Just about to start a job , system boiler , ufh zone , cyl zone , rad zone. It’s quite a big house so was going to add low loss and pump to aid , but it’s tight for space where boiler is going. Ufh manifold is going about 10m away in a cupboard , where I’d have loads of room for my zone valves , low loss and pumps. Could anyone see an issue with doing that ? 28mm from boiler to low loss 10m away ? I’ve fit them before but always put close to boiler. At a squeeze I could fit low loss with boiler and then pump to zone valves 10m away if that makes sense ? Any advice gratefully received, many thanks
 
Just about to start a job , system boiler , ufh zone , cyl zone , rad zone. It’s quite a big house so was going to add low loss and pump to aid , but it’s tight for space where boiler is going. Ufh manifold is going about 10m away in a cupboard , where I’d have loads of room for my zone valves , low loss and pumps. Could anyone see an issue with doing that ? 28mm from boiler to low loss 10m away ? I’ve fit them before but always put close to boiler. At a squeeze I could fit low loss with boiler and then pump to zone valves 10m away if that makes sense ? Any advice gratefully received, many thanks
As long as the pump on the boiler is enough to pump the circuit to the header then, no there is no problem. I have done similar before. On one commercial job I used a plate at the boiler end and a LLH at the other due to distance - with an additional pump in between - you won't need that but your idea is good, go for it.
 
Nope your fine
 

Reply to Low Loss header , remote from boiler in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I am looking to replace my existing Vaillant heat-only boiler with a new Vaillant ecotec plus 630 system boiler (30kW). I have a megaflo hot-water cylinder, a central heating system (serving 21 radiators) and an orangery built last year (6m x 4m) with underfloor heating. Through running some...
Replies
2
Views
501
Hi All, Looking for a bit of advice on the best way to pipe this. - 24kW Worcester regular boiler in kitchen, approx. 9 years old - unvented tank, zone vavles, pump, expansion is on first floor in airing cupboard - Currently piped as S-plan. - Hive controls. - Would like to fit 6-zone...
Replies
16
Views
979
I recently had a new 2023 Vaillant ecoTec plus 630 (30kW) system boiler installed along with a Low Loss Header (LLH) in my house. I have 21 rads in the house and a room with UFH. The LLH was introduced as I was finding (before the LLH was fitted) that my old boiler (Vaillant heat-only boiler)...
Replies
10
Views
733
C
I've got a Greenstar 8000 going through a low loss header feeding 3 circuits, two trad rads and one UFH. Will it increase efficiency by instaling a temp sensor on the header and setting the boiler settings accordingly?
Replies
1
Views
568
Good morning, wondered if anyone can advise please on a resolution? My set up at home is that I have a 4-bed detached with 21 radiators (includes 4 towel rails), a 6m x 4m orangery/conservatory that was built last year with under-floor heating, and a Megaflo for storing hot water. The UFH...
Replies
61
Views
5K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock