Rob Foster

Esteemed
Messages
2,083
When a 25 kw condensing boiler is going full tilt in the winter what volume of condensate water might be discharged per hour ? Obviously an overflow pipe will cope. Anybody any ideas. It could be 20KW or 30 KW I am looking for a ball park volume. Many thanks
 
Types of work ....1 Contract ch installation new build, 2 medi-gas contracting, 3 local plumbing/domestic ch installs but in a quite tight area - no adverts just word of mouth so we knew the customer and they us. 1st 2 profit is all down to margins and speed 3 is down to reputation word of mouth. Beware you have to get from one man (you) to over 5/6 very quickly or you end up not earning anything yourself Young men for 1, steady fellas for 3 and anybody who was prepared to work xmas easter and bank holiday for 2
 
Hi fixitflav thanks for that - how did you calculate it may I ask - in awe of you on this one
Originally I used a hand calculator and seem to have dropped a cod, it's actually more like 3.8 l/h.
Calculation below. I used Mathcad, but pleasantly surprised it copied in OK. Don't worry about apparent lack of conversion factors etc, Mathcad takes care of that for you. I've made one or 2 assumptions, as natural gas is not pure methane, but it won't be far out for water produced. Be interesting to compare with maker's figure, to get an idea about what fraction condenses. Come back if you need more.

upload_2018-8-7_19-17-40.png
 
Originally I used a hand calculator and seem to have dropped a cod, it's actually more like 3.8 l/h.
Calculation below. I used Mathcad, but pleasantly surprised it copied in OK. Don't worry about apparent lack of conversion factors etc, Mathcad takes care of that for you. I've made one or 2 assumptions, as natural gas is not pure methane, but it won't be far out for water produced. Be interesting to compare with maker's figure, to get an idea about what fraction condenses. Come back if you need more.

View attachment 34144

2.347m3/hr not 2.429

also that figure is a constant 25kw on a heat/system boiler which even at the middle of winter wont run constantly on full

if its a combi that figure will be lower also due to the output
 
Depends on the makeup of the gas and the assumed boiler efficiency, but either is near enough in practice.

OP said "when the boiler is going full tilt".

Yes but I would be surprised if it went for longer than 30 mins on full tilt will modulate down to half power

Also return temp matters a lot
 
Rob, when you had 20 fitters working for you what sort of work were you doing?
Rob, when you had 20 fitters working for you what sort of work were you doing?
I did not mean to end up with 20 or so. I had semi retired at 40 ish , myself and 2 others did really well in the late 80's + 90's building and property. I was stood in a pub ! fella next to me was doin xword and asked whats a greek cheese ? conversation ended with him asking me to help him with a ch installation next day. When we did it he was impressed and asked how much I wanted - I told him - Jimbo said he didnt earn that rate himself. So it ended up with me getting the work for him and about a score of his really experienced older pals at my idea of rates - it worked. wacky story but all true
 
Yes but I would be surprised if it went for longer than 30 mins on full tilt will modulate down to half power
So would I, but my calc is for an instantaneous rate. Reminds me of introduction to rates of change and differential calculus a few (!) years ago. Sir told a tale of a woman being stopped by a cop and told she was doing 45mph. Don't be silly, officer, she said, I only bought the car 10 minutes ago.
Just out of curiosity, how do you get 2.347m3/hr in #12?
 
So would I, but my calc is for an instantaneous rate. Reminds me of introduction to rates of change and differential calculus a few (!) years ago. Sir told a tale of a woman being stopped by a cop and told she was doing 45mph. Don't be silly, officer, she said, I only bought the car 10 minutes ago.
Just out of curiosity, how do you get 2.347m3/hr in #12?

25/10.65
 

Reply to Condensing Boilers - what volume of codensate is discharged in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
3
Views
134
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
203
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
131
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
199
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
2
Views
148
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock