HI,

I had a new gas meter fitted a year ago and the installer said he wasn't happy with the flue. I have lost the report but would like to correct any faults.
The boiler is an old Thorn floor mounted atmospheric boiler which is located in the corner of a single story flat roofed garage which is attached to 2 floor house. Above the boiler you can see the bottom of the brick chimney which runs up the side of the house to roof level.
A flexible stainless flue liner runs from the top to the bottom of the chimney and connects directly to the boiler. So from the boiler to the ceiling in the garage where it enters the chimney there is an exposed unprotected section of flue liner.
Is this allowable in the gas regs? Should there be a solid section of flue from boiler to the ceiling and if so should it be double skinned.
Thanks very much for any advice
Steve
 
It’s a tricky one. Some pics might help however I think you are going to need to enlist a gas engineer with a little experience of old floor standing open flued appliances. Problem with meter fitters is that most of them are just that. They know how to purge and relight appliances and if they don’t they tend to whack a warning sticker on them until you get someone out with the full ticket
 
HI,

I had a new gas meter fitted a year ago and the installer said he wasn't happy with the flue. I have lost the report but would like to correct any faults.
The boiler is an old Thorn floor mounted atmospheric boiler which is located in the corner of a single story flat roofed garage which is attached to 2 floor house. Above the boiler you can see the bottom of the brick chimney which runs up the side of the house to roof level.
A flexible stainless flue liner runs from the top to the bottom of the chimney and connects directly to the boiler. So from the boiler to the ceiling in the garage where it enters the chimney there is an exposed unprotected section of flue liner.
Is this allowable in the gas regs? Should there be a solid section of flue from boiler to the ceiling and if so should it be double skinned.
Thanks very much for any advice
Steve
Bluntly if the Gsr whom replaced ur meter did not cut you off but id you must not have been too worried at the time. However ...you and your family live in thus buiding and you must feel unsafe otherwise you would not have posted. We can give you advice based in the info you state. I think you should call out a GSR professional to advise you about your flue 1 st hand

and expect to pay ... afterall you do not want to wake up dead

Rob Foster aka centralheatking
 
I’d also prepare to not be able to flue this appliance anymore so if it’s wrong it may be new boiler time
 
The clue is in the name. Flue LINER. No part should be visible. However, without looking it up, I am 99.9% sure that, provided it passes all the safety tests, spillage and smoke, it is classed only as NCS.
To rectify, one would replace the liner with something like Selkirk IL, which is a twin wall flue.

If I was approached to rectify, I would be checking the requirements- it has been years since I fitted Selkirk.

TBH, the cost of rectification may be better spent on a new boiler
 
Non compliant, but agreed if it’s the wrong material used for flue then it could be AR
 
Thanks for the replies. I've tried to attach a picture showing the flue and boiler but it would seem like the section of flexible flue liner from the boiler to ceiling should be replaced with twin wall?

20190209_100003.jpg


20190209_095956.jpg
 
Should definitely be in solid flue.
Also the hole in the liner where they take analyser readings etc shouldn’t be there potential Products of combustion (POC) entering the room
 
Yep not right
 
It is not AR due to the bad material - IF it is pulling etc. Just because it looks crap does not nean it is AR. Being a very hot surface does not make it AR.

However, the hole, presumably for an FGA, probably does elevate it to AR.

WTF would someone do that?
 
It is not AR due to the bad material - IF it is pulling etc. Just because it looks crap does not nean it is AR. Being a very hot surface does not make it AR.

However, the hole, presumably for an FGA, probably does elevate it to AR.

WTF would someone do that?
Agreed once again showing that it’s been in for xx number of years and No ones said a word or it’s never been serviced
 
I had the boiler fitted 40+ years ago and it has only ever needed 2 thermocouples hence my reluctance to change it.
I remember a guy sticking a screwdriver in the side of the flue to make a hole for his analyser. His argument being that the draw from the chimney wouldn't let any gas escape.
So if I fill the hole in is it OK?
I was thinking of getting a 1 metre length section of twin wall to fit to the top of the boiler, then connect a 45 degree bend and then a connector to connect to the flexi flue liner ie so most of the flue in the garage is twin wall. Hopefully this will keep any further meter installers happy?
On another subject the 88 year old lady next door had a new boiler fitted by the gas board 5 years ago and also pays for an annual service/callout plan. Last year when it was serviced they frightened her by saying that it was getting a bit old, parts maybe hard to find and she could be left without heating. They said the same about the gas fire in the front room. They made her pay best part of £10,000 for another new boiler and a fire. Then in winter during a cold spell the boiler broke so she rang the gas board and they said they were too busy to take any more calls. I had a look and the condensate pipe was frozen.
This is the reason I try and keep my old reliable boiler going for as long as possible.
 
I had the boiler fitted 40+ years ago and it has only ever needed 2 thermocouples hence my reluctance to change it.
I remember a guy sticking a screwdriver in the side of the flue to make a hole for his analyser. His argument being that the draw from the chimney wouldn't let any gas escape.
So if I fill the hole in is it OK?
I was thinking of getting a 1 metre length section of twin wall to fit to the top of the boiler, then connect a 45 degree bend and then a connector to connect to the flexi flue liner ie so most of the flue in the garage is twin wall. Hopefully this will keep any further meter installers happy?
On another subject the 88 year old lady next door had a new boiler fitted by the gas board 5 years ago and also pays for an annual service/callout plan. Last year when it was serviced they frightened her by saying that it was getting a bit old, parts maybe hard to find and she could be left without heating. They said the same about the gas fire in the front room. They made her pay best part of £10,000 for another new boiler and a fire. Then in winter during a cold spell the boiler broke so she rang the gas board and they said they were too busy to take any more calls. I had a look and the condensate pipe was frozen.
This is the reason I try and keep my old reliable boiler going for as long as possible.
Please please stop right there. What you are proposing is illegal and dangerous. Do you not understand what an integral part a correctly installed flue is. It’s not in any way shape or form a DIY venture. The boiler shouldn’t even be on at the moment. Please seek the guidance of a properly trained gas engineer who can sort that mess.
 
Last edited:
I had the boiler fitted 40+ years ago and it has only ever needed 2 thermocouples hence my reluctance to change it.
I remember a guy sticking a screwdriver in the side of the flue to make a hole for his analyser. His argument being that the draw from the chimney wouldn't let any gas escape.
So if I fill the hole in is it OK?
I was thinking of getting a 1 metre length section of twin wall to fit to the top of the boiler, then connect a 45 degree bend and then a connector to connect to the flexi flue liner ie so most of the flue in the garage is twin wall. Hopefully this will keep any further meter installers happy?
On another subject the 88 year old lady next door had a new boiler fitted by the gas board 5 years ago and also pays for an annual service/callout plan. Last year when it was serviced they frightened her by saying that it was getting a bit old, parts maybe hard to find and she could be left without heating. They said the same about the gas fire in the front room. They made her pay best part of £10,000 for another new boiler and a fire. Then in winter during a cold spell the boiler broke so she rang the gas board and they said they were too busy to take any more calls. I had a look and the condensate pipe was frozen.
This is the reason I try and keep my old reliable boiler going for as long as possible.
Ps nobody “made” her pay for it. £10000 is a lot but come on she could’ve shopped around for quotes. Once again you make it sound like all installers are out to fleece you. No responsible engineer is going to tell you to change and upgrade for fun. The reluctance to upgrade to save a few quid could prove horrendously expensive with someone’s life. Don’t be a statistic please.
 
Please please stop right there. What you are proposing is illegal and dangerous. Do you not understand what an integral part a correctly installed flue is. It’s not in any way shape or form a DIY venture. The boiler shouldn’t even be on at the moment. Please seek the guidance of a properly trained gas engineer who can sort that mess.
Ok, I'll make some enquiries next week and I'm sorry if the story about my neighbour caused any offence to you guys. I appreciate all your comments
 
Wrong. NCS DOES exist, you just do not note it on a Warning Label. You can (and I do/would) nite them on my Invoice/Report sheet.

Are you under the impression that all ex NCS situations are AR?

During my recent re-assessments it was told to me that ncs wasn’t a ‘thing’ anymore however during a recent convo with another gsr engineer it appears it is. Just isn’t viable on a form as such so I’m wrong in this instance; apologises!
 
During my recent re-assessments it was told to me that ncs wasn’t a ‘thing’ anymore however during a recent convo with another gsr engineer it appears it is. Just isn’t viable on a form as such so I’m wrong in this instance; apologises!
From my assessment I was told ncs was done away with too, without double checking I'm sure we now have 2 categories of AR, one category was dealt with by just filling out a form to notify the customer which basically replaced ncs and the other where we would have to turn the appliance off, fill out a form and attach a label.
 
From my assessment I was told ncs was done away with too, without double checking I'm sure we now have 2 categories of AR, one category was dealt with by just filling out a form to notify the customer which basically replaced ncs and the other where we would have to turn the appliance off, fill out a form and attach a label.


We've been taught that they have got rid of NCS and things that would have fallen under that category are to be called none compliant. We should inform the customer of it but there are no stickers to leave/forms to fill out.
 
We've been taught that they have got rid of NCS and things that would have fallen under that category are to be called none compliant. We should inform the customer of it but there are no stickers to leave/forms to fill out.
Yeah your right, just checked and, you can still notify in writing if you wish but not as part of a warning notice, so verbally is fine.
 
Hopefully not high jacking the thread too much but seems a bit backwards in my opinion. Gas safe really didn’t relay the information too well?
Either way it’s a learning curve and happy to be corrected. Thanks
 
Ncs still exists just note it down but do nothing about it no labels nothing
 
Hopefully not high jacking the thread too much but seems a bit backwards in my opinion. Gas safe really didn’t relay the information too well?
Either way it’s a learning curve and happy to be corrected. Thanks
Don't think it's an issue with gas safe relaying the info, it's probably people (like me) forgetting.

I haven't had to use the warning system since qualifying so I guess it's easily done.
 

Reply to Flue for old atmospheric boiler in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
237
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
178
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
390
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
218
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
310
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock