Good afternoon I hope you’re well

I am trying to prove to a customer that their boiler is undersized. They have 20 radiators mostly doubles and a 220 L unvented cylinder. 18kw Worcester heat only boiler. Three years old.

I am trying to reverse calculate the heat requirements of the radiators that have been installed and I wondered if anyone had any calculator/app recommendations that might help with this?

Thanks
 
Mr combi heat loss

Cylinder alone will want 10kw
 
Sorry Shaun I lie with fork tongue it’s only a 150L but that’s still gonna be 3-5Kw
 
Sorry Shaun I lie with fork tongue it’s only a 150L but that’s still gonna be 3-5Kw

I would say / allow 8
 
In the middle of winter it’s bound to come on together
 
Well you need to have the option don’t you
I would say no, it is either but not both together. When the standard cylinder can take 18 - 20kW on its own you are never going to be able to do both successfully especially first thing in the morning when the heating load is so high.
If you dedicate all the boiler power to heat the cylinder your 18kW should heat the cylinder in around 30mins then shut off & give all the power to raising the house heating system up to running temperatures.
Once there it is not so much of a problem if it tops up. Time control is key.
 
Good afternoon I hope you’re well

I am trying to prove to a customer that their boiler is undersized. They have 20 radiators mostly doubles and a 220 L unvented cylinder. 18kw Worcester heat only boiler. Three years old.

I am trying to reverse calculate the heat requirements of the radiators that have been installed and I wondered if anyone had any calculator/app recommendations that might help with this?

Thanks
I use this to sort work that out. If we mean the same thing?
 
100% a proper full calc to demonstrate your professional skills.
100% no reason whatsoever NOT to have an uvc come on before heating and to top up when not on. Only a fool wouldn't. ;)
 
Back to Rileys original question. Would you not be better just doing a quick full house heat loss calc?
http://www.domestic-gas.co.uk/documents/CE54.pdf
This was designed to do just what you want. i.e. it provides a total heating load for sizing boilers without the need to do room by room full calculations as you would for heat emitters.

PS. you can take a view on whether you allow 2 or 3kw for DHW, personal I don't.
 
Last edited:
I would normally calculate the heat loss from the house and also use the chart I linked to, to work out what they have now and what they need. That way you show them the full picture.
 
8kW for any cylinder up to 200l Sounds excessive IMO.

My own boiler is only 8kW and will heat the cylinder from cold for around 20 minutes and then starts cycling. In practice, we tend to reheat cylinders before they are stone cold, so I can't see a cylinder accepting 8kW very often.
 
8kW for any cylinder up to 200l Sounds excessive IMO.

My own boiler is only 8kW and will heat the cylinder from cold for around 20 minutes and then starts cycling. In practice, we tend to reheat cylinders before they are stone cold, so I can't see a cylinder accepting 8kW very often.
Just what I was always told and what I now work to mate.
 
Just what I was always told and what I now work to mate.
I've been told all sorts of things, including that if you have a 22mm pipe from the hot outlet of a combi, then you'll have reduced flow to the bathroom because 'the water slows down when it hits the 22mm pipe'.

Hence why I need to understand everything and why I question things.

In a 2 bedroom house with 5.5kW heat losses at design temperature, you'd specify a system boiler capable of providing 13.5kW at whatever flow and return temperatures you have decided on? Is that right?
 
8kW for any cylinder up to 200l Sounds excessive IMO.

My own boiler is only 8kW and will heat the cylinder from cold for around 20 minutes and then starts cycling. In practice, we tend to reheat cylinders before they are stone cold, so I can't see a cylinder accepting 8kW very often.

Unvented cylinder?
 
I've been told all sorts of things, including that if you have a 22mm pipe from the hot outlet of a combi, then you'll have reduced flow to the bathroom because 'the water slows down when it hits the 22mm pipe'.

Hence why I need to understand everything and why I question things.

In a 2 bedroom house with 5.5kW heat losses at design temperature, you'd specify a system boiler capable of providing 13.5kW at whatever flow and return temperatures you have decided on? Is that right?
If you did that you would have 8kw more capacity for the HW generation but why? especially if you think about what is going to happen to the boiler during the summer (& for that matter the spring & autumn) when there is no (or reduced heat load) the boiler is then going to be oversized. I know in this case the cylinder coil could probably take the 13.5 but buying a larger boiler than the max heat load makes no sense.
I also know they can modulate but they are designed to try to match there stated outputs with the system, if they can't they will cycle which is wasteful.
We need a matched boiler to the system demands where it can adjust it's output to stay in condensing mode for as long as possible.

CE54 recommends 2kW (or 3 if very large HW demand)
Domestic Heating Design Guide suggests 2kW for 2bed, 1bath (2.5kW right up to 4bed, 1bath 1shower) only then 3.

So.. where does the 8 or 5 or 4kW come from (not having a go, just asking the question)?
I have even had people suggest that the cylinder coil rating should be added to the heating load so it can do both at the same time. Heat load at -3C might be 15kW + 18.3kW (125L Megaflo) would = 35kW boiler selection, then they wonder why it don't work!!
 
Last edited:
Unvented cylinder?
No, vented.

I quote my own system because it's the only one I've had the leisure to observe in more detail than is probably healthy. My boiler can't modulate. Previous house I put a new cylinder in to run off the existing 13kW output zombie boiler. The cylinder manufacturer told me I didn't need fast recovery on a boiler that weak... and it also cycled like a mad thing once the cylinder had lost its initial chill.

I must say I'm thinking more like Chris Watkins in that I'd rather have the boiler run flat out without excessive cycling than have an oversized boiler.
 
No, vented.

I quote my own system because it's the only one I've had the leisure to observe in more detail than is probably healthy. My boiler can't modulate. Previous house I put a new cylinder in to run off the existing 13kW output zombie boiler. The cylinder manufacturer told me I didn't need fast recovery on a boiler that weak... and it also cycled like a mad thing once the cylinder had lost its initial chill.

I must say I'm thinking more like Chris Watkins in that I'd rather have the boiler run flat out without excessive cycling than have an oversized boiler.

Auto correct of the week award goes to Ric. Zombie boiler!

Got me frightened already.
 
That’s why

Unvented required more heat / they have a bigger coil cap

If you look at gledhill 300l you will see the coil is rated at 25kw max for a re heat time for 45mins I think from cold
 
No, I meant 'zombie'. The walking dead. Decades old, inefficient by modern standards, and running off grandfathers' rights, but still in service. Saw the word in "Installer" magazine and thought it was a common term, but I think it is ONLY "Installer" that uses the term.
 
That’s why

Unvented required more heat / they have a bigger coil cap

If you look at gledhill 300l you will see the coil is rated at 25kw max for a re heat time for 45mins I think from cold
Thanks Shaun. Someone said 'any cylinder' so I assumed this included vented.

I wish I'd fitted a fast recovery in my last house: every time the boiler took an hour to reheat the water I sighed and wished I'd stuck to my guns and bought a fast recovery instead of listening to the idiot who told me my boiler wouldn't cycle. Another thing I've been told grr :) .
 
That’s why
Unvented required more heat / they have a bigger coil cap
If you look at gledhill 300l you will see the coil is rated at 25kw max for a re heat time for 45mins I think from cold
Vented or unvented an indirect hot water cylinder installed into a dwelling (heated by gas in this case) must be Part L compliment, this covers the re-heat times which must be 25 mins given the required boiler power is available.
Re-heat means 70% of its volume through 35 - 40 degC
 
Vented or unvented an indirect hot water cylinder installed into a dwelling (heated by gas in this case) must be Part L compliant, this covers the re-heat times which must be 25 mins given the required boiler power is available.
Re-heat means 70% of its volume through 35 - 40 degC
The cylinders I'm referring to are part L compliant, according to the manufacturers.
Thanks for your post - it explains a lot if re-heat times are quoted at 70% of the volume @35-40K in 25 minutes. Since we put the thermostat a third of the way up the cylinder, it's probably just below that 70%, after which the coil is half covered in heated water and heat transfer drops considerably.

What would be good would be a standard that requires a cylinder filled with 20°C water to satisfy a stat set at 60°C and located a third of the way up the cylinder, in 25 minutes, with a flow temperature to the cylinder coil of 80°C and sufficient flow to ensure the return is no lower than 70°C. You'd need to define the standard to allow for 75/55° operation too.

At least we know it would then work well, rather than just hit an arbitrary target (how do you measure the temperature of 70% of the water anyway?). But as someone who worked at the BRE when they were writing the Code for Sustainable Homes, commented 'we knew when we were writing it that it was ultimately a load of rubbish'.
 

Reply to Calculator recommendations???? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
0
Views
53
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
212
Hi guys. I'm trying to identify a toilet model before ordering a seat for a customer. I went to what used to be a Roca stockist (they no longer are) and one of the guys there reckoned it might be "The Gap". I went to the new stockist and the guy there disagreed it was "The Gap" and that he'd...
Replies
2
Views
124
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
1
Views
74
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...