jackocleebrown

Hello,

I have a vented heating system in my small end of terrace three bedroom house. Generally the system works well but I find that I get a lot of air in the system. The air tends to collects in one of the radiators - I find that I need to bleed it every two or three days in the winter (when the heating is on everyday). This seems excessive! Is the air drawn into the system when the pump starts up?! Does anyone have any suggestions how to remedy the problem?

Thanks, Jack
 
carefully set fire to the air next time you bleed,if it burns its hydrogen a by product of corrosion in which case you need a de scale
 
Wow! sounds drastic, I'll give it a go in a couple of days (just bled it about 20mins ago).
Thanks for the advice, Jack.
 
I've tried to set fire to some of the air bled from the system and it does not burn. I also drained off about a pint of water from one of the radiators and the colour of the water is almost totally clear with just a very slight yellow hint. Does this mean that there is no corrosion problem? Do you have any other ideas how the air might be getting into the system?

Thanks, Jack.
 
probably from the pump!

poor location of the heating pump is a common culprit, basically what happens is the pump draws air in from the open vent.
if poss post a couple of pics then we can tell if the pump is incorrectly positioned.

KJ
 
Thanks for your replies, photo of the pump and vent plumbing is attached.

Cheers, Jack.
 

Attachments

  • IMG_0763.jpg
    IMG_0763.jpg
    78.1 KB · Views: 30
might be my old eyes but i cant see a vent in that pic and what looks like just a cold feed coming in before the pump
 
just realised you had marked pipework yes it looks like vent cold feed is in wrong place
 
Hi Steve,

Sorry that the photo is small, I labelled what I could.
Thanks for your advice, where does the vent pipe need to be located?
Is the feed pipe in the right place?

Thanks, Jack.
 
you could try having the the vent and cold feed moved, but if i was doing that i would make it a combined cold feed and exspansion
 
hmm it looks like it is a combined vent and feed via a reducing tee!

can you tell us whether the problem has always existed or has it just recently started up? it could be drawing air in from elsewhere.

KJ
 
Status
Not open for further replies.

Reply to Heating system needs regular bleeding in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Oil boiler (now~15 years old) unvented system with 17 radiators. We moved in 5 years ago and I had to keep bleeding the same radiator. The bleed gas could be burned with a blue flame and the water was acidic (pH 5.5). Since then system has been chemically flushed (it was not too bad) and the...
Replies
1
Views
204
Hi I have a worchester heat slave 18/25 and continually needs bleeding of the Kero, runs all day when bled. when it cuts out on the stat it wont start again without bleeding
Replies
1
Views
127
When I turn on our CH there's a lot of noise from one specific part of the system - the pipes on the landing, and one radiator. It sounds like air, and the landing radiator needs bleeding regularly (about once a month), even though it isn't the highest point in the system. The two upright rads...
Replies
35
Views
1K
Hi, I am replacing our 11 year old boiler (due to H.Ex. leak) with a new one. This is in a "sealed" system with red expansion vessel in airig cupboard & a megaflo (no tank in loft). However the exisiting boiler is Vaillant ecoTEC 4xx boiler - which is satated by vaillant as an "open vent" boiler...
Replies
3
Views
436
Hi I seek some advice on replacing an existing regular boiler. I currently have an old Potterton 10-16 Netaheat electronic, which is around 35 years old and still working OK. It is fitted to a std 'Y' plan system with boiler in utility room and separate hot water tank, pump, valve etc in...
Replies
7
Views
640
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock