Hi... Wavin 22mm Hep20 coiled pipe..... flow 12.5 ltr/minute...(at nominal mains water pressure at inlet) What I need to know is the expected water pressure drop over 50 metres. Many thanks in anticipation ...Nick
 
BTW I've looked on their websiteam and I can't find it in the technical specifications
 
if you reference the CIBSE design book, it reckons 22mm @ 12.5l/m (0.2125kg/s) and has a loss of .026 m(hd)/m
 
Last edited:
Thank you very much Jay.... I make that a 1.3 metre head loss over 50 metres of pipe or about a 0.13 bar pressure drop?
 
youre ahead of me there mate, I didnt calculate the total because I wasnt sure what the multiplier was for a bend on the loops.
 
Thanks Jay..... I don't know if my sums are correct either? .. perhaps someone could give thumbs up or down..... BTW no fittings just the total pressure drop over the coil of pipe is what I'm after...
 
Thanks Jay..... I don't know if my sums are correct either? .. perhaps someone could give thumbs up or down..... BTW no fittings just the total pressure drop over the coil of pipe is what I'm after...


yea mate, assuming I got my maths right then yours is fine :)
 
Status
Not open for further replies.

Reply to Calculation help needed in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I will try to explain best I can, please bare in mind I am currently in a learning stage so just trying to understand the process behind things. A building with three floors and 69 rooms. How do you work out the pressure needed on the hot water system? I’m sure there is a calculation to...
Replies
6
Views
737
Hi all Having some renovations done on ground floor and looking to get rid of / replace some of the older looking boilers on that floor (mainly Double panel, double convector, some double panel single convector. As well as replacing these I wanted to add a couple radiators too, but have become...
Replies
16
Views
2K
Hi everyone, Just wanted some confirmation regarding a PRV fitted to the mains supply in my building. All 6 flats in the building are now connected to the mains water feed supply and the water tanks in the attic have been disconnected (each flat has a combi gas boiler). I can see there are 2...
Replies
11
Views
888
I'm in the process of refurbishing my bathroom. I'll be replacing the existing bath with a walk in shower. Will be installing a thermostatic mixer valve fed by mains on the cold side and a combi boiler (Logic Combi c30) for thr hot. Ideally what I'd like to do is have the mixer valve at the...
Replies
3
Views
720
    • Like
Hoping someone can please help. I have an intermittent fault with my electric hot water. I have an older style electric hot water service that heats on controlled load over night. The large tank is in roof space of 60s built villa unit. Every few mornings, no hot water will come out of...
Replies
6
Views
415
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock