Hi all,


I have a Wallstar Oil Boiler 12/15.

A few years ago, it developed a problem where it would fail and it required a manual reset on the boiler controller outside.

I didn't know much about oil boilers back then.

I have had a number of 'heating engineers' and so-called specialists to it but so far none have cured the problem.

I decided to figure out how these things work for myself to give me a greater understanding of what is going wrong.

So, this is what happens.

When there is demand for heat, the boiler from cold (in a none failed condition) fires up without the slightest problem.

It runs to get the water hot, shuts off, starts again as water cools etc... normal running.

Then, for no apparent reason, say after 30 mins or 1-hour etc, it will fail to ignite. This triggers the fail and requires a reset on the controller.

Sometimes the reset will work and the boiler will fire up and continue, sometimes it will just keep failing.

If I leave it to cool down for a few hours, it will generally fire up as normal (after clearing the fail with the reset).

It seems that when the boiler is very cold, there is no problem. If it is also very hot, it doesn't seem to be a problem, but in-between is where it fails.

The engineers etc have changed the nozzle, plastic pipe, solenoid, controller and filters and the problem persists.

Now then, things I have checked.

When starting, the pump runs (pulsing of the oil can be seen in the clear pipe). It does its 10-15 second purge then the solenoid clicks and the oil flows, boiler lights.

All good.

When it fails, it NEVER fails when running, only on re-starting during the normal heating cycle.

It goes through the normal procedure as above, solenoid clicks open, oil is seen to flow and then within about 3 seconds it shuts off with the fault.

Now, as I can see the oil moving, it isn't the solenoid, it’s not air as I can see the oil in the line, it’s not a blockage as again I can see the oil moving in the line.

It seems to be the igniter.

I have had it apart, cleaned the electrodes, checked the gap 3mm+-0.5mm and level with the top of the nozzle.

It's not the flame detector because when it fires up, you can hear it ignite and it doesn't get that far.

Does anyone have any experience with this same fault and how was it cured?

Could it be the transformer (that creates the spark), the leads to the electrodes or the electrodes themselves.

Puzzling as it only fails when the boiler has been running. The temperature in the burner cabinet is always quite cool, but the fault is definitely heat related!

This must be a known problem, on my street 12 houses, we all have the same boiler and 7 of them have the exact same problem.

Surely someone must know what the problem is.

Oh, the boiler is about 12 years old.

Thanks.

Martin
 
With all the parts you've had engineers randomly change you could of bought a new burner. That's another option, many decent engineers have spare burners for problem child situations like this. Maybe if they have a sound Sterling that could be fitted for a week, at least then you'll know if it's a fuel or burner problem. If that's not an option then they need to go through what I've said to rule out possibilities. If I attended and couldn't find the fault first time, after replacing the pump as you said was then I shouldn't be charging you for return visits
 
left heating engineer a voicemail on Monday morning and tried ringing him during the week. Not heard anything. Haven’t paid anything yet so I know he’ll get back at some point.
Boiler still playing up.
Yesterday morning it wouldn’t start, tried several times ended up bleeding oil line and it started.
Yesterday afternoon wouldn’t start, again tried several times. Tried bleeding oil line again but still wouldn’t start even with 2 inch air bubble. Left it 10mins and it started.
 
The pump has recently been replaced and I'm assuming the coupling along with it and seeing as it's the same problem before and after I'd suspect neither are the issue. Obviously all air needs to be removed from the pump for reliable ignition, a gauge usually fluctuates with air in pump. The motor is running and assuming the coil is sound and clicks then atomization of fuel at nozzle needs to be checked along with spark. If the pump is producing operating pressure and coil opens but no fuel out of nozzle then it could be a dodgy nozzle, a blocked/partially blocked HP line or a dodgy NRV (although I'm not sure if the Sterling has one). If you have neat fuel out of nozzle next check is spark.
 
Never did get to the bottom of this issue.

Decided rather than spend/waste money on trying to fix it.

We’ve gone down the route of having a new boiler, I purchased Worcester Greenstar heatslave II through staff discount scheme we have where I work and then paid an accredited Worcester installer to install and commission boiler.

It’s been installed 11 days and no problems at all. Starts every time and we now have constant hot water.
 
Thanks for updating us. Im sorry to hear you made that decision, although it does suggest the problem was never fuel related and was within the burner, unless the installer rectified a proper when installing.
Not a fan of combi boilers personally but if I remember correctly there's just the two of you and they are decent boilers.

Again thanks for updating us.

Many thanks, Simon
 
Thanks for updating us. Im sorry to hear you made that decision, although it does suggest the problem was never fuel related and was within the burner, unless the installer rectified a proper when installing.
Not a fan of combi boilers personally but if I remember correctly there's just the two of you and they are decent boilers.

Again thanks for updating us.

Many thanks, Simon

Hiya, only things that have changed regarding the fueling are that the boiler is now sat on the floor rather than it being in the wall so that the pump doesn’t have to lift the oil up and the fire valve has been replaced with new one instead of the HRM version with non return valve. The installer let me take off all the parts that had been replaced, which I thought was decent of him as he could have kept them and used them.

I think we will use less oil especially during the summer as both of us are at work and we have boiler set to only come on in morning and evening to give us hot water When we need it, instead of it being on all the time and keeping the heatslave tank at constant temp.
Thanks for all your help.
 
Thanks for updating us. Im sorry to hear you made that decision, although it does suggest the problem was never fuel related and was within the burner, unless the installer rectified a proper when installing.
Not a fan of combi boilers personally but if I remember correctly there's just the two of you and they are decent boilers.

Again thanks for updating us.

Many thanks, Simon

SJB, you may have a few comments to make re Stored combi boilers output and flow rates, there are numerous queries on here re gas combi flow rates as well.

I am looking at a brochure for a Firebird C35 combi boiler and to quote "D.H.W. Guide Performance in litres/min (120 litre draw-off at 40C deltaT) 20". It has a primary store of 40 litres heated to 78C.
Do you know if this guide performance is typical for oil fired combis? and also how is this number of 120 litres arrived at?
My simple calc shows that if one assumes cold water at 10C, then with a deltaT of 40C the stored cylinder will give a volume of 40*(78-10)/(50-10), 68 litres at 50C (which should give 20 LPM but only for 68/20, 3.4 mins, the burner should kick in at 73C and then the 35kw boiler will give a continuous flowrate of (35*860)/(40*60), 12.54 LPM.
My main query is this 120 litre figure?, the flow rates are simple to understand IMO.
 
120 litres to fill a bath. They want to give the idea that you can fill a bath before the store gives out. It doesn't last though.
 
Its to do with the amount of stored energy in the thermal store. 120 litres is what can be provided at that delta until the store depletes.
Gas is different, they ramp up to full output and can modulate down for the lower load of CH.
Because up until recently domestic oil burners are fixed rate they have to use a store to aid in HW production.
If my understanding and maths is correct then 20 litres per minute at a delta t of 40°c would require an input of roughly 50kw but as said above if there was no thermal store and you had a nozzle size and pressure to input 50kw for HW then the CH side will also have the same input, obviously being massively oversized.
Perhaps when fully modulating oil burners take off there will be no need for a thermal store.
Thats my understanding, if I'm wrong then please correct me.
 
My calcs show that a 70 litre store would be required to give that 120 litres, the store is definitely required as you say because of the fixed boiler output and if you only needed a flow rate of 4 or 5 LPM then the boiler would be constantly cycling on/off. A continuous 20 LPM at a deltaT of 40 requires 56kw, the more normal quoted deltaT of 35C would require 49kw.
 
Can you break down your calculation method.
Bare in mind as the store temp decreases the burner will engage and supply additional energy, until a certain point where the input cant match the output.
 
OK, you are mixing cold water (at say 10C, but you can use your own number) with hot water at 78C (stored water temp) to give a mixed temp of 50C so every 1 litre of water at 78C will give 1*(78-10)/(50-10), 1.7 litres at 50C, so a store of 40 litres at 78C will give 68 litres at 50C. Additional energy will be supplied when the store reaches 73C but store will just about be depleted then and a 35kw boiler will then have a flow temp (to the store) at 20 LPM, of ((35*860)/(20*60))+10, 35C. The only way to get a sustained flow rate at 50C after the store is depleted is to reduce the flow rate to 12.54 LPM (35*860)/(60*(50-10).
 
I presume the Firebird has a mixer to reduce the temp to ~ 65c and then the shower or whatever will reduce it to 50C but it doesn't matter as the stated conditions are water from a stored temp of 78 to water at 50C (from 10C) so the ratio is 1.7:1.

Thinking back again to the burner re firing at a store temp of 73C, if the probe picks this up very early in the draw off then you could be adding in energy early on so that will have the effect of increasing the thermal store so the 120 litres may actually be not too far off the mark as it would only need a additional ~ 2.5 kwh to achieve this but needs a bit more thought.
 
Last edited:
So have I done the maths correct.
Say we have a store of 50 litres with a temperature of 80°c and we want a delta t of 35°c and an incoming temperature of say 12°c
So 1 litre will provide 80 ÷ 35 = 2.28 litres, so 50 × 2.28 = 114 litres?
 
Not quite, the calc IMO is 1 litre will provide (80-12)/(47-12) or 1.942 litres @ 47C so 50x1.942= 97 litres. I will show the actual "long" calc when i return in ~ 2 hrs.
 
yes I slipped up. Your figure is correct.
Yes please show me later and also explain where you got this method from and how accurate it is mate please.
 
The following is the heat balance method, I just use a shortened (my own) version above but it is 100% accurate.

L Litres = volume of cold water that must be added to 1 litre of hot water to give you the required mixed water temperature.
So: (1*80)+(L*12) = (1+L)*47
80+12L = 47+47L
33 = 35L
L = 33/35 or 0.942 litres
So 1 litre of hot water at 80C will give 1.942 litres of mixed water at 47C from cold water at 12C.
 
I presume the Firebird has a mixer to reduce the temp to ~ 65c and then the shower or whatever will reduce it to 50C but it doesn't matter as the stated conditions are water from a stored temp of 78 to water at 50C (from 10C) so the ratio is 1.7:1.

Thinking back again to the burner re firing at a store temp of 73C, if the probe picks this up very early in the draw off then you could be adding in energy early on so that will have the effect of increasing the thermal store so the 120 litres may actually be not too far off the mark as it would only need a additional ~ 2.5 kwh to achieve this but needs a bit more thought.

Think I may have finally come up with a reasonable calc for the above but is based on the boiler firing up almost immediately. The 78C high temp flow rate from the store will only require a flow rate of 20/1.7, 11.76 LPM from the store until it has fully depleted its 40 litres, the 35 kw boiler will also be heating the water to almost 53C at this flowrate so by the time the 40 litres at 75C is depleted then the store will be full of water at 53C = 43 litres at 50C, so 68 litres at 50C after mixing from the 78C store plus 43 litres at 50C with a little mixing gives a total of at least 111 litres at 50C?.
 
Last edited:
I'm going to trust your maths and judgement and say you could be correct.
Most oil combis state a maximum draw off at 40°c delta t, so there will come a time I assume and as I said above where the HW output temperature will start declining until the store is recharged.
 
It certainly will fall off because if the demand is kept at 20 lpm then once the first store is drawn off then the second store flow rate will rise to 20 LPM (practically no mixing) and once this is depleted (at 50C) the 35 kw boiler will only give a steady temp of 35C (35*850/20/60)+10), the flowrate must be reduced to 12.54 LPM, (35*860/40/60), to give a steady temp of 50C. In other words a flowrate of 20 LPM @ 50C will only be maintained for 5.5 minutes, 111/20, and the temp will then fall to 35C if not throttled in., I suppose that really isn't too bad as it will (almost) fill a bath or give a super power shower of 20 LPM for over 5 minutes. The key to the increased (temporary) flow rate is the burner cutting in almost as soon as there is a flow demand.
 
Last edited:
I think I saw somewhere that the Firebird store temp has a hysteresis of 5C so the burner may not cut in instantly on flow demand? Also one would think that the very nature of a store would allow a draw off of maybe 5 litres or so depending on where the probe is positioned. It would be interesting to get some feed from someone with a stored combi oil boiler.
 
All stats have a hysteresis but I couldn't tell you how wide it is on the thermistors or stats used. If you look at the flowchart for combi boilers you'll see a series of relays and stats and other components on PCB's. Of all my manuals stored show flow switches bringing on the boiler and pump when a hot outlet is opened. The store stat can also bring on the boiler to heat when no outlet is open to top up.
Another thing I will say is the newer firebird combis don't use a flow switch but instead another thermistor on the cold inletto PHX, which detects a change in temperature and brings the boiler on that way.
 