A

AaronC

So I got called to a burner where they had the problem of it won't fire in the morning and they have to hit the button on the control box for it to fire. I have changed the pump and the box, but its still doing the same thing? I have checked the oil filter and its spotless, also I serviced it a few months ago and checked the nozzle and its still as good as new. The oil supply is fine too

Anyone any idea what else it could be?
 
Could be a few things. First of all, I assume, as you changed oil pump then the solenoid is new, so it could be motor capacitor or photocell. Also burner could be set wrong which won't start on cold start in morning. Check spark is healthy & that motor seems strong, with no bearing noise.
 
Yep, new solenoid with pump. When we did fire it, there was no bearing noise, sounded healthy enough. In what way would the burner be set wrong that it won't start on a cold morning?
 
It could be overaired, you have to make an allowance for summer settings and winter settings, warm air has less oxygen content than cold air hence if it is a cold morning and the boiler is setup right on the borderline it could have too much oxygen.
I agree with best on everything else, it could also be air in the oil line, check there are no weeping joints. My bet would probably be with the capacitor as Best says
 
Last edited by a moderator:
As Kimbo says, too much air to the oil mixture will prevent it igniting or burning correctly on start up, & can lock out. Very common when we get cold mornings. Usually caused by air setting too high, but obviously if oil pump pressure is too low or nozzle partly blocked, same happens.
Capacitors seem to be a common fault on Sterlings. Try listening carefully to burner motor start by switching burner on a lot of times. If it sounds sluggish on the split second start any one time, then change the capacitor.
 
Last edited:
Sorry, I had said solenoid in last post but meant change capacitor! Have edited it now.
 
Try an ebi transformer had bother with few of these intermedent
 
If the motor turns OK and it only trips when it comes on in the morning, sounds like you are getting air in the fuel line.

Without seeing it, if I were guessing I would suspect the following scenario - fuel supply is lower than the boiler and there is a slight leak in the supply pipework allowing air in, causing the oil to fall back down the pipe to its natural level due to gravity. The air coming in is only gradual so it's only when the boiler has not been operating for a significant length of time that the oil has run far enough back down the supply pipe that the fuel does not reach the pump before the controller times out.

Rectification - firstly the usual culprit for this is a wheel head fire valve as these are prone to leaking as they age. Use a Rothenberger type pressure test pump on the line (at the tank end) and when you pressure it up with oil (6 bar), the leak will become obvious.
 
Last edited:
Status
Not open for further replies.

Reply to Sterling Burner Problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I'm looking for some advice on a frustrating problem I'm having with my old Eurostar 50-60s oil boiler please? Although it's old, most parts needed to operate it are now new. The symptoms indicated a broken/seized burner motor or oil pump. I wrongly assumed the motor so I ordered a new one only...
Replies
3
Views
711
L
Camray 5 (90A) (20 year old) oil boiler, had a noisy fan on the boiler so investigated, just a bit of dirt in the casing however, having removed the burner unit I replaced the Burner Nozzle no problem, old was very dirty and sooty. Found the boiler wouldn't fire up. SO rather than than mess...
Replies
3
Views
962
Heating and hot water is not working. Plenty of heating oil. I have replaced batteries in thermostat and it seems to be working ok, showing flame to call for heat, and the receiver seems to be working ok with green light, but heating is just not firing. I really am not sure what the problem is...
Replies
5
Views
316
L
Camray 5 (90A) (20 year old) oil boiler, had a noisy fan on the boiler so investigated, just a bit of dirt in the casing however, having removed the burner unit I replaced the Burner Nozzle no problem, old was very dirty and sooty. Found the boiler wouldn't fire up. SO rather than than mess...
Replies
0
Views
872
Lincoln22
L
I have a customers trianco burner that starts from cold ok for a few minutes (say 3minutes) then locks out then will not stay on. Boiler had not been serviced in a long time and oil filters were bunged up as was the nozzle. I decided to service it with hopes it was simple starving of fuel from...