Help needed again problem on the above boiler. Hot water works fine however the heating comes on temp on display goes to 70-80 and the boiler turns off.
None of the flow or return valves get hot although the main heat exchanger does.
DV motor operates, even with the motor disconnected and the DV pin manually pushed in the boiler does the same..... what is causing the boiler to overheat and switch off????
Pump operates, tried another pump same fault.????
 
Sure the isolation valves are clear and haven't broken inside?
Could be blockage in flow or return too.

What's the system pressure reading?

And of course the regular question, are you a GSR?
 
I’d check the system filter if it not full of muck, I’ve not worked on one recently but I think they may have a mesh filter in the flow or return valve check that.

I know the earlier models had an issue with the diverter valve.

Check the resistance on the CH thermistor and if possible link out any control.
 
Thanks for your help guys. The flow and return valves are opened..... could they break in closed position if they haven’t been touched by the customer???
The water pressure is 1.5 bar.
Will open up and visually check the flow and return valves, will also check the built in filter if I can find it....... the boiler reaches temp and just a down so I assume the thermistor is ok....
Just never had a circulation issue like this where the flow valve doesn’t even warn up
 
Hello All a bit of an update....... flow and return isolation valve are open on the boiler.
Then.... I pressurised the system to 1.5 bar and isolated the magna clean valves, I drained down the magna clean then when I opened up the top magna clean isolation valve the magna clean started to fill up, so I closed it, then with the top magna clean isolation valve closed I opened up the bottom magna clean isolation and there was no water coming through, both magna clean isolation valves work......is that proving there is a blockage in the system? Hence the boiler heating circuit overheating?
 
Yes on the return........ just can’t get my head round why the boiler in heating mode does not get rid of some heat even if it’s 1 metre of warmth from the flow pipe?????
 
I'd say definite blockage, are you sure the blockage isn't in the magna clean? Opening the bottom valve and getting no water through would suggest either the valve itself is blocked or the blockage is close by.
 
No heat transfer to Dhw.......
Both magna clean filters are opened, I removed the push fit magna clean and visually checked the bottom isolation valve
 
No heat transfer to Dhw...
Both magna clean filters are opened, I removed the push fit magna clean and visually checked the bottom isolation valve
But if your getting no water through the bottom valve then that would suggest a blockage between the filter and the last rad on the system.

Actually, what side of the system is the bottom valve on? The return to the boiler or the return from the radiators?
 
Return to the rads

EEE4DF62-B69E-4992-84CB-BDDFA397A013.jpeg
 
I'd be tempted to cut the pipe below the elbow circled in red. Then check the pipe leading up to the magna clean. It is unusual for a 22mm pipe to block though. There isn't anything stupid like an isolation valve under the floor in the cupboard is there?
 
And the magnacleanse valve is definitely open and not blocked. Easy way to tell would be loosen the magnclean valve nut at the bottom and move slightly off the olive. I've had those snap internally... Though that was on the old ones to be fair.
 

Reply to Ideal logic + combi 30 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
222
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
300
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...