Discuss Balancing Problems Since Drain and Refill in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Messages
9
Since drain and refill of our gravity fed system I cannot get heat to alot of the downstairs rads. One downstairs rad is boiling but turning that off doesn't have any positive effect.
Most of the upstairs get nice and warm but if I turn off all of the upstairs rads then the boiler simply turns off instead of pushing heat downstairs. Boiler only gets call for heat again once upstairs are turned back on.

Any ideas please. Thank you
 
is the system zoned or perhaps a valve closed some where on the downstairs circuit

also sealed system or open vent?

If its open vented you could have a bad airlock in the downstairs circuit
 
Last edited:
If the above suggestions aren't the answer, you're left with 'sludge' blocking the downstairs circuit. Easily washed down in the draining process if you weren't very careful. Assuming the pipes are copper (or plastic) you may have some luck locating the blockage with a strong magnet.
 
Close the cylinder return gate valve, close all upstairs radiators, turn the boiler temperature down so it doesn't lock out.

Put the heating on, the pump should circulate around the downstairs circuit and push the air out. You might want to close all but one of the downstairs radiators then open them up one by one as they get hot.

I'd be listening for air moving around the system and watching the vent pipe over the tank to see if it pumps over, if it does your looking at sludge in the downstairs circuit.

If nothing happens I'd be checking the pump

Too be honest your getting into heating engineer territory
 
I'm guessing that the value bottom right is the cylinder return. Thank you.

20181203_082516.jpg
 

Reply to Balancing Problems Since Drain and Refill in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
256
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
176
My son has an apprenticeship interview for to become a plumber and heating engineer. The have said there will be a multiple choice exam for this for suitability. The thing is my son panics during tests/exams. Is there any book I can buy him to practice the multiple choice test for the exam? What...
Replies
3
Views
357
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
0
Views
117
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
207
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock