Hello,
I hope someone can give some advice with this problem.
I have a Vaillant ecoTec plus 418 with Drayton MA1 mid-position actuator, Drayton HTS3 cylinder stat, Honeywell DT90E room stat and Drayton LP522 controller.
Boiler fires up reliably, but after it cuts out as soon as the DHW temperature is reached despite room stat being set above current room temp.
The reset (flame) button will not restart the system and the only way I can restart it is to switch off power to the boiler for a few seconds and then switch on again.
The Vaillant fault code is S.30 (no demand) despite the timer being on and the room stat being set above current temp.
The boiler runs reliably if I switch off DHW at the controller.
I have lived with this problem for a while and last year I replaced the thermostat and controller with no change to the problem.
I suspect the problem is in the Drayton mid-position actuator, but would appreciate some advice on how to check it out with a multimeter.
Many thanks for any help! Bill
 
Blocking / anti cycling probably does it come back on after 5-10 mins ?
 

Reply to Central Heating cuts out when DHW reaches set temperature in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
2
Views
60
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
280
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
451
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock