This may be a bit of a daft question but seem to be having issues with 4 Atag xl110 when running on low fire and believe there could be an issue with the flue but when check-in Mis I noticed it says flue gas outlets under pressured and flue gas outlets over pressured. What is the difference in these configurations? Cheers
 
are you commercial ?
 
whats the issue on low fire?
 
whats the issue on low fire?
The O2 percentage is meant to be between 5-7% there is 4 boilers back to back going onto a common flue header but when running on low fire the percentage was 12% when trying to adjust the offset on gas valve when I was getting to roughly 10% the CO ppm was flying through the roof. These are newly installed boilers but have used existing class 1 flue
 
What was the high fire stats
 
Have you tried firing one boiler at a time on low ?
 
How long are the flue and is there a secondary flue fan fitted ?
 
Is could I would find out the max flue run on the Atags should be in the manual and then go from there

If you can’t find it phone tech up there a good bunch but commercial only so need to know what your talking about
 

Reply to Atag XL110 Flueing issue in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
119
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
200
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
1
Views
74
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
0
Views
53
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
354
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock