I want to install an Essex Flange to the cylinder for a shower pump. (Cylinder is surrounded by shelving plus is about 15 years old and has overlapping pipes at top connection so I'd prefer to drill a hole in the cylinder and leave the older connections alone)
The flange I have is the E1R type
31212-5c8bf4e0152b9f33d95ce98bbae3d600.jpg
3/4 inch with no compression fitting. Can I use male couplers on either side of this type of flange to connect 3/4 inch pipe to and from the cylinder? Or would you solder some suitable brass threads onto the outside of the flange to convert it to a compression fitting type flange? Is it advisable not to have a compression fitting inside the cylinder submerged in water permanently? Would really appreciate any advice. Thanks very much in advance!! (Sorry for sending PMs of this to a few guys!! My first time using this!)
 
Remove an immersion ....if you get it wrong curtains. Always leave it full of water with the drain connected to a hose. this way the cylinder is stronger and will not crumple, when just loose drain water out ..simplse
Cenralheatking, bit of heat but don’t burn the plastic stuff
 
You obviously don’t live with hard water!
Leave tank full to crack open immersion, as you say to maintain integrity of wafer thin copper.
Then whip off top connection, bung hose pipe in and suck away! Syphon out tank in minutes - but via draincock at bottom amongst all the sludge it takes hours!
Plus no worry of drain cock weeping afterwards.
To finish off , 9 iron or wedge through immersion hole and oik out the scale with aid of wet vacuum.
 
You obviously don’t live with hard water!
Leave tank full to crack open immersion, as you say to maintain integrity of wafer thin copper.
Then whip off top connection, bung hose pipe in and suck away! Syphon out tank in minutes - but via draincock at bottom amongst all the sludge it takes hours!
Plus no worry of drain cock weeping afterwards.
To finish off , 9 iron or wedge through immersion hole and oik out the scale with aid of wet vacuum.
Used to do this in Bath ..yes ur right but we usually scrapped them if that bad ...however one good trick when the hot water flow gets slow is to turn of water supply , crack open top nut move it over and use a masonry drill to clear the blockage ....the rock migrates to the top nut . Bingo full,bore hot water supply restored
 
Thanks very much for all the replies!! I'll probably leave the immersion alone and use the male iron to compression fittings. Cheers!
 
Essex flanges are probably the most hateful plumbing invention.
I never use them, except to do a swap when they start flooding.
I would use Surrey or Warix flange in top of cylinder, regardless of the work involved
 
Essex flanges are probably the most hateful plumbing invention.
I never use them, except to do a swap when they start flooding.
I would use Surrey or Warix flange in top of cylinder, regardless of the work involved
Good to know. Do you think anyone out there still uses them at all?
 
Good to know. Do you think anyone out there still uses them at all?

Yes, some people still use them. It is one of the methods pump manufacturers state for hot draw off.
The flanges for screwing into top of cylinders are easier to install and no drilling.
Heat eventually destroys the soft rubber washers on Essex flanges
 
Yes, some people still use them. It is one of the methods pump manufacturers state for hot draw off.
The flanges for screwing into top of cylinders are easier to install and no drilling.
Heat eventually destroys the soft rubber washers on Essex flanges
Bes gas electric avenue Brum
Chk
 
Yes, some people still use them. It is one of the methods pump manufacturers state for hot draw off.
The flanges for screwing into top of cylinders are easier to install and no drilling.
Heat eventually destroys the soft rubber washers on Essex flanges
I thought so alright. Thanks again for the feedback. The washers that came with it seem to be pretty thick ones like wine bottle cork stuff. Manufacturer claims it can take up to 120 degrees celsius which would be hotter than a kettle!! Cheers.
 
I thought so alright. Thanks again for the feedback. The washers that came with it seem to be pretty thick ones like wine bottle cork stuff. Manufacturer claims it can take up to 120 degrees celsius which would be hotter than a kettle!! Cheers.

That is news to me. The washers are usually very soft white rubber (to guarantee they mould to the curve shape of the cylinder and the uneven surface often caused when it is drilled.
They certainly used to be only suitable for 60 degrees or so.
Once they go hard they can leak and sooner if the pipe gets a knock
 
That is news to me. The washers are usually very soft white rubber (to guarantee they mould to the curve shape of the cylinder and the uneven surface often caused when it is drilled.
They certainly used to be only suitable for 60 degrees or so.
Once they go hard they can leak and sooner if the pipe gets a knock
Yes I've seen those type online. Creamy white looking washers. Look very dodgy. These hard cork ones are flexible to take the shape of the surface too. Maybe I'll get a bottle of plonk, boil it and see at what temp does a cork start to dissolve!!! Thanks for the quick replies.
 
You say you leave the immersion alone, how are you going to get the Essex flange inside the cylinder?
I’d definitely use Surrey, or even tee off hot feed half way down cylinder in preference to Essex- but I’m a scardy cat having dropped one in cylinder before....
 
You say you leave the immersion alone, how are you going to get the Essex flange inside the cylinder?
I’d definitely use Surrey, or even tee off hot feed half way down cylinder in preference to Essex- but I’m a scardy cat having dropped one in cylinder before..

Sure he can just fit the Essex flange from the drill hole?
That is what it is designed for. The split copper washer covers inside the oversize hole
If anyone was to fit it from an immersion hole, just need a piece of stiff wire (earth wire good) and just use a brass tank fitting with something to seal it and let it thread through the wire. Drill hole then can be tight fit
 
Sure he can just fit the Essex flange from the drill hole?
That is what it is designed for. The split copper washer covers inside the oversize hole
If anyone was to fit it from an immersion hole, just need a piece of stiff wire (earth wire good) and just use a brass tank fitting with something to seal it and let it thread through the wire. Drill hole then can be tight fit
Yes. That's the route I think I'll take. Have a 38mm bimetal holesaw and will use my own long wire. But original reason for post was to find out if it's ok to have a male iron compression fitting inside the cylinder submerged permanently in the water to attach a piece of pipe to the flange on the inside with a 45 degree angle cut out for air to travel around the pipe and not up it. Thanks again for your advice.
 
Yes. That's the route I think I'll take. Have a 38mm bimetal holesaw and will use my own long wire. But original reason for post was to find out if it's ok to have a male iron compression fitting inside the cylinder submerged permanently in the water to attach a piece of pipe to the flange on the inside with a 45 degree angle cut out for air to travel around the pipe and not up it. Thanks again for your advice.

I hadn’t realised that is what you were thinking.
You can use a brass tank fitting if you use proper seals on it, but it will not fit through the top of cylinder unless you use the immersion hole, which is a problem to remove immersion.
 
I hadn’t realised that is what you were thinking.
You can use a brass tank fitting if you use proper seals on it, but it will not fit through the top of cylinder unless you use the immersion hole, which is a problem to remove immersion.
Thanks. Will post some pics of the idea I had in mind tomorrow because luckily I have a scrapped cylinder to do a mock up of the connections I have in mind. Cheers
 
Yes, sorry Best you’re right. Just I like to cut a nice tight hole if at all possible to get better coverage on the washers.
 
Yes, sorry Best you’re right. Just I like to cut a nice tight hole if at all possible to get better coverage on the washers.

I used to just fit brass tank fittings.
Far superior job, tight fit hole in cylinder and no rubber washers. Much cheaper too!
Used to fit 15mm tank fittings for return connection to Willis Immersion heaters (you probably won’t have heard of them)
Prefer to buy cylinders with extra bosses now.
And the 1/2” drain tapping doubles up for Willis pipe
 
External immersion feeds back into top of cylinder, never seen one in ‘real life’ though.
If a new cylinder, our merchants do gledhill who will make up to your exact requirements- a god send when replacing in a tight space (the old - put cylinder and pipe work, then build cupboard too tight- six the next plumber).
You can have as many bosses of chosen size precisely where you want! It’s a great service, have had it next day.
 
External immersion feeds back into top of cylinder, never seen one in ‘real life’ though.
If a new cylinder, our merchants do gledhill who will make up to your exact requirements- a god send when replacing in a tight space (the old - put cylinder and pipe work, then build cupboard too tight- six the next plumber).
You can have as many bosses of chosen size precisely where you want! It’s a great service, have had it next day.

Yes, a lot of copper cylinder manufacturers do “specials”.
Very handy in a tight space, as you say and well worth the effort to survey the job and make it easy for yourself later.

The Willis heaters use a 3kw (usually) 11” element. Save money because you can have a small amount of very hot water in a couple of minutes. It was invented in NI and very common here
 
I want to install an Essex Flange to the cylinder for a shower pump. ............

(My edit)

Would really appreciate any advice. Thanks very much in advance!! (Sorry for sending PMs of this to a few guys!! My first time using this!)
No worries about the PM as a newbie, far better off posting it here and getting replies plus you learnt a valuable lesson, Shaun the mod will read, edit or delete PM`s as he see`s fit being Judge, Jury and Executioner.
Enjoy the forum.
 
No worries about the PM as a newbie, far better off posting it here and getting replies plus you learnt a valuable lesson, Shaun the mod will read, edit or delete PM`s as he see`s fit being Judge, Jury and Executioner.
Enjoy the forum.
Thanks!
 
Top of the cylinder is a pain and is 20 inches below ceiling slab as cylinder is raised off the floor.
cyl1.jpg top1.jpg offthefloor.jpg
I was going to use this set up. Probably insane but is it a possibility?setup.jpg Pipe on the left of the set up to go into the cylinder is this one:

pipe1.jpg
Connection would be in this handy area place for flange.jpg just below the seam.
Don't mind drilling the hole. Only concern is the compression fittiing on the inside. Is it doable, possible, madness??
Thanks!
 
All interesting stuff...
Recently I was asked to survey a job to check whether a positive or negative head pump was required for a shower installation job required, ... this is what I found!
20181120_131004.jpg
 
I want to install an Essex Flange to the cylinder for a shower pump. (Cylinder is surrounded by shelving plus is about 15 years old and has overlapping pipes at top connection so I'd prefer to drill a hole in the cylinder and leave the older connections alone)
The flange I have is the E1R type
31212-5c8bf4e0152b9f33d95ce98bbae3d600.jpg
3/4 inch with no compression fitting. Can I use male couplers on either side of this type of flange to connect 3/4 inch pipe to and from the cylinder? Or would you solder some suitable brass threads onto the outside of the flange to convert it to a compression fitting type flange? Is it advisable not to have a compression fitting inside the cylinder submerged in water permanently? Would really appreciate any advice. Thanks very much in advance!! (Sorry for sending PMs of this to a few guys!! My first time using this!)
Why add a connection to the cylinder, with possible problems? You could take it from the HW cylinder vent pipe in the loft, and put the pump up there. Cold to pump direct from the CW storage tank. As long as the pump is > 0.5m or so below CW tank top level it's OK. Usually the pipes from the pump can drop conveniently straight on the shower inlets. They do say the vent pipe should be at 45° and the pump suction taken off downward (there are pics somewhere on the forum) to avoid risk of air into the pump. I don't know whether that's essential, once things have settled down there shouldn't be any air, and traces entering the pump won't hurt it.
I have a gravity shower piped that way (tee'd straight off the vertical vent pipe) and it works fine.
 
You obviously don’t live with hard water!
Leave tank full to crack open immersion, as you say to maintain integrity of wafer thin copper.
Then whip off top connection, bung hose pipe in and suck away! Syphon out tank in minutes - but via draincock at bottom amongst all the sludge it takes hours!
Plus no worry of drain cock weeping afterwards.
To finish off , 9 iron or wedge through immersion hole and oik out the scale with aid of wet vacuum.

Personally I’d use a sandwedge and a putter on my approach to the immersion hole :)
 

Reply to Essex Flange for a Shower Pump in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock