some advice needed, I could do with some input on a fanned flue outlet being 200 mm away from a cooker hood vent, the vent has flaps which close when not under positive pressure from hood. would this be classed as safe due to the flaps closing when cooker hood not in operation. I respect the fact maufactures instructions and bs expect 300 mm but I am a suing this would be in an open vent or window which is not under any pressure. any help would be great
 
Yes but I would note it down anyway
 
some advice needed, I could do with some input on a fanned flue outlet being 200 mm away from a cooker hood vent, the vent has flaps which close when not under positive pressure from hood. would this be classed as safe due to the flaps closing when cooker hood not in operation. I respect the fact maufactures instructions and bs expect 300 mm but I am a suing this would be in an open vent or window which is not under any pressure. any help would be great
I would not class this as safe. Both manufacturers and bs state 300mm. In the end if something goes wrong you are the one who gets the problem. Especially when people cook a lot they will use it.
 
some advice needed, I could do with some input on a fanned flue outlet being 200 mm away from a cooker hood vent, the vent has flaps which close when not under positive pressure from hood. would this be classed as safe due to the flaps closing when cooker hood not in operation. I respect the fact maufactures instructions and bs expect 300 mm but I am a suing this would be in an open vent or window which is not under any pressure. any help would be great

The 300mm does not apply to vents from a fixed appliance, such as cooker hoods.
I will dig out a reference
 

Reply to flue terminal too close to cooker vent in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We are considering buying a house which currently has a 20 year old Ideal Icos boiler, so we're factoring in replacing the boiler soon. Current boiler is on an external kitchen wall with the flue going straight out. However, it's positioned in between a door and the kitchen window, quite close...
Replies
2
Views
450
E
Hi all, Apologies if this has been covered elsewhere but I can't find an answer to my questions. I have a back boiler and gas fire which h has been serviced regularly over the years by different engineers with no issues. Last time , the guy wanted to condem it due to not being compliant with...
Replies
3
Views
915
My installation has been classed as Dangerous 'Do not use' by my boiler manufacturer. I have an Ideal Logic 30kw Combi boiler mounted as high as can be on the kitchen wall. Flue exits out through the wall via an elbow but emerges above a flat roof. Unfortunately it's somewhat less than the...
Replies
9
Views
1K
I live on the 3rd floor of a 6-story block of flats. (26 flats in total). During the evening when all people are inside their flats and using their boilers to heat their flats, there is obviously lots of steam coming out of all the different Boiler Flue Vents. if I open my window or go outside...
Replies
1
Views
1K
Hi I've got water hammer issues with my cold feed and some with the hot feed. When the cold sink tap, cold bath tap and thermostatic shower in the main bathroom is opened and closed there are hammering sounds from the living room ceiling. It sounds like knocking. There's no hammering whilst...
Replies
1
Views
424
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock