adjust the clock so the hot water comes on at a time the heating is not required.


Aw you mean have hot bath in a cold bathroom or a cold bath in a warm bathroom, electrical shower will fix that

:75:
 
Set the water to come on an hour before the heating. If that doesn't solve the problem then there are further problems with the install.
 
What actual problem has the customer got? I agree with Ray, it should be fine. Seen this set up many a time
 
What temperature is the boiler set too?
It could be as simple as a faulty boiler stat.
Check the flow temp and see if it correlates with the boiler thermostat setting.
You don't need much of a temperature drop for a borderline boiler to really under perform.

Oz Plumber
 
I must have a weird way of looking at things. I suppose during the winter the heatings been next to useless most of the time its run.

if they haven't fitted a lockshield valve to the coil then it will offer next to no resistance, easily more than half the heat will run around that and give unsatisfactory performance to both. By the time the cylinder reaches temp then the heating will be going off.
 
Aw you mean have hot bath in a cold bathroom or a cold bath in a warm bathroom, electrical shower will fix that

:75:


LOL, if the cylinder is modern, it should keep warm for many, many hours. long enough for the heating to warm up :)
 
Non issue in my eyes, as said just vary the timings slightly. We have the same at home boiler is currently range rated to 19kW with 15 rads (in 2 zones) and 300l unvented and we have never been cold or had no hot water.
 
they used to say allow 2kw for the hw on vented cylinders do unvented cylinders realy need that much kw .
 
No, the modern unvented cylinders just have much more efficient heat exchangers so they can actually disperse more power into the water quicker. You could charge them with 2kw of heat from the boiler and for similar sized cylinders they would heat up in exactly the same time as an older vented one. Well a bit quicker actually due to better insulation but let's not split hairs!
 
depends on the demand if its used by a few teenagers its gonna rob the heating regardless how long it heats or keeps the heat..i do like to learn and if 20kw can can heat a big house and big cylinder I'll be fitting smaller boilers in future.
 
Our cheap skate new home builders installed a Potterton Promax 15 SL 15KW system boiler onto our system. It has an unvented hot water cylinder with an 18.3KW heat exchanger. There are just under 15KW of radiators in our house.

You can get away with sizing a boiler to suit the heating requirement only in a house like Ray says. The rads will not be heated for the half hour or so a modern unvented cylinder takes to recharge, in practise it will hardly be noticed.

I caveat this with there are just 2 of us in the house and we use showers only most of the time.

Our house is a 5 bedroom detached house. I would say the boiler is undersized and when we change it I will fit a 24KW system boiler but it does the job.
 
Last edited:
There is no requirement to allow both the heating and hot water to be run at the same time under full load. Remember, the heat loss calculated will be at -1,-3 or whatever ie 1-2 weeks a year.

The rating of the coil is irrelevant really as long as heat up time complies with part L. In reality who's checking? How often will you need to heat the entire cylinder from cold?

if you are adding the coil size to the heat loss then your massively over sizing boilers.

Sounds like this boiler was sized perfectly which makes a change.

Also, who's to say the radiators aren't over sized? Sizing a boiler should be done by heat loss of the building not radiator sizes.

if they are running out of water, the cylinder is undersized not the boiler.
 
Suppose its like everything, make do and change settings or get it changed..also being there and knowing if their bath people or shower, and when through the day are people using hw....
 
im assuming its balanced. i still believe it to be undersized but hay ho.
 
Last edited by a moderator:
Status
Not open for further replies.

Reply to under sized boiler ??? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock