Hi All,

Hoping to get some sound advice regarding combi boiler sizing for a large 3 Bed House.

We are refurbishing the house and plan to strip out the old boiler and pipework from the loft to relocate to the kitchen / diner whilst also renewing all copper pipework and installing new radiators.

We are also keen to future proof for a potential loft extension to come in the next 5-10 years which could potentially add 2 more bedrooms and a small en-suite shower room.

I've used 3 different BTU calculators online which based on my room sizes recommend the following BTU requirements per room

Lounge & Dining Room (we've knocked through): 14691
Hallway Downstairs: TBC - hard to calculate due to varying ceiling height and will also heat upstairs hallway - the neighbors have a radiator that gives out approx 6000 BTU
Kitchen: 10958
Our Bedroom: 5614
Bedroom2: 4105
Bedroom3: 2878
Bathroom: 2900

This equates to a total of 47.5 KW. Surely this doesn't mean that we would need a 47.5KW combi boiler? It seems excessive but as stated the BTU requirements are taken as an average from 3 different websites.

We do have a 5KW wood burner stove going in the Lounge / diner which could reduce requirements accordingly?

Plumbers that have quoted for the work are recommending between 33-38KW, Valiant Eco Tech or similar.

I've attached the floor plan to give you an idea of the scale of the house,

any advice you can give would be much appreciated,

Thank you
 

Attachments

  • Floor Plan - Copy (2).jpg
    Floor Plan - Copy (2).jpg
    152.8 KB · Views: 12
It’s a no on the combi unless you are happy with just using one hot outlet at a time

But to answer your Heatloss questions if there correct then yes your load is 50k btu eg 15 kw
 
One BTU is the amount of heat required to raise the temperature of one pound of water by one degree Fahrenheit. When used to measure an appliance, the term “BTU” actually refers to BTUs per hour (BTU/h).

One watt is one joule per second. It takes about 4.2 joules to raise the temperature of 1 gram of water by one degree Celsius.

One BTU/h is about 0.293 watts.

It appears that your total heat calculation is 13.81 kW.

BTU/hkW
14,691​
4.30​
6,000​
1.76​
10,958​
3.21​
5,614​
1.64​
4,105​
1.20​
2,878​
0.84​
2,900​
0.85​
47,146
13.81


Combi boilers are sized for hot water flow.
 
One BTU is the amount of heat required to raise the temperature of one pound of water by one degree Fahrenheit. When used to measure an appliance, the term “BTU” actually refers to BTUs per hour (BTU/h).

One watt is one joule per second. It takes about 4.2 joules to raise the temperature of 1 gram of water by one degree Celsius.

One BTU/h is about 0.293 watts.

It appears that your total heat calculation is 13.81 kW.

BTU/hkW
14,691​
4.30​
6,000​
1.76​
10,958​
3.21​
5,614​
1.64​
4,105​
1.20​
2,878​
0.84​
2,900​
0.85​
47,146
13.81


Combi boilers are sized for hot water flow.

Thanks for this
 
As has been said you have your units mixed up so just divide your BTUs by 3.412 to get KW. Agree with recommendation of a Viessman 200W with WC as modulation is so good especially as you have a stove.

You could always bolt on an unvented cylinder afterwards when you extend as long as you have or leave room for it.
 
Well the first thing i would be doing is Looking at a Viessmann system Boiler and a unvented cyclinder and have the bedrooms on one circuit and the rest of the heating on another circuit as a matter of fact you can have independant hot water from a Visemann But another thing you should look at is a Insulation of all external walls this includes attic space and if possible under wooden floors if you have wooden floors down stairs And of course if you can change class in windows to trebble glazing . And look for any Grants you can get Hope this is of some Help
 

Reply to Boiler Sizing - Large 3 Bed House in the USA area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
251
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
194
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
446
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and pebbles!) We saw that the pipe that takes water down the gutter was visibly full to the top. He said he will return with a coil to push through...
Replies
1
Views
47
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock