only place i can put the boiler is in the kitchen, i cant get the flue anymore than about 250mm ish from a window the flue would exit 250mm above window and 200mm from the edge of window
 
If you fit a worcester then you can overcome this by using a plume management kit. The manufacturers instructions say this is OK. (Other makes may be similar but check MI's first). Will try and find a link.
 
installation-and-servicing-manual-for-greenstar-i-junior--manufactured-from-august-09.jpg
Hope this works. Its from the Greenstar Jnr i range of combi's from Worcester.
 
cheers mark i was hopeing to fit a vaillant dont know if they do plume managment kit
 
Even if Vaillant do a plume management kit it doesnt mean it will be OK to use it in your situation unless the Manufacturers Instructions state you can. Why not go to vaillants website and download the manual and see what it says.
 
id like to know that one to steve me and my boss were disscussing it today and think these people just make these things up when they like

where do you see a minimum distance from air intake to opening? if it is a concentric flue then you measure to the flue and ignore the air intake, on the original post, if i read it correctly and the flue exits above the window then there is no problem with the 200mm to the side
 
(200 x 200) + (250 x 250) = 102,500
Square root 102,500 = 320.156 (Pythagoras' theorum)
I also agree with kirkgas - BS 5440-1 indicates 300mm directly above the opening
 
where do you see a minimum distance from air intake to opening? if it is a concentric flue then you measure to the flue and ignore the air intake, on the original post, if i read it correctly and the flue exits above the window then there is no problem with the 200mm to the side
thats what i thought but when i checked on vailants site there is a minimum of 300 mm above an opening not sure when this came in im sure it wasnt there before
probably there to sell plume kits
 
Status
Not open for further replies.

Reply to flue position in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
365
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
229
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
300
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock