I have got a problem with a commercial system. One zone is working fine, the other isn't. There are two vaillant boiler linked together through a low loss header and controlled by a VRC 630 control unit.

When the zone which is causing issues is turned on, the zone valve opens as per the attached picture but the pump doesn't run. I have no power to the pump at all. When both zones via the override feature on the control unit then both pumps run but one zone gets really hot and the other the rads get luke warm. The return is the hotter pipe as well on the zone which doesn't heat up properly.

So I have two questions as I didn't have the time to have a proper look when I was there yesterday. When the zone valve opens should it switch on the pump or would that be controlled by anything else?

Why would the return be hotter than the flow?


com pic 1.JPG com pic 2.JPG

com pic 3.JPG


com pic 4.JPG
 
I have got a problem with a commercial system. One zone is working fine, the other isn't. There are two vaillant boiler linked together through a low loss header and controlled by a VRC 630 control unit.

When the zone which is causing issues is turned on, the zone valve opens as per the attached picture but the pump doesn't run. I have no power to the pump at all. When both zones via the override feature on the control unit then both pumps run but one zone gets really hot and the other the rads get luke warm. The return is the hotter pipe as well on the zone which doesn't heat up properly.

So I have two questions as I didn't have the time to have a proper look when I was there yesterday. When the zone valve opens should it switch on the pump or would that be controlled by anything else?

Why would the return be hotter than the flow?


View attachment 32796 View attachment 32797

View attachment 32798

View attachment 32799
As far as what turns the pumps on, that depends how it's wired.


I cannot see any NRV's ? reverse circulation caused by the lack of those maybe?
 
What could possibly control the pump? I'm new to the commercial world and I am trying to get a better understanding of systems etc.

There aren't any non return valves. Could a weak pump on one zone cause it to reverse circulate easily?
 
the vaillint controller you should see hk 1 (zone number) p (pump)

do you have voltage coming out?
 
the vaillint controller you should see hk 1 (zone number) p (pump)

do you have voltage coming out?

The controller was definitely opening the valves above the pumps but when the valve on the zone which doesn't work was open I was getting no voltage to the pump. Does the controller send voltage to the pump? And not the valve when it opens like on a domestic set up?
 
Yes it sends voltage to the pump and the valve doesn't have an orange wire just two
 
Follow this link to the manual and the wiring diagram.
You're best to read through the info there and then compare it to what you have on-site.
It is really supposed to be wired so the 630 controls the pump and a mixer valve, for example but people can wire things bespoke too. I know I have.
Which two Vaillant Boilers are they and which other controls do you have in the zones?
 
Ok thanks, I will have to allow a couple hours to go back there and have a proper look. There is no mixer valve that I could see. Just need to work out why the pump isn't coming on. The zone valve opened and the boiler fired but the pump for that zone only came on when both zones were on "override" on the programmer
 
Status
Not open for further replies.

Reply to Issues with commercial heating system in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We have a three zone heating system plus water cylinder (OSO Super S 250L) on an Valliant EcoTec 637. Two CH zones and a UFH zone. Boiler is rarely at maximum power rating, even at full tilt. The UFH zone has it's own pump and the other two zones (three storey house) are just pumped from the...
Replies
3
Views
229
I have an older gas boiler HW heating system with a taco circulator pump for each zone that worked fine last season. When turning it on for the 1st time this season I found a problem with the boiler not running on one of the zones. If I turn on the heat to zone 1 I hear the system...
Replies
4
Views
425
Afternoon Fellas If anyone has time to help with this snag it'd be much appreciated. We have a wet-floor system controlled by John Guest UH3 and rather dated Heatmiser DT thermostats. One of the upstairs zones is combined for the bedroom/dressing room. So that's 2 rooms, 2 manifolds, but one...
Replies
2
Views
446
  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always amazed at the water pressure so on the odd occasion that the water was only luke warm it was easily forgiven, but over time we have come to realise that...
Replies
8
Views
375
Hi I have a 4 zone / 7 loop UFH system. 2 zones (4 loops) always get hot when the system is on when the zone thermostats and actuators are off. The video posted shows when I turn on another zones the flow meters drop. (Kitchen prep and kitchen TV are the issue, two at either end of the...
Replies
14
Views
1K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock