Hi,

I had a new boiler installed at the beginning of 2018 and the plumber installed a Dab Evosta circulator. A few nights ago it started making a high pitch squeak which can be heard throughout the house. I therefore looked it up and found the instruction manual.

I tried bleeding the pump but no air came out, only water.

I did, however, notice that the pump was set to “Constant Differential Pressure” which, according to the manual was for underfloor heating systems. I have radiators.

When I changed the setting on the pump to “Proportional Differential Pressure” which appears to be for radiators the squeaking stopped!

My concern is why the plumber initially set it up as Constant as opposed to Proportional? Have I changed anything significant? Is it going to have an adverse affect? Would the initial setting have had an adverse affect over the past year and a quarter?

I have attached some photos.

Thank you in advance.

Tom

51384760-153A-44FD-85C9-A1B7A82FA50E.jpeg


73B2F2B6-4701-4692-A95C-8D10AA0CDB5B.jpeg
 
IF its like the one in the attachment then it has three constant curves, ("fixed speed"), speed 3 is 7M which is very high if it was set to this, speed 2 is 5.5M which should be more than adequate for most houses.
It has 6 proportional pressure settings PP6 is the highest at 4.8M (probably the one to go for) and PP5 is 3.8M which may be OK for a 8 rad house or so. The proportional Pressure setting (PP) will mean that the pump speed/head falls with the shutting off of zones or TRVs and saves power.
 

Attachments

  • DAB EVOSTA 4-7.pdf
    967.1 KB · Views: 3
Last edited:
If the system works okay with a lower pump setting that's probably a better one to use in many cases.

It is not uncommon for installers to pay little attention to the details of pump curves and settings, radiator balancing, etc.. I guess that they subscribe to the philosophy that as long as all the radiators get hot the job is done. They also often to leave the settings higher than strictly necessary, 'to be on the safe side'. This is particularly the case when an existing system is being worked on rather than installed from scratch.

To be honest, I have some sympathy with them. Doing a proper heat loss calculation for each area and then balancing and getting the deltaT values just right for a house takes hours not minutes and needs to be done when the weather is cold, which is not when a planned installation happens. Very few houseowners want to pay the several hundred pounds this sort of commissioning/service cost and it may make relatively little difference in practice anyway.
 
Yes of course, plumbers have to make a few bob as well so will generally set to constant curve (fixed speed 2 or 3). My own (Wilo), I,ve set to PP4 (4M) and it averages around 16W, fixed speed 2 = 25W & fixed speed 3 is 40W so saving assuming ~ 2700 circ pump running hrs/year, 24 kwh/annum, say £5 or, 65 kwh say £12. Of course if *** million people used the PP setting(s) it would save a power station or two.
Generally, I would say that you won't get many call backs if you set the pump to a PP setting of 5M or so.
 
Thank you everyone.

It’s a 4-bed house with 13 radiators and 2 heated towel rails. Do you think the PP6 setting will be sufficient or should I raise to CP2?

Or is it a case on continually increasing the setting until all the radiators are sufficiently hot?
 
If your boiler has a automatic by pass valve (ABV) then it is recommended that you do not use PP but use the fixed speed or constant pressure modes if fitted so fixed speed 2 or 1 may be more appropriate. What is the Wilo pump used for ??
 
If your boiler has a automatic by pass valve (ABV) then it is recommended that you do not use PP but use the fixed speed or constant pressure modes if fitted so fixed speed 2 or 1 may be more appropriate. What is the Wilo pump used for ??

The Boiler is a Grant 26-36 Utility Pro. Not sure if it has an ABV? Will change to CP2 and see if that gets all the Radiators hot enough.

The Wilo pump is for the underfloor heating in our Conservatory. That hasn’t worked all winter but haven’t have the money to get anyone out to look at it. :-(
 
You probably havn,t a ABV (oil fired boiler). That pump should still be under warranty so should be replaced FOC if noisy at the highest setting, you shouldn,t have to settle for a lower setting and possibly lower rad output because of this.
 

Reply to Evosta Circulator Squeeking, Setting Query in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
207
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
256
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock