Got a Worcester combi boiler that gets serviced every year through BG, but we are finding that the hot water is never that hot.

I think the water is passing through the boiler too fast and doesn't get a chance to heat properly.

Very noticeable on the bath, where we have to close the tap down quite a bit until the flow rate reduces coming out the tap.

Is there a way to reduce the flow rate as it goes through the boiler?
 
Has it ever been hot or is the problem your describing always been present since install?

If it has then what you need to understand is depending on model, your boiler may only be capable of delivering as little as 10ltr/min of what you would class as hot water, or as much as 17ltr/min. If you have a lower kw rated combi you could quite easily be expecting to much from it.

If however, when installed, your hot water was great but is now poor. This could indicate a problem within your boiler. It's fairly easy to diagnose so long as your engineer is aware of the problem.
 
What’s the model of the boiler ?
 
Bit of background. The house is 11 years old and was built with a Gloworm system boiler and hot water tank. 4 bedroom, 2 showers and a bath.
Because of really poor hot water pressure from the tank, we decided to have it changed to a combi, and free up the tank cupboard for storage.
Local Gas Safe plumber did the work, and we have had BG service it every year since.
I wouldn't say it was perfect from day 1, but certainly better than it was.

The boiler is a Worcester 37i (?) I think, without going out to the garage to check, and was told at installation it was the biggest they do.
I don't think there is a pressure reducing valve on the cold main.
There is an anti scald valve under the bath, but its set to be as hot as it can be.
 
Will that cure it though?
I’ve never come across these but after a little googling I get the impression the combisave reduces the flow until the dhw temp reaches 45C then opens fully. This way it saves water on the initial draw off, but after that you’re back to where you were to start with surely? Full flow which isnt getting hot enough, then I’m assuming the combisave willjust modulate the flow up and down with the temp? Or did I miss something here??
Thats no fix, you need to be looking at what’s coming in to the boiler instead of some gimmick. Get a proper plumber in to test your water flow rate, pressure and the blend valve under the bath, then adjust accordingly.
 
Will that cure it though?
I’ve never come across these but after a little googling I get the impression the combisave reduces the flow until the dhw temp reaches 45C then opens fully. This way it saves water on the initial draw off, but after that you’re back to where you were to start with surely? Full flow which isnt getting hot enough, then I’m assuming the combisave willjust modulate the flow up and down with the temp? Or did I miss something here??
Thats no fix, you need to be looking at what’s coming in to the boiler instead of some gimmick. Get a proper plumber in to test your water flow rate, pressure and the blend valve under the bath, then adjust accordingly.
Do both and you will never look back. chking
 
I think installing a combi save would be really worth it. This would save you water and save fiddling round with flow rates. A 37i is well powerfull enough.
centralheatking

Honestly how much water do they save though? Modern combos fire up and ramp up to max within a matter of seconds the plate starts getting hot within 10 seconds so with a 30kw combi probably save a litre if you open the tap fully straight away. Most of the water people waste is what's in the pipe.
 
Did a little research, and I can get the combisave gizmo for 50 quid. Worth a shot.
I understand how it works, and for filling a bath, it seems sensible... but what happens with the showers? Will they fluctuate in pressure with the combisave in use?
 
Did a little research, and I can get the combisave gizmo for 50 quid. Worth a shot.
I understand how it works, and for filling a bath, it seems sensible... but what happens with the showers? Will they fluctuate in pressure with the combisave in use?
Have a look at shower power booster from Alan Wright ..he was on dragons den, nice man very clever unit. centralheatking
 
Has BG looked at it can't see it just being too fast a flow there must be another problem if water not hot enough eg:- heat DHW heat ex clogged up or sensors out of wack
 
Has BG looked at it can't see it just being too fast a flow there must be another problem if water not hot enough eg:- heat DHW heat ex clogged up or sensors out of wack

If bg thought there was even the slightest bit of muck in there they would be charging them £1000+ for a power flush.
 
Don't disagree but you've got to admit they are very quick to blame sludge and will soon push their very expensive flush
Agree on that one, I had one customer who had been told by BG her system was full of sludge and needed a powerflush. Stupid quote for the work when all that was needed was a new ball valve in the loft as it had seized and system had dried up.
 
Agree on that one, I had one customer who had been told by BG her system was full of sludge and needed a powerflush. Stupid quote for the work when all that was needed was a new ball valve in the loft as it had seized and system had dried up.

That's bl00dy appalling :mad:
 
That's bl00dy appalling :mad:
bg staff are largely sales driven NOT problem solvers. there is little profit in their servicing business its the add ons that they can sell that keep,that business alive. and of course the radicals but you need experienced staff allocated enough time to do radical jobs properly
Rob Foster
aka centralheatking
 
Even though to get hot water you need to close the tap to a trickle but believe you can get adequate flow - albeit if cold, the alternatives are simply that either the **amended as mentions boiler repairs**. I realise that either of these should affect the total flow and not just hot flow, but I have seen exactly this symptom on a W-B 34 combi in a very hard water area (Bath). If either prove to be the problem, you could - after fixing - also install a CombiMate to help reduce its tendency to scale the DHW side (the CH side should not scale).
 
Last edited by a moderator:
It’s Scottish water, so doesn’t have the scale problems as other parts of the uk.

Beginning to sound like it could be a number of things.
Maybe I’ll just contact bg to fix as I have their repair plan
 

Reply to Hot water, but only just in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Looking for any ideas to help. I've a Heatrae Sadia Hot Water tank, heated through Oil fired boiler (working fine). A week ago I reset the air gap as I was having dripping from the pressure relief valve. Since then I've lost a lot of pressure from the hot water feed to my shower. The rest of...
Replies
8
Views
263
Afternoon. I have an issue with no water flow from any of the hot taps in the house, I can't seem to find a solution to the issue. System is a megaflo unvented indirect cylinder (125i) boiler is a Worcester greenstar. I have good pressure on the cold feed and all the usual stuff works, taps...
Replies
11
Views
287
The Water Board have just replaced the main water supply to our property. We have a ground floor combi boiler. The central heating system for the whole house is working as normal. Hot water is working as normal on the ground floor. However, there is no hot water to the first floor bathroom. This...
Replies
9
Views
445
I live in an apartment block where generally hot water is supplied from the communal hot water cylinder and cold water to bathrooms is supplied from cold water tanks in the loft. It is a vented system. However, in a basement flat and a ground floor flat cold water supply to bathrooms is...
Replies
4
Views
571
    • Like
Hoping someone can please help. I have an intermittent fault with my electric hot water. I have an older style electric hot water service that heats on controlled load over night. The large tank is in roof space of 60s built villa unit. Every few mornings, no hot water will come out of...
Replies
6
Views
409
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock