Hi Cardiff Plumber.
Wow what place that Lymm Water Tower is!!! I wish mine was anywhere near as good! Impressive work!!

I have considered Thermal Stores before and they sound a good idea. The only problem I have with them is that not many plumbers are familiar with them, so if and when things go wrong with them, I wouldn't be able to just phone the first available plumber to sort the problem.

Also in my particular case, wouldn't it again involve heating a large cylinder of water for the occasional use of the bath?
 
Lol!! Yeah, wasn't it this Predictability factor that first lead scientists to discover quantum theory?!
 
Hi Bogrodder.

There's a temporary curved 25mm copper pipe, shaped like a tap with a lever ball valve as a tap connected to the blue incoming mains. (there is also stopcock on it but I've left that open).

I filled a bucket to 25 litres in 25 seconds. I don't know the pressure as I don't have a gauge.

Bye the way I'm sorry if this is the second time you've received this reply as I'm sure I've already sent it, but I cannot see it on the page. It may have something to do with me using Safari as a browser. Anyway apologies again.
 
Hi Snowhead.
Lol! I think that symbol (which I can’t do on my keyboard) = Unpredictability.
So Predictability would be 1/ (that symbol) which would make it pretty close to zero as Ray stated.

It’s a good thing that there aren’t many female plumbers out there or else we’d get deluged with lots admonishing replies from irate members.

In fact I’m going to have to have the Hide button ready when writing in this forum, just incase she walks in! . . . . . . Which will be okay cos she’ll think I’m just looking at naughty stuff again, which is usually considered a lesser crime than any form of direct criticism!
 
Unvented cylinder and combi boiler used as a system boiler but the hot water from combi supplying the bath and basin in the bathroom.
 
Unvented cylinder and combi boiler used as a system boiler but the hot water from combi supplying the bath and basin in the bathroom.

If there is no shortage of incoming pressure and flow (and it sounds like there isn't) then this would be an excellent solution, and very cost effective both to install and to run.
 
Hi Gray0689

Could you explain what a solar thermal is please.

Solar thermal
Basically tubes or panels on roof (South facing preferably)
That when sun out will heat hot water through a coil at the bottom of your cylinder

And stay away from thermal stores there not good
 
And stay away from thermal stores there not good

Thermal stores are excellent if you need to integrate multiple heat sources, particularly hard-to-control or unpredictable sources like solid fuel or renewables.

If there is no need to manage such challenging inputs, then its difficult to make the case for a thermal store in a domestic installation.
 
You could fit an unvented sized for just the shower & hot taps and fit a combi boiler zoned for heating & cylinder but using the hot water side just for the bath.
 
I wouldnt be keen using a combi to fill such a large bath. It takes about 25 minutes just to fill a standard bath with our gas combi.
 
Unvented cylinder and combi boiler used as a system boiler but the hot water from combi supplying the bath and basin in the bathroom.

Hi AWheating

Could you please explain the above system a little more. So would that be the one boiler (a Combi boiler) and one unvented cylinder? If so, could you explain a little more how it would work?
 
Hi AWheating

Could you please explain the above system a little more. So would that be the one boiler (a Combi boiler) and one unvented cylinder? If so, could you explain a little more how it would work?

Hi Dragoon. I'm not sure whether AW is online, but in case he isn't, this is what he is suggesting.

On the heating side, a combi is just like any other boiler - it has a flow and return which can be used as an S plan (preferred) or Y plan (if you must) to heat a cylinder as well as heating the radiators.

In addition to that, it has the instanteous hot water system, albeit with a limited flow rate, as you have identified.

So if you mate a combi with an unvented cylinder, you can have stored water available for some outlets and instantaneously heated water for others. Exactly how you divide them up is up to you, but normally outlets that use a lot of water, relatively rarely (say a bath) should be fed by stored hot water, whereas outlets that frequently use just a few litres (say kitchen sink) would be better on the instant.

The limiting factor (assuming that the cylinder is unvented) is the capacity of the incoming cold main, but yours sounds like it has plenty of flow at least.
 
Hi Cardiff Plumber.
Wow what place that Lymm Water Tower is!!! I wish mine was anywhere near as good! Impressive work!!

I have considered Thermal Stores before and they sound a good idea. The only problem I have with them is that not many plumbers are familiar with them, so if and when things go wrong with them, I wouldn't be able to just phone the first available plumber to sort the problem.

Also in my particular case, wouldn't it again involve heating a large cylinder of water for the occasional use of the bath?

Well you would have superb insulation with a decent thermal store, so you would be just topping up temp each day. It works very well and have never had any problems in the past.
 
Thermal stores are excellent if you need to integrate multiple heat sources, particularly hard-to-control or unpredictable sources like solid fuel or renewables.

If there is no need to manage such challenging inputs, then its difficult to make the case for a thermal store in a domestic installation.


Hi Ray.
Thermal stores sound like a good idea, however I don't have multiple heat sources so it's not really needed in my case. But also I heard that they can be problematic (as with all systems really as they age), and because not many plumbers are familiar with them, that would be my biggest cause of worry with them.
 
Hi Dragoon. I'm not sure whether AW is online, but in case he isn't, this is what he is suggesting.

On the heating side, a combi is just like any other boiler - it has a flow and return which can be used as an S plan (preferred) or Y plan (if you must) to heat a cylinder as well as heating the radiators.

In addition to that, it has the instanteous hot water system, albeit with a limited flow rate, as you have identified.

So if you mate a combi with an unvented cylinder, you can have stored water available for some outlets and instantaneously heated water for others. Exactly how you divide them up is up to you, but normally outlets that use a lot of water, relatively rarely (say a bath) should be fed by stored hot water, whereas outlets that frequently use just a few litres (say kitchen sink) would be better on the instant.

The limiting factor (assuming that the cylinder is unvented) is the capacity of the incoming cold main, but yours sounds like it has plenty of flow at least.

Thanks Ray, so would you suggest that in my case the shower and the sinks etc be fed by the unvented cylinder, while the large bath and the bath basin be fed by the instantaneously heated side? That sounds pretty good to me, as a small drop in flow rate at the bath shouldn't make too much of a difference.
 
Well you would have superb insulation with a decent thermal store, so you would be just topping up temp each day. It works very well and have never had any problems in the past.

Hi Cardiff Plumber. That sounds good actually. But would that be the same for an unvented cylinder i.e.. that it would just be topping up temp each day?
If I lived anywhere near you (Cardiff) I might seriously consider it, but as I've said before it's hard to find people who have a good working knowledge of Thermal Stores.
 
Sounds like a good idea don't it, however your bath would be cold by the time it is full & you are ready to get in.
Your bath 400+ Litres I believe, combi flow rate lets say it's a 28kW @ 12 L/M @35deg C rise = 33mins to fill it i.e. cold & a long wait.
 
Last edited:
Sounds like a good idea don't it, however your bath would be cold by the time it is full & you are ready to get in.
Your bath 400+ Litres I believe, combi flow rate lets say it's a 28kW @ 12 L/M @35deg C rise = 33mins to fill it i.e. cold & a long wait.

Hi Chris
Yeah, that's true. Do you think that what Cardiff Plumber says is true for unvented i.e. that I would just be topping up temperature each day so it wouldn't be too expensive?
 
Sounds like a good idea don't it, however your bath would be cold by the time it is full & you are ready to get in.
Your bath 400+ Litres I believe, combi flow rate lets say it's a 28kW @ 12 L/M @35deg C rise = 33mins to fill it i.e. cold & a long wait.

However, as you said before, filling a bath would be 60(hot):40(cold) so for a 400ltr bath I would need 240 ltrs hot water which, at 12 ltrs/min would take 20 mins.
Is 20 mins okay to fill a bath? I don't really have baths often so I wouldn't know. This is really just for the girlfriend!
 
Thanks Ray, so would you suggest that in my case the shower and the sinks etc be fed by the unvented cylinder, while the large bath and the bath basin be fed by the instantaneously heated side? That sounds pretty good to me, as a small drop in flow rate at the bath shouldn't make too much of a difference.

Nope. Other way round.

Infrequent use but lots of water = bath. Take that off the cylinder.

Frequent use but middling amounts of water = shower/basin/sink. Take them from the combi.

Maybe also think about the most likely clashes, and make sure they are on separate supplies
 
How about a smaller bath? :hurray:

I'd stick with a 250-300 litre cylinder. Wire the system to prioritise hot water so when your running a bath the boiler is diverted to hot water only.

Also remember to subtract the water displaced by people being in the bath. (Depending what you were going to use a big bath for :rolleyes2:)

The heat losses between the 300 and the 180 is less than a kW a day. Gas is approx 4.5p per kW so (ignoring boiler efficiency) and assuming it all goes to waste (ie not airing clothes etc) your looking at less than £20 a year. The additional cost in complex installation would far outweigh the saving.
 
Last edited:
Nope. Other way round.

Infrequent use but lots of water = bath. Take that off the cylinder.

Frequent use but middling amounts of water = shower/basin/sink. Take them from the combi.

Maybe also think about the most likely clashes, and make sure they are on separate supplies

So the cylinder would be heated up every day, but not used until Bath day while the Combi would be in use everyday for the rest of the outlets?

Wouldn’t it be better to have it the other way around where the cylinder can be used like a ‘normal’ unvented system (where the cylinder is heated up everyday), and then on Bath day we can have the extra hot water “straight from the tap” without any storage?

Or am I missing the point? (which wouldn’t be the first time I can assure you!)
 
How about a smaller bath? :hurray:

I'd stick with a 250-300 litre cylinder. Wire the system to prioritise hot water so when your running a bath the boiler is diverted to hot water only.

Also remember to subtract the water displaced by people being in the bath. (Depending what you were going to use a big bath for :rolleyes2:)

The heat losses between the 300 and the 180 is less than a kW a day. Gas is approx 4.5p per kW so (ignoring boiler efficiency) and assuming it all goes to waste (ie not airing clothes etc) your looking at less than £20 a year. The additional cost in complex installation would far outweigh the saving.

Hi Nostrum.
You’re right! I completely forgot about the displaced water! Also, it would actually be worth it if the rolling eyes were applicable! But she likes lighting candles and reading her books in the bath.

And it has been bugging me if I’m being overly concerned about the extra expense. When you say that the heat losses between the 300 and the 180 is less than a kW a day what does that mean?
 
The energy losses of a good unvented cylinder are 1.5 - 2.5 kWh's per day. Ie naff all. You are worrying over nothing, or pennies per day.

:welcome:
 
However, as you said before, filling a bath would be 60(hot):40(cold) so for a 400ltr bath I would need 240 ltrs hot water which, at 12 ltrs/min would take 20 mins.
Is 20 mins okay to fill a bath? I don't really have baths often so I wouldn't know. This is really just for the girlfriend!

The 60/40 bit only works if hot is around 60 - 65 & cold is around 10deg C the blend would give hot water at around 40. With a combi (instantaneous heater) the power is fixed (say 28kW) & the flow rate can be adjusted to give the require outlet temperature. So increase the flow & outlet temp goes down, slow it & it increase (it is said to be proportionate).
Most manufacturers state the flow rate with a 35deg rise, so if incoming mains water is at 10 deg C the outlet temp would be 45 with a flow rate of 12L/M.

45 is little more than hand hot so by the time it gets to said bath & heats up the material, sits around for half hour it all equals a cold bath.
 
Thermal store for your situation is not a good idea
They are ok for a solid fuel link up just about IMHO
 
400ltr bath, minus the volume of the two people enjoying each others company. ;)

may even increase the water temps........
 
The energy losses of a good unvented cylinder are 1.5 - 2.5 kWh's per day. Ie naff all. You are worrying over nothing, or pennies per day.

:welcome:

Hi Nostrum.

Thanks for putting some sort of a figure on the losses for me. If it only amounts to just pennies a day, it’s not really worth compromising on flow rates.

Also the system will be housed in a dedicated small boiler room, which I intend to also use as a largish airing cupboard. And any heat losses from that will go to heat the hall so really the losses will be almost negligible.

Oh and thanks for the welcome!
 
You could also make sure the pipes are well insulated at the unvented unit - especially the hot supply pipe leaving the top of the cylinder. If that pipe drops downwards, it will prevent heat gravitating up the pipe. Small savings, but still helps.
Also get rid of any women from your house. :smile:
 
The 60/40 bit only works if hot is around 60 - 65 & cold is around 10deg C the blend would give hot water at around 40. With a combi (instantaneous heater) the power is fixed (say 28kW) & the flow rate can be adjusted to give the require outlet temperature. So increase the flow & outlet temp goes down, slow it & it increase (it is said to be proportionate).
Most manufacturers state the flow rate with a 35deg rise, so if incoming mains water is at 10 deg C the outlet temp would be 45 with a flow rate of 12L/M.

45 is little more than hand hot so by the time it gets to said bath & heats up the material, sits around for half hour it all equals a cold bath.

Hi Chris.

Thanks for that, I never did understand the 35deg rise as quoted by boiler companies, now I do. So that’s why Ray suggested that the cylinder should feed the bath and the combi should feed the shower and the rest.

So do you think I should just stick with a system boiler with an unvented cylinder? As Nostrum suggested that I’m worrying over nothing and that the energy losses will not really amount to that much, just pennies a day?
 
You could also make sure the pipes are well insulated at the unvented unit - especially the hot supply pipe leaving the top of the cylinder. If that pipe drops downwards, it will prevent heat gravitating up the pipe. Small savings, but still helps.
Also get rid of any women from your house. :smile:


The place is a bungalow on just the ground floor, so the pipe leaving the top of the cylinder will probably have to drop downward at some point.

Also I've tried doing without the women before. . . . . . but it's not good for the ol' eye sight. . . . if you know what I mean!:chinese:
 
400ltr bath, minus the volume of the two people enjoying each others company. ;)

may even increase the water temps........

Well that was the idea behind the large bath, but judging from previous attempts, the increase in the water temp was quickly counteracted by the coldness of a shoulder which she offered, before going back to reading her book! :disappointed:
 
Thermal store for your situation is not a good idea
They are ok for a solid fuel link up just about IMHO


Hi Gray.

I actually like the idea of the way Thermal Stores work, it's almost like a large powerful Combi. However I don't know anyone who has one installed, and from the net the picture I get is that they can be temperamental, so some people really hate them while others rave about them. And like you said I don't think it's a good idea for my situation.
 
Theres nothing temperamental, special or complicated with a thermal store. Without having multiple inputs though it will cost you an arm and a leg maintaining sufficient temperature in the thermal store for your requirements.
 
Status
Not open for further replies.

Reply to Linking Two Unvented Cylinders in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
199
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock