it’s a game of opinions?
Perceptible movement is 0.2mb on a digital gauge so your 0.15 drop is within these limits so not an issue.
Dont like using digital gauges anyway. Especially on a windy day as bounces around too much!
Cant beat the Regin Premier when got a full day of CP12's.
 

Reply to Tightness testing on gas installations in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to...
Replies
6
Views
287
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
315

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock