Hi

I’m trying to put more pressure into my external oil combo boiler (heatslave ii 1825) but can’t ring the filling loop

The only thing I can see which looks like a braided pipe with 2 black valves is right at the back of the boiler so is pretty much unreachable. So I’m assuming that can’t be it?

Does anyone have any experience of this type of boiler?
 
Pic of said valves
 
Hi

I’m trying to put more pressure into my external oil combo boiler (heatslave ii 1825) but can’t ring the filling loop

The only thing I can see which looks like a braided pipe with 2 black valves is right at the back of the boiler so is pretty much unreachable. So I’m assuming that can’t be it?

Does anyone have any experience of this type of boiler?
Your on the right lines already
Piccy is best tho as Shaun asked
Centralheatking
 
Hi

It’s so far back of the boiler behind so many wires that I can’t work get a decent snap

If it is there there is no way I can reach it I reckon

567B7C43-CCEF-4E4D-A05D-17887C3816F8.jpeg


3CB600E5-5E6B-4500-A8F8-105031B07B81.jpeg


A12EA797-F67D-4190-8A00-13AAEC0D91DD.jpeg
 
Same type of braided pipe but in a more obvious place , right under boiler, usually next to a mains cold water supply about 10 inches distance. BUT sometimes they can be elsewhere ...keep,looking you will find it ...let us know
centralheatking
 
Have you checked the manual? Its not the most helpful as it doesn't say where it is, just that you installer should have shown you, but it does say that the pressure guage is visible from the filling loop which might narrow it down.

Could it be that the braded filling loop hose isn't attached which could be why you can't find it.
 
I know this is an old thread but, did you ever find the filling loop? I'm in rented accommodation and having the same issue with the same boiler. The manual only explains how to use a filling loop not where to find it. I've reported the fault to the letting agents but they usually take days if not weeks to sort out repairs. I've never had a problem repressurising boilers in previous rental properties but this one is a complete mystery!
 
So I know this is an old thread but I'm sure others will still come across this needing to do this on their Greenstar Heatslave ii 18/25 boiler. Of course MAKE SURE YOU SWITCH BOILER OFF WHILE DOING THIS, and allow pipes to cool down too before attempting or you may scald yourself.

I have today successfully increased the pressure on my boiler using the filling loop which is inconveniently positioned towards the back (of the top left hand side of the internal boiler gubbins).

There are two flexible/braided hoses inside. Ignore the long one closest to the front of the boiler opening which is attached to the red expansion vessel.

The filling loop hose is the smaller one in length further and towards the back of the boiler. On ours it has 2x black plastic on/off valves at either end of the hose. One of these is visible on the right hand side hose end, but the second one is not on the left hand side hose as it is slightly underneath the isolation joint.

To start with I didn't know this as couldn't see the second valve, so turned on the first valve and nothing happened. After routing around a bit at the left side hose I found by feel the second valve and it was quite stiff. Took a bit of jiggle to loosen and then it also allowed to turn on.

My advice would be to turn on the more tricky out of sight (left hose end) valve first to the open position (mine was horizontal for closed and turned downwards to open), then position yourself so you have your hand on the other right side hose valve but at the same time can see the pressure gauge, slowly open the second valve and because you have already opened the first one you will start to hear water squirting through under pressure. I say do it slowly as you want to keep an eye on the pressure gauge as it increases towards around the no 1 mark. So doing this slowly allows you to control the increase easily without over doing it. Then when the needle reaches 1 close this valve. Then remember to close the other valve on the left side too back to the original off/closed position.

Job done👍👍

Added some photos to assist too, hope this helps others like this forum thread originally helped me determine this was the right course of action!

IMG_20201110_135330.jpg
IMG_20201110_135330.jpg
IMG_20201110_135304.jpg
IMG_20201110_135426.jpg
 

Reply to Filling loop on Greenstar Heatslave ii 18/25 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
301
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
215
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock