We had this one before. G3 is for above 15 litres. 15 and under you don't need G3 but you do need to follow the instructions around pressure relief, check valve, expansion and first draw off points.
 
Since 2010 G3 is for all hot water storage - vented & unvented.
 
I stand corrected, section 3.19 of document G3 " Water heaters with a capacity of 15 litres or less that have appropriate safety devices for temperature and pressure will generally satisfy the requirements set out in G3(3)."

Good call Blod.
 
Bloomin red tape ...

:mad:

It's not so much the red tap as the ambiguity of the statement in the G3 regs they have a set of regs upto 500 litres but then make special mention of under 15 litres. So why don't the 15 litre and under come under the upto 500 litres.
 
they couldn't be bothered to rewrite all of the regulations and just changed the parts that had changed.
 
15 litres burting isnt going to bring a house down
It might not bring the house down, but if installed incorrectly it still has the potential to become a pressure cooker and burn your skin off if it was breached suddenly.
At 3bar pressure the boiling point is approx. 150°C. If that is suddenly vented to atmosphere it will instantly turn to steam.
 
if water is even getting to the tundish it means you got problems. not might be a big one but an issue that should be looked at.
 
Status
Not open for further replies.

Reply to Megaflo Tundish in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock