Hi,

I wonder if someone can help answer some questions please.
In our house we have two boilers : a 37kw and a 30kw.
The max flow rate required for the two is 4.1 and 3.24 cu m/h (7.34 cu m/h)

this exceeds the meters limit of 6 cu m/h.

What options do I have resolve?

I have been told that a U6 meter can go up to 64kw total. So one option is to downgrade the 30kw boiler to 25kw. However, if we do that, the flow requirement is still more than 6 cu m/h. So how does that work? (what is the relationship between kW and flowrate?)

Is it possible to change to a different meter with a qmax of 10 cu m/h. (without going to a U16) :: Would that solve my issue?

I am in the process of getting a GT1 test done to establish what the current pipes to the house are capable of supplying.

Incidentally the 30kw should never have been installed but that is done and due to unforeseen circumstances, are now in a position where I have to deal with it.

Any suggestions/explanations on how this all works would be greatly appreciated.

The energy company is saying that I may need to upgrade to a U16 meter which may require new pipes from the streets. This seems overkill to me, so I am looking for a sensible solution....

I have noticed meters being designed with a U6 or a G6, is there a difference? So a G6 diaphragm has a flow rate up to 10 cu m/h, which would meet one of the requirements, as well as work with existing standard connections...

thank you kindly for your time
 
Get a u16 fitted you will be fine then

Any other appliances on gas ?
 
Hi Shaun,

Thank you for your msg. There are no other gas appliances.

It may be more cost effective to downgrade the boiler. The chap from SGN was just doing the GT1 test this afternoon. We'll see where we get to........

Thanks,
 
Do you know what boilers they are ?
 
You need a U16 installing unless - as you say - you reduce the Boiler sizes.
Why do you have Boilers that big?
Are they Combination Boilers?
How big is the house?
 
As others have said a U16 meter is needed some boilers can be down rated in the parameter settings what boilers are fitted ? Cheers kop
 
Status
Not open for further replies.

Reply to Gas Supply and Gas Meter Issue When Running 2 Boilers in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Had conventional boiler and tanks removed last year and new combi fitted and just recently had it serviced but the guy who did it has given me a gas warning notice for at risk as the outside wall meter box has been drilled through for the gas pipe to go horizontal straight to the boiler. The...
Replies
9
Views
697
Hi all, Does anyone have any feedback as to which is best. Running the pipe from the outdoor gas meter to a new boiler on an outside wall or run the pipe under the floor (suspended timber) which is our existing setup and the new boiler is being sited in same location as old. I ask just in...
Replies
15
Views
1K
I had a boiler check today all went well, and then he went to check on the gas meter which is in my larder in the kitchen high up on the wall. That wasn’t too much of an issue, although the gas engineer did say that it wasn’t a common place to have it, but it was there when we moved in so...
Replies
1
Views
663
I have a domestic gas meter located at one side of my building and my boiler/cooker (only 2 gas devices) on the other side of the building. There is currently a 28mm gas pipe from meter to the boiler which is approx 25m and a further 5m to the gas cooker. My gas engineer is saying that the...
Replies
18
Views
3K
Hi, I am currently having issues with an Ariston Combi A series boiler giving an E08 - "No water in primary circuit" error code, the circuit is holding water pressure fine, the pump runs and seems to have a bit of force behind it and I have replaced the pressure sensor but the problem persists...
Replies
0
Views
327
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock