Evening all,

Can I ask you good folk, if low loss headers require a zone valve after the pump for each zone? My zones are ufh, towel rails and hot water.

Thanks in advance
 
No just a nrv on the flow if pumps on return etc
 
Saves using a relay upto you
 
A lot depends on the circuits you're controlling. If it's domestic or a small installation, you could get away with a small domestic sized pump/one size of pump for all circuits, (as long as the index is covered). That's possibly why KOP used the zone valves, (I'm guessing). On Commercial it is done in different ways owing to what the different types of circuit might be, so as Shaun said, you normally see different sized pumps and NRV's as a basic.
 
Thanks for your replies, I’m talking about zone valves with a pump for each circuit
If you use three pumps that's your choice.
If you don't use a valve or NRV then all three circuits could warm up when any one of them is on.
i.e. If you install three pumps, one on each circuit and only one pump switches on, you will have nothing to prevent flow through other circuits. Even if it is by Gravity. It might not do of course, it might work well depending on the installation pipe work but I would want a more positive set up. I would probably use MV's and one pump by the sound of the installation.
I might be misunderstanding your question here Bogrodder.

Installations that utilise different pumps for different circuit/duties only really/usually need an NRV to prevent circulation in other circuits when those circuits are piped off a LLH. If you want to use three pumps, off a LLH then you could use NRV's. You would need something though in my opinion. I have not seen the set up so it's difficult to say for certain.
 
Made a start yesterday people

8C2C4C55-F92F-4E54-904B-DB3B76345710.jpeg
 
Drain offs bog ?
 
Is that 15 mm pipe tee'd in after between pump and Boiler for the F&E (fill or feed and expansion)?
If it is, I would have placed it behind the pump.
It won't make a huge difference in all honesty due to the Header but I still think it better to do it that way. Others may disagree with that of course. We all work our own way.
 
Last edited:
Is that 15 mm pipe tee'd in after between pump and Boiler for the F&E (fill or feed and expansion)?
If it is, I would have placed it behind the pump.
It won't make a huge difference in all honesty due to the Header but I still think it better to do it that way. Others may disagree with that of course. We all work our own way.

Yes, it’s actually a 22mm for the expansion vessel and the prv point.
 
Third days progress, been slow today...as I’ve been connecting all the pipework in the false ceiling above. Up and down flipping ladders all day. Can I ask you good people if 1.5” solvent weld waste waste pipe and fitting would be suffice enough for the outlet from the Sanicom2?

340F0387-C82A-4C88-840E-E1B8479D892B.jpeg
 
End of week progress. I’m still waiting if stuff to arrive, was hoping to get filled up today.... but I didn’t fancy filling up on a Friday.... for obvious reasons

60B22F24-3442-4A81-B3D9-12A790BF8ED5.jpeg
 
Bit of a restriction going down from 40mm to 28mm ?

Nice tesla tun tho :)
 

Reply to Low loss headers and zone valves in the Plumbing Zone area at PlumbersForums.net

Similar plumbing topics

Hi. I need a new toilet supply line but don’t know the size type of the fitting at the shut off valve. It is not 3/8 compression. It is a plastic nut about the same size as the one going into the cistern but has a different thread. Attached is a photo. Can you advise. Thanks.
Replies
2
Views
177
Hi all Noticed bad smell in my drain out side put my hand down and it unclogged it for now however I checked my sewer drain and after flushing my toilet a good few times nothing is going to the sewer so don't know is there a blockage or what way it works many thanks and advice would be grateful
Replies
3
Views
462
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
221
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
297
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
221
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock