Discuss Just had an argument about tightness testing in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
as director then the company number is yours, and as you rightly say and know you dont need gas quals to run a gas company (which is where a lot of the bother starts haha) im sure when i log in i use company 6 digit number and personal ID number, but cant be 100% as i dont go on it too often and cant remember just seem to do it automatically, as we get update info from various sources, you will obviously also know as director you have sole responsibility for ensuring you have a robust Gas Management System or Method Statement and that all your operatives are kept updated with all new reg changes, TB's and every other piece of blame that will come your way if one of the operatives comes a cropper, but thats why you get the big bucks and the company Jaguar

Yes right!
 
I don't Want to argue with you BUT...! Only joking
Actually, despite being a pleb it is my number and password.
Well, I think it is? May be it isn't, may be it is Mr TPs? We do have other opperative too.
I am a director and we have only ever had one log in number, which is 5 digits and a password.
The problem I have with the password is the mix of captials, lower case and numbers.
I think i type them in all the wrong order and I don't think it recognises the numbers if I type on the number keypad. I always end up having to imput it all 3 or 4 times before I get in.

i can conclude a few points from this
1,kirk,mrs tara plumbing and tamz are spot on
2,tamz has pulled .....LOL......:D:D:D:D:D
 
Second post in as many days.
Just been in plumb centre and was earwigging on two guys talking about testing.
Now I'm a commercial fitter with domestic as well. Granted I have not used my domestic that much over the years but it does get used.

Now the way I was taught was the following;

Upon entering a building to do gas work you do the following:
1 minute let-by at 10mbar
1 minute stabilisation at 20mbar keeping at 20 for that minute
2 minutes at 20mbar.
Anything above 75mbar is medium pressure and requires a different test (this was where I got into conversation with them as they said anything over 82.5 was medium)

Any Drops at stabilisation are fine, any drops within 2 minute test need to be within permitted limit otherwise test fail and you need to find the source

You then do any work IE boiler service, then after the work do the same again.

Now these two guys argued with me for five minutes that you do only need to do a 2 minute test at 20mbar.
Any drop is fine as long as there is no smell of gas.
Also that doing a test upon entry is not needed, and I was wasting my time.

Now somebody please tell me I'm right, I don't have my domestic viper with Me so cannot check, but I will be mortified if I have been doing it wrong all these years!

Honestly these lads have put complete doubt in my mind now, to the point that I'm worried about doing a test today!

YOUR 100% CORRECT, these lads by the sound of it are dangerous! any drop is permissable if you cant smell it lol, you are correct in what you say in that you are allowed drop on EXISTING pipe work if it is within permissable drop associated with the type of meter you are working from :)
 
From IGE UP1B

5.4 NEW EXTENSIONS/ALTERATIONS TO EXISTING INSTALLATIONS
Before commencing the new work, the existing installation shall be tightness
tested in accordance with clause 5.3.2 and any permissible pressure drop over
the 2 minute test period noted (see also Sub-Section 4.2).
Upon completion of the work to the existing system, the tightness test shall be
repeated and the pressure loss after the 2 minute test period shall be no greater
than that previously measured and there shall be no smell of gas.


This is how it should be done.

This one has been a bit of a bug bear with me. Imagine this ...

One appliance in the home, an old boiler, and it's going to be replaced. Pipework is extended to a new location and the boiler's hung and tested. From the install, you then get a LGSR that says, "1.5mbar drop over 2 mins, no smell of gas", showing the tightness test as passed.

I feel, given the scenario above, the installation has failed the tightness test.

The lines seem to be a bit blurred as to what is considered a new installation vs existing. We have existing pipework as well as new and a new appliance. I can (almost) see where some might consider this an existing installation because of the pipework.

Even if the initial TT showed a drop of 1.5mbar or less given the single appliance, I still believe you can't have any drop in this case.
 
tt before install and having 1.5 drop there is no way I will fit a new boiler to it ,is going to be new gas run !
did safety check last winter and fined 3.5m bar drop ,two weeks earlier company fit new gas fire to existing pipework with
3.5m bar drop
 
There are many engineers out there that do not understand the difference between an allowable drop with exsisting appliances connected and no allowable drop on pipework only or new work.
 
This one has been a bit of a bug bear with me. Imagine this ...

One appliance in the home, an old boiler, and it's going to be replaced. Pipework is extended to a new location and the boiler's hung and tested. From the install, you then get a LGSR that says, "1.5mbar drop over 2 mins, no smell of gas", showing the tightness test as passed.

I feel, given the scenario above, the installation has failed the tightness test.

The lines seem to be a bit blurred as to what is considered a new installation vs existing. We have existing pipework as well as new and a new appliance. I can (almost) see where some might consider this an existing installation because of the pipework.

Even if the initial TT showed a drop of 1.5mbar or less given the single appliance, I still believe you can't have any drop in this case.

if you have 1 or 15 existing appliances you can leave the 1.5mb drop, however this is where i encourage engineering judgement and understanding of why we are allowed the leak in the first place, ie through miniscule drop/leak as it is undetectable, if you fit a brand new boiler and carcass on monday you cant have any drop, but on tuesday when i go to fit the new cooker, i will test and find and be allowed to leave up to 4mb, as it is existing to me, BECAUSE i know what im doing i wont leave this as it is clear there is a major problem on an install that is 24hrs old there will not be microscopic leaks as the boiler is designed differently, but as per the letter of the law i can leave it
 
This one has been a bit of a bug bear with me. Imagine this ...

One appliance in the home, an old boiler, and it's going to be replaced. Pipework is extended to a new location and the boiler's hung and tested. From the install, you then get a LGSR that says, "1.5mbar drop over 2 mins, no smell of gas", showing the tightness test as passed.

I feel, given the scenario above, the installation has failed the tightness test.

You are 100% correct. It has failed as the boiler was a new installation.
The drop is only allowed with existing appliances connected. As the (only) existing appliance has been removed you now have some existing pipework and a new bit of pipe run. No leakage is allowed on pipework, existing or otherwise.
Hope i explained that right as i'm in a hurry to get to the pub.
 
yes it is imprortant to know that the drop is only allowed with appliances included in TT, if you isolate appliances and test carcass and there is a drop that is a big NO NO
 
'Sok Tamz, you explained it perfectly and I'm just home from the pub! *hic*
 
Sound like the sort of tossers I used to see in Plumb Centers all the time before I stopped using em; Snickers work trousers (Regulation bright blue), Walk straight round counter like they own the place and get their gear from the back themselves, rest beer gut on counter while drinking free coffee and telling everyone that will listen that "They're pulled out with work, aint had a day off since 1976, fitted 2 full systems since 8 this morning and still got another 3 to fit before 4 o clock & I don't need to do a tightness test cos I'm the bestest fastest gas fitter in (Insert the town/city of your choice)!" I always do a test before and after every job cos to be honest, I'm just too pretty to go to prison:cool:
These sort of blokes can make you doubt yourself and love to think they look big in the merchants. Rant over!!:mad:

Hahahahaha..that description is so true...as is the OPs methodology.

Always test before doing anything.

That way,you know where your starting from and most importantly,you can indicate to the customer that there are issues before starting,thus keeping yourself in the clear,giving the punter confidence in your work and maybe picking up some extra business in finding and fixing the problem.
 
every landlord cert ive seen says TT test yes/no ,so if its not needed whys it on there,i would always do one ,cos youre the last in there and owt gones wrong your to blame full stop they.ll come after you doesnt matter to me weather its a l mb drop or a four mb drop i still dont feel comforable with any drop as it will only get worse over time ,so i always cover myself
 
the permisable drop is only allowed on existing appliances, if you isolate all the appliances and test the pipework only then there is no drop allowed at all. even if there is on an existing appliance with no smell of gas id find out which applience it is an investigate it. at the end of the day its down to you with this rule. i dont like having a drop at all. test at beggining to make sure its not you that has disturbed the pipework. always good to excercise caution.
 
I am a ng engineer and if I talked to those too knob heads at a job and they gave me those answer's, riddor and hse would be my next conversation, and to the guy who posted this, your spot on with your testing limits. , But you are allowed a pd drop depending on mtr size and pipework size and installation. As long as there is no smell,
 
Second post in as many days.
Just been in plumb centre and was earwigging on two guys talking about testing.
Now I'm a commercial fitter with domestic as well. Granted I have not used my domestic that much over the years but it does get used.

Now the way I was taught was the following;

Upon entering a building to do gas work you do the following:
1 minute let-by at 10mbar
1 minute stabilisation at 20mbar keeping at 20 for that minute
2 minutes at 20mbar.
Anything above 75mbar is medium pressure and requires a different test (this was where I got into conversation with them as they said anything over 82.5 was medium)

Any Drops at stabilisation are fine, any drops within 2 minute test need to be within permitted limit otherwise test fail and you need to find the source

You then do any work IE boiler service, then after the work do the same again.

Now these two guys argued with me for five minutes that you do only need to do a 2 minute test at 20mbar.
Any drop is fine as long as there is no smell of gas.
Also that doing a test upon entry is not needed, and I was wasting my time.

Now somebody please tell me I'm right, I don't have my domestic viper with Me so cannot check, but I will be mortified if I have been doing it wrong all these years!

Honestly these lads have put complete doubt in my mind now, to the point that I'm worried about doing a test today!

Now I am not gas safe registered yet, but isnt it obvious, if there is a drop, there is a leak, which means that there is gas leaking into a house, which means that the installation is dangerous, I also got told by college that the first test must be done as if it is leaking then you must cut the gas off and declare it as unsafe, if the customer does not let you fix it, then you must report it to the gas board, I believe.

And common sense is that if you don't do the test first, then when you work on it, you may cause the already leaking pipe to get worse and of course, the customer will always blame you.
"it was working before you came"
 
Now I am not gas safe registered yet, but isnt it obvious, if there is a drop, there is a leak, which means that there is gas leaking into a house, which means that the installation is dangerous, I also got told by college that the first test must be done as if it is leaking then you must cut the gas off and declare it as unsafe, if the customer does not let you fix it, then you must report it to the gas board, I believe.

And common sense is that if you don't do the test first, then when you work on it, you may cause the already leaking pipe to get worse and of course, the customer will always blame you.
"it was working before you came"


you are allowed a small drop if appliances are connected as stated by others in the post.

you can only "cut the gas off" with permission, if you can not gain permission you then need to inform the gas board. They will then come along and do whatever is needed to make safe, this can include digging up road and cutting gas supply.
 
As many will know, its quite possible to have no perceptible drop but still have a smellable leak.

Equally, in the right circ you could have a drop or a rise which isnt attributable to leakage/let by.
 
As many will know, its quite possible to have no perceptible drop but still have a smellable leak.

Equally, in the right circ you could have a drop or a rise which isnt attributable to leakage/let by.

where can you have a leak that is large enough to smell but doesnt show as a drop on a u gauge? unless you mean on the upstream side of the ECV
 
Last edited by a moderator:
You can have fluctuations with the pipework temperature, but in rare circumstances you could have let by from the ecv and a leak at the same rate, so it shows no drop but there is a leak, in two places. You would be unlucky to get that. But if in doubt, unscrew the governor and spray leak detector into the closed ecv.
 
I would say that I have to contact southern gas to either change the ecv(let by) or governor(working pressure let by) on 1 in every 6 safety checks I do. I do not understand chaps that don't do let by/tightness tests when cariing out safety checks/servicing!
 
havent read all the post but your bang on in my book ryster i do a let by and tightness before starting work so if there is a problem you let them know before you start dont know if its manditory but i do better safe than sorry
 
Devils Advocate.

Who is to say, after you do your let by test then open and close the valve to increase the pressure for your test, that the valve is still holding 100%?

All that is between you and a leaking ECV is perhaps a bit dried out grease!
 
You can have fluctuations with the pipework temperature, but in rare circumstances you could have let by from the ecv and a leak at the same rate, so it shows no drop but there is a leak, in two places. You would be unlucky to get that. But if in doubt, unscrew the governor and spray leak detector into the closed ecv.

if you have a leak rate at the same rate as the ecv lets by this is why you do let by at 10mb and TT at 20mb, so that the leak will show on the TT, as it is being done at a different pressure
 
Take it you not has it before then, trust me it happens. Found the leak to be on a boiler, isolated it then retested, at 10 mbar at first as you rightly say you should, and I had let by. Which didn't show at first. Had transco fit a new ecv, I fixed the boiler. All good after that. That's why I'm saying it's not always so obvious, even with the guide lines and and so on. You have to be confident and know what your doing.
 
generally a tightness test is carried out , if it is a new supply,or the supply has been turned off, if you are going to work on the actual installation or add appliances, or the customer suspects a gas leak (smell of gas). You dont have to do a tightness test if you are servicing an appliance ,unless your company wants you to do one, as you can isolate at the isolating valve test disturbed joints with LDF. Contrary to a previous reply, a tightness test includes a let by test for 1 minute at 7-10mb, a temperature stabilisation for 1 minute at 20-21mb, and a tightness for 2 minutes at 20-21mb / this is for a low pressure installation. Its never been acceptable for a stabilisation test to be done with the let by test (thats for bartdude pubmember attention)
 
generally a tightness test is carried out , if it is a new supply,or the supply has been turned off, if you are going to work on the actual installation or add appliances, or the customer suspects a gas leak (smell of gas). You dont have to do a tightness test if you are servicing an appliance ,unless your company wants you to do one, as you can isolate at the isolating valve test disturbed joints with LDF. Contrary to a previous reply, a tightness test includes a let by test for 1 minute at 7-10mb, a temperature stabilisation for 1 minute at 20-21mb, and a tightness for 2 minutes at 20-21mb / this is for a low pressure installation. Its never been acceptable for a stabilisation test to be done with the let by test (thats for bartdude pubmember attention)
Threads 4 years old hope they'd have worked it out by now
 
Or is it ?? [emoji12]
Maybe I have been given super mod powers to open threads just by looking at them !!!
 
Well Kirk teaches the rules every day,so now I guess he's on a busmans holiday:)

Kirk is spot on, as always.
But teaching every day is no guarantee of accuracy.
I was in a training centre recently, and the trainer absolutely insisted there should be no flexible connection on a suspended heater.
 
Status
Not open for further replies.

Reply to Just had an argument about tightness testing in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

B
    • Friendly
Hi, I've followed this excellent forum for several years but have never posted, so decided I'd better give some details. My status is the upper...
Replies
2
Views
272
I have done pressure test for 2" high pressure pipe line by closing the pipe with rubber plugs at the ends. It was 3 bar and I kept it for 24...
Replies
6
Views
317
Hi, Later this year I am going away for a 2 week holiday and as the weather will be warm there is no need for the heating to be on and arguably...
Replies
1
Views
175
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
469
Hi guys....we have an old Astracast sink top....I think its a composite sink....has a big single bowl. My wife thinks it looks scruffy....looks...
Replies
2
Views
239
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock