S

Swale

Hi all
i would really like some advice please
2 zone heating 1 upstairs 1 downstairs on an ideal combi boiler
2 Honeywell cm707 programmable stats one for each valve
wired to Honeywell junction box(wiring centre) as follows
perm live from fused spur to term 1
perm live from term 1 to boiler
perm live to both stats in term 1
perm live (grey) to both valves in term 1
All neutrals in term 2
all earths in term 3
the stats have the perm live going in term A with the
return term B out of stat (black) going to wiring centre in with brown upto valves
orange from valve back to wiring centre with a grey going to boiler s/l
each black from stat go into a separate terminal 4 and 6 with a brown from the valve

when the stat is pumped up for heat the valves open but boiler does not fire is the wiring correct
the valves are Drayton any help much appreciated thanks
 
Mr Swale of Swale Heating, currently taking a bashing on another forum?
 
Mr Swale of Swale Heating, currently taking a bashing on another forum?

Hi Iam not mr swale Iam a new build installed trying to get my head round this 2 zone heating that contractors want in, never done it before, swale is the river next to me
 
Thanks for reply, 240v at both terminals 4-6
240v at terminal 10 orange x 2 and s/l grey upto boiler
240v at boiler perm live and switched live when stats are on
 
Hi all
i would really like some advice please
2 zone heating 1 upstairs 1 downstairs on an ideal combi boiler
2 Honeywell cm707 programmable stats one for each valve
wired to Honeywell junction box(wiring centre) as follows
perm live from fused spur to term 1
perm live from term 1 to boiler
perm live to both stats in term 1
perm live (grey) to both valves in term 1
All neutrals in term 2
all earths in term 3
the stats have the perm live going in term A with the
return term B out of stat (black) going to wiring centre in with brown upto valves
orange from valve back to wiring centre with a grey going to boiler s/l
each black from stat go into a separate terminal 4 and 6 with a brown from the valve

when the stat is pumped up for heat the valves open but boiler does not fire is the wiring correct
the valves are Drayton any help much appreciated thanks

Thanks for reply, 240v at both terminals 4-6
240v at terminal 10 orange x 2 and s/l grey upto boiler
240v at boiler perm live and switched live when stats are on

Sorry, I'm finding it hard to visualise what you're describing. A photo or diagram would be really helpful.

Alternatively, take a look at the Honeywell website for a standard S-plan system which is what you're trying to configure. Follow the diagram and you won't go wrong. Terminal numbers and wire colours aren't that important, just follow the switching sequence..
 
Last edited by a moderator:
Use multimeter not volt stick. If perm live and s/l going to boiler are both 240v. then, other than checking fuse on PCB, you will need GS engineer.
 
Status
Not open for further replies.

Reply to Boiler not firing in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the outputs goes to a 2 port diverter prior to the Megaflo (I believe this is some safety feature). I have run into an intermittent problem where some...
Replies
5
Views
225
I've recently replaced an immersion heater for a direct cylinder, for 2.75-3kW. The new one seemed to be working a week before I got a callback. I checked the resistance of the immersion heater, and it read 19ohms, and the voltage on the live and neutral read 230V, but there was no humming or...
Replies
5
Views
166
I just installed second zone onto my ideal independent c35 original I had one hive thermostat now I added two two port valves ( with Bypass) and two hive thermostat V3 it wired into a wiring centre looking at the wiring on the boiler shall I put back the room stat/ timer loop back in as...
Replies
4
Views
418
Hi I have a Glow-worm back boiler which is giving me grief (I would have upgraded it by now but its a listed building and there's issues with venting through the external wall and I'm reluctant to go with an electric boiler instead (because of the consumption cost)). It's a sealed system. The...
Replies
6
Views
419
Customer complains of Intermittent heating on Y plan with Stat satisfied. New boiler fitted last year (no permanent live required or fitted previously) on an existing Y plan system. Existing timer was a Randall 103 (no hot water off position as its a timer not a programmer). The customer wanted...
Replies
25
Views
2K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock