Discuss GRANT 26 COMBI OIL FIRED BOILER. INCONSISTENT HOT WATER in the Oil and Solid Fuel Forum area at PlumbersForums.net

Messages
1
Hi,
Firstly, I am neither plumber nor heating engineer, just a willing diy, have a go guy.
I have a Grant 26 oil fired combi boiler which started continually leaking water from the prv to the outside. The pressure was at 1 bar until the heating system cut in, when it would increase to 2.5 and then blow the prv.
I depressurised the system, checked the EV standing charge was correct at 1 bar [as per manual] also that it held the pressure in the tank and at the valve.... a.o.k.!
I decided to replace the plate heat exchanger, thinking this was the only cause of the constant build up of water pressure in the ch system [i.e. maybe an internal leak/split between hw & ch etc.]
Presto! no more prv leaks or excessive pressure build up, so far!
However! When installed, new [3 years ago] the water temp. on both dhw and chw systems worked fine, until this year [well before the prv leaking issue started] when running the bath, [which we do every day] the hw starts off hot then reduces to just warm, after a short while, basically not holding a constant temp. after running for a while!
Is it advisable to fit a mains water regulator, in case it's above the recommended 8 bar max.? Is there a boiler problem? Is it a service issue? Can the actuator have anything to do with it? Any answers or advice would be greatly appreciated.
p.s. The central heating is working fine.
Thanks for any help guys
 
First if your boiler was installed/ commissioned by a Grant registered engineer and has been serviced its still under warranty (5 years)
Water pressure needs checking before fitting a prv.
Burner cut in as soon as tap opened?
Continue to run when tap turned off?
 
Simple things first, 26 kw will give you a flow rate of ~ 11.6 LPM at 40C and/or 10 LPM at 45C, so, just in case the mains pressure has increased dramatically, measure the flowrate/temp while filling the bath to rule this out.

OF boilers have primary stored water so this will give a higher flow rate for a short period but the continuous flow rate ( I think) should be then constant as above once this is exhausted, there is also a store on/off switch on the boiler, when this on the boiler will maintain this stored water at its stored temp of ~ 75C. These boilers may also have TMV to maintain the exit temp at 60C so check this out in case faulty.
The Grant combi I saw also had a DHW pump (2 pumps internally) which circulated the water through the DHW Hx (no diverting valve) but I think they just use one circ pump now with a diverter valve. Maybe thermistor fault somewhere. As above, check boiler fires up and remains fired up while drawing off water. Faulty flow switch??.
 
Morning John
Grants still have 2 pumps DHW pump is on right at bottom.
Thermistor faults are known but rare if they are playing up it's normally board.
As there are a number of possibilities maybe a competent oil engineer?
Unless OP is in a very hard water area in which case some frm of water treatment needed or healing system not very clean I suspect there was not much up with plate to plate
 
Hi,
Firstly, I am neither plumber nor heating engineer, just a willing diy, have a go guy.
I have a Grant 26 oil fired combi boiler which started continually leaking water from the prv to the outside. The pressure was at 1 bar until the heating system cut in, when it would increase to 2.5 and then blow the prv.
I depressurised the system, checked the EV standing charge was correct at 1 bar [as per manual] also that it held the pressure in the tank and at the valve.*** a.o.k.!
I decided to replace the plate heat exchanger, thinking this was the only cause of the constant build up of water pressure in the ch system [i.e. maybe an internal leak/split between hw & ch etc.]
Presto! no more prv leaks or excessive pressure build up, so far!
However! When installed, new [3 years ago] the water temp. on both dhw and chw systems worked fine, until this year [well before the prv leaking issue started] when running the bath, [which we do every day] the hw starts off hot then reduces to just warm, after a short while, basically not holding a constant temp. after running for a while!
Is it advisable to fit a mains water regulator, in case it's above the recommended 8 bar max.? Is there a boiler problem? Is it a service issue? Can the actuator have anything to do with it? Any answers or advice would be greatly appreciated.
p.s. The central heating is working fine.
Thanks for any help guys
Not sure if you've got to the bottom of this but before you fit a pressure regulator just get a pressure gauge on the garden tap and that should tell you if you need one.
As for the reduction in water temperature, I would think that it's a faulty fow switch.
Good luck with this.
 

Reply to GRANT 26 COMBI OIL FIRED BOILER. INCONSISTENT HOT WATER in the Oil and Solid Fuel Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
123
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
129
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
274
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
442
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock