Hi, I’ve had a problem recently since I moved the pipes to my radiator from one side of the room to the other (in a bungalow so pipes go through ceiling into loft).
Even with the CH turned off I still get hot flow pipes to all radiators, the rads are just slightly warm at the top & all return pipes are cold. In this warm spell I’ve had to turn off all the rad valves on the flow side to get rid of the heat out of the pipes, but as soon as I open them the flow pipes heat up again. I have a standard oil boiler & 3 port motorised valve in my system if that helps for any info. Thanks in advance for any help.
 
Sounds like your 3 port valve is faulty (Letting By) depending on age may be better to replace complete valve, as it could be the motor or the body that is at fault, but get it tested first as other controls could be causing the fault, Controller, Room stat,
 
Hi, I’ve had a problem recently since I moved the pipes to my radiator from one side of the room to the other (in a bungalow so pipes go through ceiling into loft).
Even with the CH turned off I still get hot flow pipes to all radiators, the rads are just slightly warm at the top & all return pipes are cold. In this warm spell I’ve had to turn off all the rad valves on the flow side to get rid of the heat out of the pipes, but as soon as I open them the flow pipes heat up again. I have a standard oil boiler & 3 port motorised valve in my system if that helps for any info. Thanks in advance for any help.
All the heating return pipes must be commoned before joining the HW return pipe, otherwise your symptoms will happen. If everything was OK before you moved the pipes, is it possible it's now piped wrong?
 
All the heating return pipes must be commoned before joining the HW return pipe, otherwise your symptoms will happen.
If reverse circulation is occurring then the return pipe will get hot, not the flow which is what the OP is experiencing.
 
Leave all the rads on except the one you repiped. If prob goes away you've got your return from this rad connected wrong
 
If reverse circulation is occurring then the return pipe will get hot, not the flow which is what the OP is experiencing.
If the connection is wrong, one rad (or set of rads) gets warm on the returns, the other rad (or set) gets warm on the flow. But it could be either way round, depending on which way round the connections are. So if all the flows are warm and all the returns cold, after running like that for a while, that would rule it out. But I'd still be interested in OP confirming the pipe routing is correct. And is he sure which are the flows and returns? Maybe he is, but I wouldn't know offhand on my rads, if I needed to find out I would have to switch on from cold and feel the pipes.
 
ok, I’ve been in the loft & traced out the pipework & im connected correctly with flow/return. I thought it may be the motor in the valve so replaced that (cheap option as was only a tenner) but problem still the same. I have recently installed a new Salus IT500 thermostat. I’m now wondering if it may be the valve not quite operating fully & is passing as suggested.
Thanks for the help so far by the way

E55CF310-D401-487F-84BB-F6143F7B4637.jpeg
 
ok, I’ve been in the loft & traced out the pipework & im connected correctly with flow/return. I thought it may be the motor in the valve so replaced that (cheap option as was only a tenner) but problem still the same. I have recently installed a new Salus IT500 thermostat. I’m now wondering if it may be the valve not quite operating fully & is passing as suggested.
Thanks for the help so far by the way

View attachment 33633
OK it seemed like a coincidence that the problem started after the pipes modded, but coincidences do happen!
These 3-port valves can give problems, mine is a Honeywell clone, with a rubber ball on a lever, covering either of the ports, don't know if yours works same way. Had one where the lever broke off the shaft, another where the shaft through the ball fell out - poor design, just threaded in. I put Loctite on it and rivetted the end over, then I got symptoms like yours. I had to bend the arm slightly to cure it, took several tries and was a pita. It might be worth dismantling yours and see if it gives any clues.
 
Ah ok fixitflav, thanks for that, I’ll get the valve out tomorrow & have a look at it or if needed get it replaced
 
as i said earlier just turn off the rad you repiped and leave the rest on. if prob goes away youve got your return wrong on your repiping. why are you taking out the 3 port. just start everything from cold with hot water on only and feel the heating pipe as far away from the 3 port as you possibly can, youll soon know bif 3 port is letting by
 
as i said earlier just turn off the rad you repiped and leave the rest on. if prob goes away youve got your return wrong on your repiping. why are you taking out the 3 port. just start everything from cold with hot water on only and feel the heating pipe as far away from the 3 port as you possibly can, youll soon know bif 3 port is letting by
Good point, easier than taking the valve apart. I should have thought of that as that's how I checked mine when getting it to work properly. But the pipe shouldn't get warm more than 2-3 ft from the valve should it?
 
as i said earlier just turn off the rad you repiped and leave the rest on. if prob goes away youve got your return wrong on your repiping. why are you taking out the 3 port. just start everything from cold with hot water on only and feel the heating pipe as far away from the 3 port as you possibly can, youll soon know bif 3 port is letting by
Fair comment, easier/quicker option than removing the valve so will give it a go & let you know how I get on
 
as i said earlier just turn off the rad you repiped and leave the rest on. if prob goes away youve got your return wrong on your repiping. why are you taking out the 3 port. just start everything from cold with hot water on only and feel the heating pipe as far away from the 3 port as you possibly can, youll soon know bif 3 port is letting by
With the repiped rad switched off (fow & return), CH turned off, just the hot water on, the flow pipes to every other rad in the bungalow heated up inside 10mins. So do you think the next step is the valve passing?
 
With the repiped rad switched off (fow & return), CH turned off, just the hot water on, the flow pipes to every other rad in the bungalow heated up inside 10mins. So do you think the next step is the valve passing?
Did you feel the pipe from the 3-port valve to the rads, as garygvl suggested?
 
Did you feel the pipe from the 3-port valve to the rads, as garygvl suggested?
Yes, felt it in the loft just before it’s tee’d into the pipe that provides the flow to the rads & it’s hot. But wouldn’t that be the same as the flow pipes coming down to the rads from the loft?
 
Yes, felt it in the loft just before it’s tee’d into the pipe that provides the flow to the rads & it’s hot. But wouldn’t that be the same as the flow pipes coming down to the rads from the loft?
Not sure what you mean without knowing the layout, but the pipe going to the rads shouldn't be hot if the controls are calling for HW only.
I would feel the pipe (the one to the rads obviously) at the 3-port valve and work further along towards the rads. It might be hot close to the valve, but if it's hot more than a few feet along it looks like your valve is passing.
 
Not sure what you mean without knowing the layout, but the pipe going to the rads shouldn't be hot if the controls are calling for HW only.
I would feel the pipe (the one to the rads obviously) at the 3-port valve and work further along towards the rads. It might be hot close to the valve, but if it's hot more than a few feet along it looks like your valve is passing.
The pipes are hot literally all the way from the 3 port to the TRV’s, there’s very slight warmth at the top of the rads but it’s cold at the return end of the rad & in the return pipes. I’m really starting to believe the valve is passing
 
It may seem a stupid question, but: how do you know which is the flow pipe?

If it's every other rad, what happens to the remaining rads?
The end of the rads with the TRV’s are the flow into the rad so traced that pipe into the loft & went from there. Also it’s not every other rad, it’s all the rads
 
The pipes are hot literally all the way from the 3 port to the TRV’s, there’s very slight warmth at the top of the rads but it’s cold at the return end of the rad & in the return pipes. I’m really starting to believe the valve is passing
It does look like it. I think the next step is to dismantle the valve. It might be something obvious like the ball fallen off the shaft.
 
Well thankyou all for your advice/help so far it is very much appreciated. It will be a little while before I’m able to strip the valve out but once I have I will definitely post & let you know the outcome ... watch this space! :)
 
Just replace the 3port valve,you can get the paddle for them valves which is cheaper but is more involved to strip down.
 
Just replace the 3port valve,you can get the paddle for them valves which is cheaper but is more involved to strip down.
He can take the top off to inspect it without undoing the pipework connections. If it can be repaired, good, if not he hasn't lost anything.
But before that it would be worth taking the cover off the actuator and checking that's doing what it should. Maybe that's where the problem is.
 
Hi all, update on my original problem, rather than remove the 3 port valve to see if it was repairable I spent £20 on a new one, fitted it today & it is all working as it should now, no hot flow pipes when CH is off!!!
So a big thanks to all who offered help & advice, very much appreciated & hope it helps someone else in the future if they get this problem.
 
Hi all, update on my original problem, rather than remove the 3 port valve to see if it was repairable I spent £20 on a new one, fitted it today & it is all working as it should now, no hot flow pipes when CH is off!!!
So a big thanks to all who offered help & advice, very much appreciated & hope it helps someone else in the future if they get this problem.
Great, good to hear it's fixed. If you're that way inclined, why not take it apart and see if you can see what was wrong with it.
 
Ok, so finally got to strip down the valve & found the face that seals the CH side of it had a build up of hard dirt on it, very small but enough to allow water to pass by. The stem & seals are all in good order so I’ve cleaned it all up, reassembled it & will keep it as a spare.
Just for info though, if anyone has the same problem, stripping the valve is very simple, so don’t be afraid to give it a go (hindsight is a wonderful thing!)
 
Ok, so finally got to strip down the valve & found the face that seals the CH side of it had a build up of hard dirt on it, very small but enough to allow water to pass by. The stem & seals are all in good order so I’ve cleaned it all up, reassembled it & will keep it as a spare.
Just for info though, if anyone has the same problem, stripping the valve is very simple, so don’t be afraid to give it a go (hindsight is a wonderful thing!)
Result! Thanks for letting us know.
 
Status
Not open for further replies.

Reply to CH flow pipework still hot even with CH turned off in the Plumbing Jobs | The Job-board area at PlumbersForums.net